Power Supply in Parallel

06/14/2010 1:45 PM

When you have two 10A 24VDC power supplies in parrallel does the current double meaning 20Amps are available?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster
#1

Re: Power Supply in Parallel

06/14/2010 1:51 PM

Let's see.

Quantity (2)

Current per Supply (10 amps)

Total Current Available = 2 x 10 = 20 amps.

Yes.

Register to Reply
Anonymous Poster
#2

Re: Power Supply in Parallel

06/14/2010 2:04 PM

you copied my M Tech project!!!!.........

Register to Reply
2
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#3
In reply to #2

Re: Power Supply in Parallel

06/14/2010 4:30 PM

The answer is Yes or No.

If the purpose of the two 10A power sources is for maintaining the redundancy of supply for the vital load (if one supply is down, the other one keeps on for the continuity of supply), the total capacity is then 10A and the answer is No.

If the purpose of the two 10A power sources is not for maintaining the redundancy and for the case of one source is down, half of the loads can be remained down, the total capacity is then 20A and the answer is Yes.

In general, the dual power source is used for the redundancy of supply and I assume yours is for the same purpose. So, 'No' is the most probable answer in this case.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply Good Answer (Score 2)
Commentator

Join Date: Sep 2009
Posts: 59
#4
In reply to #3

Re: Power Supply in Parallel

06/14/2010 4:36 PM

Thanks for pointing that out. Yes I am using the power supply for redundancy, but if no power supplies fail the total current available is still 20 Amps, until one fails then I only have 10 Amps available.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#13
In reply to #4

Re: Power Supply in Parallel

06/15/2010 2:53 AM

Therefore the philosophy is incorrect.

  • If the second power supply has been installed as a redundant backup for the first supply, and if both are rated at 10A, then provided the load draws no more than 10A then either or both supplies will support the load. If one of them fails then the supply that has not failed will continue to support the up-to-10A load.
  • If the total load is between 10A and 20A and one of the supplies fails, then the second will not be adequate to support the load and it too will fail on overcurrent, thereby turning off the load. In this case, the second supply is vital, and not a redundant backup.

While both configurations are tolerable and safe, the acceptability of each arrangement is to be determined.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Feb 2006
Posts: 1758
Good Answers: 6
#15
In reply to #3

Re: Power Supply in Parallel

06/15/2010 9:55 AM

Good Answer.

For redundancy of 20A load needs 3x10A supplies.

As in Redundant UPS Systems; one module is addional than the number of modules required for actual load. If one module fails, it is isolated from system and still the system can take the full load.

Regards

Register to Reply
Guru
Hobbies - DIY Welding - Don't Know What Made The Old Title Attractive... Popular Science - Weaponology - New Member United States - US - Statue of Liberty - 60 Year Member

Join Date: Apr 2009
Location: Yellowstone Valley, in Big Sky Country
Posts: 7425
Good Answers: 295
#5

Re: Power Supply in Parallel

06/14/2010 4:47 PM

Hello rabat.

I have needed to do this a few times, and I have one comment, and a follow up question.

The power supplies I have used are all 120VAC 60 Hz filtered and regulated supplies. I have always cautioned the electrician energizing these to be certain the 120VAC supply for them was from the same phase.

Was this an unnecessary precaution?

__________________
Semper Ubi Sub Ubi
Register to Reply
Commentator

Join Date: Sep 2009
Posts: 59
#6
In reply to #5

Re: Power Supply in Parallel

06/14/2010 4:50 PM

The application I am using both 24VDC power supplies will receive it's 120VAC power from the same phase or source.

Register to Reply
Guru
Hobbies - DIY Welding - Don't Know What Made The Old Title Attractive... Popular Science - Weaponology - New Member United States - US - Statue of Liberty - 60 Year Member

Join Date: Apr 2009
Location: Yellowstone Valley, in Big Sky Country
Posts: 7425
Good Answers: 295
#7
In reply to #6

Re: Power Supply in Parallel

06/14/2010 5:14 PM

Let me rephrase my question, addressed to mostly other CR4 members:

The question is, is it necessary to energize the power supplies (in the intent of this thread) on the same phase?

On occasion, I have two (or more) power supplies from different parts of a building all energizing a common piece of equipment. Even though not a scheduled event, it is possible that all of my control boxes will energize this common equipment at the same time. When the power supplies are not/cannot be on the same phase, I have installed a relay isolator, to ensure the sources do not intermix.

To restate my question a little differently, is this isolation effort necessary if the power supplies are energized with different phases from the 120VAC?

__________________
Semper Ubi Sub Ubi
Register to Reply
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#11
In reply to #7

Re: Power Supply in Parallel

06/15/2010 12:27 AM

For almost every appication of linear pwr supplies (transformer, 1/2 or full wave rectifier, basic filtering) where the transformer primaries are not specifically tied together in some unique manner electrically, the primaries of the transformers do not have to be in phase with each other. Since the secondaries are isolated from each other by the transformers and the rectifiers they will only effect each other in a positive way---> less ripple!

A detailed discussion is much too long for this forum but a rectified 3 phase system has much less ripple and therefore requires much less filtering than a corresponding rectified single phase system

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Dec 2006
Posts: 346
Good Answers: 6
#12
In reply to #5

Re: Power Supply in Parallel

06/15/2010 12:57 AM

Doorman; i would use different phase! your way would be if the breaker tripped, you would be dead. perry

Register to Reply Score 1 for Good Answer
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#14
In reply to #5

Re: Power Supply in Parallel

06/15/2010 3:11 AM

If redundancy is the reason, then its not a good idea to supply both from the same source as if the source goes down, both are out!!!

As long as both have an isolation transformer as part of their design, then mormally no problems will happen. Diodes may be needed to prevent feedback from a working supply into a not working supply......depending upon design....

Each supply should be fused at 10 amps, so that if for any reason one supply takes too much load, the fuse will open the circuit.

Its a good idea to have a tiny bit of "droop" in such supplies, so that when one gets loaded first, it "droops" a tiny amount and brings the second supply "online". As setting them up to an identical voltage may prove to be difficult.....

I have built and used (and still use!) a really good double power supply (for my CNC work) from the Elektor magazine, that uses 2 x 5 amp chips to supply from 0 to 10 amps....

The circuit is very efficient and saves me money as when I am not drawing current, it only takes about 15% of the power at idle. (Most cheap Power supplies take almost the same power loaded or empty and give the excess power off as heat!!)

One chip is set up to work from 0 to 5 amps, the second "chimes in" when the load exceeds 5 amps.....eg. fills in the gap!!!

A true SMPS will be even slightly more efficient, but complex and difficult/dangerous to set up, this Elektor circuit uses a ring transformer to get the voltage into the required area first, isolating the circuit from the mains and also making the voltage levels far less dangerous. It can be set up to output from 5 to 40 volts as required.

Marking as off topic....

I forgot to mark it as off topic, now it won't let me with editting, sorry.....

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru
Hobbies - DIY Welding - Don't Know What Made The Old Title Attractive... Popular Science - Weaponology - New Member United States - US - Statue of Liberty - 60 Year Member

Join Date: Apr 2009
Location: Yellowstone Valley, in Big Sky Country
Posts: 7425
Good Answers: 295
#16
In reply to #14

Re: Power Supply in Parallel

06/15/2010 9:56 AM

Thanks Andy. And thanks to everyone for your interest and comments.

My application is the access and egress control systems of the memory care area of a convelescent home. There is always a struggle between Life Safety requirements and the need to control access and egress of memory care patients. Some of these systems get pretty 'busy'.

__________________
Semper Ubi Sub Ubi
Register to Reply Off Topic (Score 5)
Guru

Join Date: Feb 2006
Posts: 1758
Good Answers: 6
#17
In reply to #5

Re: Power Supply in Parallel

06/15/2010 9:58 AM

Yes !

It is un-neccessary; but all the PSUs be swithed on simulteneously otherwise there is a chance of failure of the supply switche on first.

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15601
Good Answers: 981
#8

Re: Power Supply in Parallel

06/14/2010 5:21 PM

It all depends on the actual output impedance and in the case of a diode coupled redundant power supply configuration you should not expect any added current capability for two reasons. First, by definition for redundancy each supply should be capable of driving the load alone. Second, the voltage drop across a diode is inversely related to the temperature of the junction. So as one supply starts to provide a little more current through it's power diode (A) than the other diode (B) a positive feedback happens. This happens because the forward bias equation for a PN junction is actually :

i=IS(e(qv/nkT) -1)

The variables and constants are the following:

  • i Forward diode current
  • IS Reverses diode saturation current
  • v Potential voltage across the diode
  • q Charge of an electron: 1.6E-19 joules/volt
  • k Boltzmann's constant: 1.38E-23 joules/°K
  • T Absolute temperature of junction in Kelvin
  • n Empirical scaling constant, typically between 0.5 and 2 for silicon. (Doping and topology effects this value.)
  • e Euler's constant: ≈2.71828

So with a constant current going through a diode, as the diode temperature increases from self heating the diode voltage drop decreases.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#9

Re: Power Supply in Parallel

06/14/2010 7:44 PM

Some power supplies can be used thus (e.g. Power One Type W) - some can't (without additional circuitry). If in doubt, consult the datasheet for your power supplies, or contact the manufacturers.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply Score 1 for Good Answer
Guru
United States - Member - New Member Engineering Fields - Mechanical Engineering - New Member Engineering Fields - Petroleum Engineering - New Member Hobbies - Target Shooting - New Member

Join Date: Jan 2008
Location: Spring, Texas
Posts: 3403
Good Answers: 150
#10

Re: Power Supply in Parallel

06/14/2010 11:25 PM

Generally speaking, the answer is usually no unless the supplies are specifically designed to be paralleled. what happens is that one supply will be a fraction of a volt higher than the other and it will supply virtually all of the current and the other supply will essentially just be barely ticking over. It also depends on the type of supply it is. linear supplies do not parallel worth a flip. Switch mode supplies with MOSFET outputs often can because MOSFETS have a negative temperature coefficient. As the current increases, the on resistance increases and the current goes back down. so MOSFETs in parallel share loads fairly well. If you are using switch-mode supplies with MOSFET outputs, you should probably put a very low resistance high wattage resistor in series with each supply.

__________________
Who is John Galt?
Register to Reply Score 1 for Good Answer
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#18
In reply to #10

Re: Power Supply in Parallel

06/15/2010 9:12 PM

Friends,

Last two answers are best. Let me add--go to the manufacturer's literature and check their application instructions. If they say you can parallel the outputs, then you can. If they say that the inputs of paralleled supplies must all be on the same phase or same circuit, then that is a mandatory requirement and you violate it at your own peril/liability. Depending on the degree of reliability or redundancy needed in your system, particularly if life safety or security is involved, you may want to include methods to monitor the health and operation of each of the supplies in addition to monitoring the total current draw, etc. Remember that most fire codes will require that any electrically-locked exit doors be unlocked in the event of a fire alarm. This is true even in a mental institution with locked wards.

--JMM

Register to Reply
Guru

Join Date: Feb 2006
Posts: 1758
Good Answers: 6
#19
In reply to #18

Re: Power Supply in Parallel

06/16/2010 4:52 AM

Regards.

Today most of the Dual Supplies are manufactured to be connected in parallel to double the current & in series to double the Voltage ratings.

These supplies are with a sngle power cord so no question of connecting to different phases.

The output of all supplies is DC, if connected to different phases of the same grid there seems to be no problem as the N & E are common.

We ar not connecting AC in parralel where In-Phase connection is required.

Register to Reply
Power-User

Join Date: May 2010
Location: longo tempo dos macaco do pilas. Felizment.
Posts: 251
#20

Re: Power Supply in Parallel

06/16/2010 2:37 PM

Yes....but bear in mind how you achieve this connection I would use 2 diodes and at least one condenser.

__________________
I am a deeply religious nonbeliever - this is a somewhat new kind of religion. Albert Einstein
Register to Reply
Guru

Join Date: Feb 2006
Posts: 1758
Good Answers: 6
#21
In reply to #20

Re: Power Supply in Parallel

06/17/2010 8:27 AM

Why the condenser?

To make sure that .....main supply ripples are minmum

have always a ceramic 0.001µF capacitor to remove hi freq noice/ripples

Regards

Register to Reply
Power-User

Join Date: May 2010
Location: longo tempo dos macaco do pilas. Felizment.
Posts: 251
#22
In reply to #21

Re: Power Supply in Parallel

07/29/2010 6:38 PM

Why the condenser?

This is why.......as you said it.

To make sure that .....main supply ripples are minimum

have always a ceramic 0.001µF capacitor to remove hi freq noice/ripples

A condenser is what you call a capacitor....ceramic 0.001µF capacitor.

__________________
I am a deeply religious nonbeliever - this is a somewhat new kind of religion. Albert Einstein
Register to Reply Off Topic (Score 5)
Power-User

Join Date: May 2010
Location: longo tempo dos macaco do pilas. Felizment.
Posts: 251
#23
In reply to #21

Re: Power Supply in Parallel

07/29/2010 6:39 PM

What do you think a condenser is ????

__________________
I am a deeply religious nonbeliever - this is a somewhat new kind of religion. Albert Einstein
Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#24
In reply to #23

Re: Power Supply in Parallel

07/29/2010 6:59 PM

The name 'condenser' was used when I was very young, and I was familiar with it through the pages of library books, and magazines such as Practical Wireless. I have not encountered it in an electronics context during my working life - about 35 years.

It is certainly is not current terminology in most English-speaking countries.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply Off Topic (Score 5)
Power-User

Join Date: May 2010
Location: longo tempo dos macaco do pilas. Felizment.
Posts: 251
#25
In reply to #24

Re: Power Supply in Parallel

07/29/2010 7:07 PM

Well whatever a condenser is a capacitor what do you think I meant by a condenser ?

It condenses electrons...I am only 45 and have been in electronics for 20 years and I call them condensers.

So why do ask the question ?

That is all.

__________________
I am a deeply religious nonbeliever - this is a somewhat new kind of religion. Albert Einstein
Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#26
In reply to #25

Re: Power Supply in Parallel

07/29/2010 7:14 PM

"So why do ask the question ?"

I did not.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply Off Topic (Score 5)
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#27
In reply to #24

Re: Power Supply in Parallel

07/30/2010 12:03 PM

I would still expect anyone doing electronics to be able to understand the word, or have the gumption to be able to look it up and work out which entry is valid.........

I checked an online English dictionary and got this:-

con·dens·er (kn-dnsr) n.

1. One that condenses, especially an apparatus used to condense vapor.2. See capacitor.3. A mirror, lens, or combination of lenses used to gather light and direct it upon an object or through a projection lens.

Now how difficult was that?

Which entry would you pick?

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply Off Topic (Score 5)
Guru

Join Date: Feb 2006
Posts: 1758
Good Answers: 6
#28
In reply to #27

Re: Power Supply in Parallel

07/30/2010 1:06 PM

As far as I remember CONDENSER is also used for RADIATOR/COOLING PART of Airconditioner /refrigrator:

The refrigerant travels to the condenser (Which can be air cooled by fans or water cooled by tower or city water). The condenser changes the refrigerant from a high temperature gas to a warm temperature liquid. It then travels into a receiver (optional component). It continues to the Thermal Expansion valve or TXV. The TXV meters the proper amount of refrigerant into the evaporator. The TXV takes the high pressure liquid and changes it to a low pressure cold saturated gas ...

from:

http://www.chillers.com/RefrigCycle.htm

Register to Reply Off Topic (Score 5)
Power-User

Join Date: May 2010
Location: longo tempo dos macaco do pilas. Felizment.
Posts: 251
#33
In reply to #28

Re: Power Supply in Parallel

07/30/2010 6:47 PM

Yeah maybe and there is also a condenser microphone.

A condenser just gathers things together.

http://www.mediacollege.com/audio/microphones/condenser.html

and maybe this will help.

http://www.electro-tech-online.com/general-electronics-chat/30116-capacitor-vs-condenser.html

If you talk about condensers in electronics you mean these objects some people call capacitors which are objects very different from a cooling part would be silly to attach to the circuit described unless you wanted to cool the circuit.

Sorry you mis-understood the word condenser but that is all I think that happened.

__________________
I am a deeply religious nonbeliever - this is a somewhat new kind of religion. Albert Einstein
Register to Reply Off Topic (Score 5)
Guru

Join Date: Feb 2006
Posts: 1758
Good Answers: 6
#34
In reply to #33

Re: Power Supply in Parallel

07/30/2010 7:39 PM

Yes !

Well known Mic having low background noise.

Register to Reply
Power-User

Join Date: May 2010
Location: longo tempo dos macaco do pilas. Felizment.
Posts: 251
#47
In reply to #28

Re: Power Supply in Parallel

08/01/2010 10:24 PM

What has that got to do with an electrical condenser ?

__________________
I am a deeply religious nonbeliever - this is a somewhat new kind of religion. Albert Einstein
Register to Reply Off Topic (Score 5)
Guru
Safety - Hazmat - New Member Safety - ESD - New Member Engineering Fields - Transportation Engineering - New Member Popular Science - Evolution - New Member Technical Fields - Procurement - New Member Hobbies - Target Shooting - New Member Popular Science - Cosmology - New Member Engineering Fields - Architectural Engineering - New Member Technical Fields - Marketing/Advertising - New Member Engineering Fields - Food Process Engineering - New Member

Join Date: Dec 2005
Location: Mariposa Ca
Posts: 5800
Good Answers: 114
#48
In reply to #47

Re: Power Supply in Parallel

08/01/2010 10:57 PM

They share the same level of relevance to the original question

or

Eles compartilham o mesmo nível de relevância para a questão original

or for AG

Sie teilen das gleiche Maß an Relevanz für die ursprüngliche Frage

Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#29
In reply to #27

Re: Power Supply in Parallel

07/30/2010 4:26 PM

Andy, you and I both know what a condenser is (or was) in electronics and in other contexts. My point is that this word (in electronics) is obsolete today. The component under discussion is known as a capacitor, and has been for many years. Why should young(er) engineers be expected to recognize the word in this context, when its use (as the name of a component) amounts to an anachronism?

Maybe you can help us out by explaining to the younger members how best to adjust the whisker on the crystal when using a semiconductor diode?

Perhaps you'd rather start by explaining diode valves (or should I call them tubes?). What is an appropriate current for the filament?

Why do you think anyone should need to reach for the dictionary when such an occasion arises?

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply Off Topic (Score 5)
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#30
In reply to #29

Re: Power Supply in Parallel

07/30/2010 5:21 PM

What you may also be forgetting is that many countries STILL use the word for Condenser, Germany for one uses the word "Kondensator"...

Does not the person concerned live in Spain or Portugal or somewhere like that? Might it be that where he lives they still use the word "Condenser" today in his language?

I personally still feel that its not old fashioned to "understand" the word, its just old fashioned to "use" it daily....

Not knowing the word at all, if one is in the electronics industry in some fashion, shows some missing information.

If its only this one word - no problem. But it could be indicative of maybe a larger area of missing knowledge/expertize....

As I mentioned earlier, in the one online dictionary I looked at it was mentioned exactly what it was!! Also I am sure its not the only one around that manages to have the correct explanation....

I can read and understand 17-19th Century English, I need it for some of the old books I read.....but I don't use the words/structure when talking to anyone, well not often at least!!!

I can also read Teutonic/Gothic style of German texts, as they were still used in some newspapers when I first came here:-

But it does not mean that I write using it either!!!!

Have a great day/weekend.

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply Off Topic (Score 5)
Associate

Join Date: Jun 2010
Location: Dancing Over the Icelandic Abyss
Posts: 41
#38
In reply to #30

Re: Power Supply in Parallel

08/01/2010 1:11 PM

When you are on an German [or portugese] language websites feel free to use as many alternate words & definitions as you please.

On this site you should stick with the more common technical terms

But I know you & your little friend love to pick fights, to belittle others & try to impress us all with your knowledge & sometimes forget to actually read the questions or responses

__________________
Charter Member CR4 Community Moderation Oversite Commitee
Register to Reply Off Topic (Score 5)
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15601
Good Answers: 981
#39
In reply to #38

Re: Power Supply in Parallel

08/01/2010 3:02 PM

Here is the essence of this argument. You, VisiGuest and those who dislike the term condenser, never want to hear two conductors separated by an insulator as anything but the single term capacitor.

How stuck up and sanctimonious can you get you small minded, overly opinionated fools. You've wandered directly into the fool-hearted, soulless mindset of Luddites, the Spanish Inquisition and programming languages. I take that back, even in programming languages there is more than one way to express a concept. Instead of berating anyone for using any term you might conceive as antiquated, obsolete, antediluvian or just simply baffling to your bigoted perspective just ask for a clarification. Too many people come here with insufficient information for any of us to assist them. You should relish people that accurately describe things in any form.

So please, SHUT THE DUCK UP!

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Off Topic (Score 6)
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#41
In reply to #39

Re: Power Supply in Parallel

08/01/2010 4:08 PM

LOL!!

Like it!!!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Associate

Join Date: Jun 2010
Location: Dancing Over the Icelandic Abyss
Posts: 41
#45
In reply to #39

An Over Supply of Egos in Parallel

08/01/2010 8:46 PM

So by preferring the use of more common terms [as agreed by all the parties] so as not to confuse, I am to be likened to a perpetrator of the spanish inquisition? & Wouldn't a luddite prefer an obsolete term?

You have spewed a verbose rant, do you feel better? Why don't you and your clan of egomaniacs try for the accuracy you claim to relish .!.. next time?

__________________
Charter Member CR4 Community Moderation Oversite Commitee
Register to Reply
Guru
Safety - Hazmat - New Member Safety - ESD - New Member Engineering Fields - Transportation Engineering - New Member Popular Science - Evolution - New Member Technical Fields - Procurement - New Member Hobbies - Target Shooting - New Member Popular Science - Cosmology - New Member Engineering Fields - Architectural Engineering - New Member Technical Fields - Marketing/Advertising - New Member Engineering Fields - Food Process Engineering - New Member

Join Date: Dec 2005
Location: Mariposa Ca
Posts: 5800
Good Answers: 114
#46
In reply to #45

Re: An Over Supply of Egos in Parallel

08/01/2010 9:22 PM

Hmm

So is the IQ of 3 brains in parallel additive like Capacitors? only my refrigerator has has a condensor

By the looks of this thread, I think the resistor formula is more likely to be correct

Register to Reply
Anonymous Poster
#49
In reply to #46

Re: An Over Supply of Egos in Parallel

08/02/2010 11:59 AM

Talking to yourself?

Register to Reply
Associate

Join Date: Jun 2010
Location: Dancing Over the Icelandic Abyss
Posts: 41
#50
In reply to #49

Re: An Over Supply of Egos in Parallel

08/02/2010 12:52 PM

How many guests does it take to screw in a light bulb?

__________________
Charter Member CR4 Community Moderation Oversite Commitee
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#40
In reply to #38

Re: Power Supply in Parallel

08/01/2010 4:07 PM

I hope you now feel better........

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15601
Good Answers: 981
#42
In reply to #40

Re: Power Supply in Parallel

08/01/2010 4:58 PM

Actually, I do feel better. Thank You. I'm glad you liked it.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#43
In reply to #42

Re: Power Supply in Parallel

08/01/2010 5:41 PM

I wasn't actually addressing you at that point in time (check back!!), but I am still VERY glad you do feel better my friend!!!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Power-User

Join Date: May 2010
Location: longo tempo dos macaco do pilas. Felizment.
Posts: 251
#32
In reply to #29

Re: Power Supply in Parallel

07/30/2010 5:59 PM

It is not an obsolete word at all...you seem to be using it a lot !

Is a coil a winding ?

Is a winding a motor or generator ?

A capacitor has capacitance.

A condenser condenses.

A wire has capacitance...is the wire a capacitor ?

A condenser is an electronic component and if you do not know , young or old , then you have not studied the subject properly and should not be playing around with electricity or the components.

__________________
I am a deeply religious nonbeliever - this is a somewhat new kind of religion. Albert Einstein
Register to Reply Off Topic (Score 5)
Guru

Join Date: Feb 2006
Posts: 1758
Good Answers: 6
#35
In reply to #29

Re: Power Supply in Parallel

07/30/2010 7:42 PM

Yes!

Not only the word but also the old notations for it

Register to Reply Off Topic (Score 5)
Power-User

Join Date: May 2010
Location: longo tempo dos macaco do pilas. Felizment.
Posts: 251
#31
In reply to #24

Re: Power Supply in Parallel

07/30/2010 5:49 PM

I used the term "condenser" in the UK and I was understood by engineers.

It was only the people with "degree's" who did not understand me.

Why the condenser? was the question and then they state...

To make sure that .....main supply ripples are minmum

have always a ceramic 0.001µF capacitor to remove hi freq noice/ripples.

That was the question dear yoric.

__________________
I am a deeply religious nonbeliever - this is a somewhat new kind of religion. Albert Einstein
Register to Reply Off Topic (Score 5)
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#36
In reply to #31

Re: Power Supply in Parallel

07/31/2010 10:45 AM

LOL!!

Maybe the Universities today have cut out all references to such a name!!! They are saving money!!!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply Off Topic (Score 5)
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#37

Re: Power Supply in Parallel

07/31/2010 10:54 AM

Maybe we should start a thread on names for electronic names/devices that have either been forgotten or are not generally used anymore!

Wasn't the original Condenser/Capacitor a "Leyden Jar"? That also showed if there was a charge stored on it visually!!

Rheostat? Nowadays a variable potentiometer......Though I personally tend to think of Rheostats as handling amps rather than milliamps.....

Cat's whisker, an early forerunner of the diode, but needed careful handling. My Father as a kid woould make them from a short length of aluminium rod and a piece of coal....for his "Crystal set".......

Valves are still in use, but not quite so much by the amateur anymore.....

Anymore Guys?

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Power-User

Join Date: May 2010
Location: longo tempo dos macaco do pilas. Felizment.
Posts: 251
#44
In reply to #37

Re: Power Supply in Parallel

08/01/2010 5:55 PM

I have started a new topic.

Find it and I will be interested in your response.

__________________
I am a deeply religious nonbeliever - this is a somewhat new kind of religion. Albert Einstein
Register to Reply Off Topic (Score 5)
Power-User

Join Date: May 2010
Location: longo tempo dos macaco do pilas. Felizment.
Posts: 251
#51
In reply to #37

Re: Power Supply in Parallel

08/02/2010 3:12 PM

A variable resistor do you mean ?

All working potentiometers are variable are the not ?

Pelter device by my other posts nobody knows these components at all.

__________________
I am a deeply religious nonbeliever - this is a somewhat new kind of religion. Albert Einstein
Register to Reply Off Topic (Score 5)
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#52
In reply to #51

Re: Power Supply in Parallel

08/02/2010 4:05 PM

A variable resistor was once called a Rheostat.......

Look here:-

Rheostat

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru

Join Date: Feb 2006
Posts: 1758
Good Answers: 6
#53
In reply to #52

Re: Power Supply in Parallel

08/02/2010 4:14 PM

Yes !

But normally big [Hi-Power used to control current thru or Voltage accross] a power device like Fan speed, light dimming, etc etc.

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#54
In reply to #53

Re: Power Supply in Parallel

08/02/2010 4:55 PM

Exactly as I already mentioned some days ago in post #37 (this is nowpost #54 or so!!!) AND it was re-mentioned in the link I posted.

Now you have mentioned it a third time......

Was that REALLY needed ?

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15601
Good Answers: 981
#55
In reply to #54

Re: Power Supply in Parallel

08/02/2010 5:02 PM

De Ja Vu all over again.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#56
In reply to #55

Re: Power Supply in Parallel

08/02/2010 5:16 PM

Time to introduce the Bose-Einstein Condenser.

(I have one in my pocket - but it's freezing my balls off).

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply Off Topic (Score 5)
Power-User

Join Date: May 2010
Location: longo tempo dos macaco do pilas. Felizment.
Posts: 251
#57
In reply to #55

Re: Power Supply in Parallel

08/02/2010 5:32 PM

Déjà vu but we have been here before.

__________________
I am a deeply religious nonbeliever - this is a somewhat new kind of religion. Albert Einstein
Register to Reply Off Topic (Score 5)
Register to Reply 57 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Andy Germany (10); Anonymous Poster (3); Doorman (3); Garthh (2); Haajee (8); jmueller (1); JohnDG (5); msamad (1); old salt (1); perry (1); portugalphilip (11); PWSlack (1); rabat (2); redfred (4); Rorschach (1); VisiGuest (3)