Anonymous Poster

Electrical Engineering

06/15/2010 9:14 AM

Do 3 phase motor require a neutral

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: Electrical Engineering

06/15/2010 9:19 AM

I am not able to give you the proper answer. But you will get good enough continuied by this reply. A 3 phase motor required neutral only. Are you just landed from the space right now??...

Reply
Commentator

Join Date: Dec 2009
Location: Mangalore, India
Posts: 65
Good Answers: 4
#2

Re: Electrical Engineering

06/15/2010 10:03 AM

NO. A 3 phase motor does not require a neutral. Refer to the name plate for the voltage rating of the motor.

Only a source (generator, distribution transformer) will have a neutral.

Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#3

Re: Electrical Engineering

06/15/2010 10:28 AM

To wire a three phase motor in a Wye configuration, one should include a neutral connection. But I believe that technically this is not required, only advised. To wire a three phase motor in a delta configuration obviously does not requires a neutral.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#5
In reply to #3

Re: Electrical Engineering

06/15/2010 2:28 PM

In 35+ years in this industry, I have never once seen a wye wound motor wired with a neutral circuit brought out to the peckerhead.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#6
In reply to #5

Re: Electrical Engineering

06/15/2010 2:31 PM

OK, my folly then.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: Electrical Engineering

06/15/2010 11:44 AM

If it is wired in star at the motor terminals, any neutral provided will carry any imbalance current between the three phases. It is not usually needed.

If it is connected in delta or to a star-delta starter, then a neutral cannot be connected; there is no scope for it.

If in doubt, consult a qualified electrician.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Anonymous Poster
#7

Re: Electrical Engineering

06/15/2010 2:45 PM

Thanks everybody....i removed the neutral now. I wired 4 wires to motor and i couldnt see the place for connecting the neutral...is it ok if i connect neutral alongwith one of the terminal..U,V, or W??

Reply
Guru

Join Date: Jul 2008
Location: SoCal USA
Posts: 556
Good Answers: 23
#8
In reply to #7

Re: Electrical Engineering

06/16/2010 2:39 AM

Not necessary. You could however keep it set aside as a replacement should you have a problem with one of the other conductors that does not involve it's conduit mates.

Just a thought. CJM

__________________
I do not 'know it all', but i will admit that I would like to. CJM
Reply