Digital Electronic Energy Meters

06/20/2010 11:44 AM

another question for problem solvers.

in electronic digital energy meters why fuse is not used in CT connection .

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Feb 2008
Location: Large hole formally occupied by furry woodland creature.
Posts: 3385
Good Answers: 97
#1

Re: Digital Electronic Energy Meters

06/20/2010 11:56 AM

An open secondary on a CT is dangerous if energized.

__________________
CRTL-Z
Register to Reply Score 1 for Good Answer
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#2

Re: Digital Electronic Energy Meters

06/20/2010 3:00 PM

Current transformers are never fused for safety reasons, the fuse (or similar protective device) would actually create a more dangerous situation than if it were just left out.

http://en.wikipedia.org/wiki/Current_transformer

A common method in the power and instrumentation industries is to instead install shorting links to allow the CT output to be shorted for maintenance or live removal, however I doubt this is applicable or necessary for your application.

__________________
jack of all trades
Register to Reply Score 1 for Good Answer
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#3

Re: Digital Electronic Energy Meters

06/20/2010 4:56 PM

The load of a CT is characterized as "burden". Meaning the CT has to be balanced with a meter load circuit that is stable.

A fuse in this line compromises the efficiency of this circuit because of a big difference in conductor size and the permanent change in conductivity between a cold and hot fuse wire.

(Burden mostly ranges in values lower than 0.5 ohms).

A electronic meter starts fusing the electronic circuits, loose from this circuit - it is IN the meter printed circuit.

__________________
Plenty of room here
Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#4

Re: Digital Electronic Energy Meters

06/21/2010 9:21 AM

CTs work on Short circuit basis. A fuse is not Useful BUT detrimental as follows:

if YOU OPEN THE CIRCUIT when there is a current flowing in the main cable (Primary), the Voltage at the Open ends will be very HIGH and will start destroying the CT windings: This will result in burning the winding due to shorts created by the very high voltage. (Sometimes it might explode) but then evrything stops as soon as the CT is compromised.

Register to Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#5

Re: Digital Electronic Energy Meters

06/21/2010 11:35 PM

Salahuddin Zia,

A CT is a transformer in which the design is a ratio of primary current to secondary current, not voltage to voltage. Thus it is inherently current-limiting. As others have said repeatedly, an open-circuit on the secondary of a CT is potentially dangerous whereas a short-circuit is fully within its design capabilities. Thus, a fuse is not only unnecessary (current-limiting design) but potentially dangerous (uncontrolled open-circuit voltage). In ammeter switches, where one meter can read any of the CT's on a 3-phase system, the wiring of the switches short-circuits the CT's that are not connected to the meter.

--JMM

Register to Reply
Anonymous Poster
#6

Re: Digital Electronic Energy Meters

08/04/2010 5:02 AM

rvt is provided

Register to Reply
Register to Reply 6 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!