I am having strange problem in my 100MVA transformer. First let me describe what we did a week before
- There was some oil leakage in transformer
- I kept the valve of buchholz relay off and drained some oil to drum to lowe the level.( about 300 ltr of oil was drained)
-after doing bushing job, I opened the buchholz valve and conservator tank oil came in main tank. while doing so I did venting of air from buchholz and bushing
-then I top up the drained oil from conservator tank from top
-oil level was same before and after the job
after one day the transfor charged, it tripped on bchholz. Now we have to do air venting after every two hours. otherwise it will trip in 5 to 6 hours on buchholz. DGA shows N2 and O2 % is high.
We dont know from where these much air is coming.(Even afer 7 days)
transformer is running 24 hrs.
If any idea is there please comment..