Resistance of Earth/Ground Electrode

06/14/2010 1:34 PM

While measuring the resistance of a ground electrode by the three terminal method I got a lower reading when I substituted a long rod instead of the short spike supplied by the manufacturer. Is it because the top layer of soil may not be compacted sufficiently with the already existing soil in the new work site or in every location it will happen? Have anybody tried?

__________________
pnaban
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: resistance of earth/ground electrode

06/14/2010 2:27 PM

Dry dirt has higher resistance than wet dirt. Maybe the surface dirt is dry. Probably has less to do with compaction than humidity of the soil.

Register to Reply Score 1 for Good Answer
Anonymous Poster
#2

Re: resistance of earth/ground electrode

06/14/2010 2:44 PM

See the below thread for better earthing knowledge.

http://cr4.globalspec.com/comment/576932/Re-earth-pits

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3
In reply to #2

Re: resistance of earth/ground electrode

06/14/2010 8:47 PM

That's dirty. Shot with my own arrow. That's the pits.......................

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#4

Re: Resistance of Earth/Ground Electrode

06/14/2010 10:19 PM

The longer the rod, the more area of contact, the less resistance; especially if the increased length encounters some wetter portions of the soil. That's a Homer Simpson problem...doh!

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Power-User
Engineering Fields - Power Engineering - New Member

Join Date: Nov 2009
Location: Abuja, Nigeria.
Posts: 126
#5

Re: Resistance of Earth/Ground Electrode

06/15/2010 2:07 AM

It happens in very dry areas but much job is still required from U as to how the main earth pit was prepared. There are areas that will never improve in its earth electrode resistance because of its soil structure, areas of these nature will definitely require other forms of earthing or earth leakage protection.

I have witnessed two tanker load of water emptied in an earth pit in trying to improve the earth electrode resistance area, actually it worked out when the water completely seeped through the soil. The earth pit was now prepared and completed with the necessary material and when tested it came out fine. compacting soil is different from bonding of soil. Bonding will have to do with the binding together of the soil and the main earth electrode as one unit. Water plays a very important rule, any soil that can not retain water will have a poor earth electrode resistance.

Check Ur soil and see if water is needed as a result of the compacted area. U can try this by puring water from the main electrode to the auxiliary electrode points; leaving it for one hour before replacing the electrodes and taking another test. If its a good soil for earthing, U will have an improved reading. U can now prepare the earth pit by introducing enough water.

If Ur soil is sandy, try Protective multiple earthing or other form of earth leakage protection.

Dickson

__________________
There is peace in silence and achievement in plans.
Register to Reply
Anonymous Poster
#6

Re: Resistance of Earth/Ground Electrode

06/15/2010 6:38 AM

The earth tester is designed to get the proper value with the given short spikes and not with any long rods. Use long rods, you will get lower reading and that will not be correct.

Register to Reply
Active Contributor

Join Date: May 2008
Location: Chandigarh , India
Posts: 11
#7

Re: Resistance of Earth/Ground Electrode

06/15/2010 6:47 AM

Yes,

Longer the spikes lesser the resistance, Secondly if u move deeper moisture in soil increase, third earth pit is of atleast 14 feet deep so more u go deeper better will be circuit close loop , all three results less resistance

Register to Reply Off Topic (Score 5)
Register to Reply 7 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); Dickson (1); lyn (2); Punit Sharma (1); Tornado (1)

Previous in Forum: DG Sizing   Next in Forum: Power Supply in Parallel

Advertisement