60 hz to 50hz?

06/21/2010 11:03 AM

If I have a device that is for 60hz 120v 1A.... it would be 120W ..If I were to use that in a country where power is consumed @ 50hz ...230V would the current just be .5A? Does the power stay the same @ 120W? I was looking at a spec sheet for a device. It says 120V 1.4A 60hz 220 to 230V 95W @ 50Hz shouldn't the power stay the same when you go from 60 to 50hz?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: May 2010
Location: in optimism
Posts: 4050
Good Answers: 130
#1

Re: 60 Hz to 50Hz?

06/21/2010 11:37 AM

The RMS (root mean square) value changes with the frequency.

If it is transformer based, the turns to iron ratio is 'ideally' for a frequency.

Similarly a switching type may be more efficient at a design frequency.

Meaning it just may be more efficient at 50Hz than 60.

Would help if you said what the device was.

__________________
There is no sin except stupidity. (Oscar Wilde, Irish dramatist, novelist, & poet (1854 - 1900))
Register to Reply
Member

Join Date: Jun 2010
Posts: 6
#2

Re: 60 hz to 50hz?

06/21/2010 11:54 AM

if i just use the adapter into the wall... is that ideal? not ideal? im still confused on how i would calculate the power consumption @ 50hz.

Register to Reply
Anonymous Poster
#3

Re: 60 hz to 50hz?

06/21/2010 12:42 PM

Depends on the type of device it is and whether there is any internal conversion of the input power.

Consider an ohmic device like an incandescent light bulb. A 120 W light bulb would put out 480 watts if if were connected to a 240 V source; though not for very long since it would burn out much quicker.

Register to Reply
Member

Join Date: Jun 2010
Posts: 6
#4

Re: 60 hz to 50hz?

06/21/2010 12:47 PM

so is there a way to calculate how much power a 60hz device would consume on a 50hz source?

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#5
In reply to #4

Re: 60 hz to 50hz?

06/21/2010 1:08 PM

Yes, there is a way to calculate how much power a device designed to operate on 120VAC 60 Hz power will draw when attached directly to 220VAC 50 Hz power. But which calculation one should use to produce an accurate value will depend solely on identifying the input impedance of the device. Without knowing what the device is or the input impedance then no equation can be offered.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#6
In reply to #5

Re: 60 hz to 50hz?

06/21/2010 1:16 PM

I forgot to mention that the key factor that you are missing that will permit us to calculate the input impedance from the data you've provided is the phase angle between the 1 ampere of current and 120VAC power. Oh, your power calculation is not correct without knowing this information. Without knowing this, all that you can say is that you have 120VA which means the maximum power you can draw is 120 Watts.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Member

Join Date: Jun 2010
Posts: 6
#7

Re: 60 hz to 50hz?

06/21/2010 1:18 PM

i dont see the impedance on the device... so lets say its 2.2 impedance

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#8
In reply to #7

Re: 60 hz to 50hz?

06/21/2010 1:30 PM

Electrical impedance requires two numbers.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Power-User
Fans of Old Computers - ZX-81 - New Member

Join Date: Feb 2008
Location: Beirut Lebanon
Posts: 197
Good Answers: 8
#9

Re: 60 hz to 50hz?

06/21/2010 1:40 PM

it depends on the nature of your device,

if it is a resistor(heater) frequency dont matter too much, just the voltage,

you cannot apply a voltage over than the nominal voltage of the device whatever this device is,

you cannot apply a 230V-50Hz supply to a 120V-60hz device, you will burn, it you need an adapter..

BTW, what is this device? a shaving machine by any chance?

__________________
dont say it, write it
Register to Reply Score 1 for Good Answer
Member

Join Date: Jun 2010
Posts: 6
#10

Re: 60 hz to 50hz?

06/21/2010 1:47 PM

ok what if i forget about using the 60hz device on 50hz service... but a spec sheet states It says 120V 1.4A @ 60hz 220 to 230V 95W @ 50Hz so is there normally a drop in power?

Register to Reply
Power-User
Fans of Old Computers - ZX-81 - New Member

Join Date: Feb 2008
Location: Beirut Lebanon
Posts: 197
Good Answers: 8
#11
In reply to #10

Re: 60 hz to 50hz?

06/21/2010 1:51 PM

Not in Power, in Power factor

again it depends of the device....what is this device/?

__________________
dont say it, write it
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#12
In reply to #11

Re: 60 hz to 50hz?

06/21/2010 1:55 PM

Face it, he/she's not going to tell us. No matter how many ways or how politely we ask this is going to stay a "device."

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Power-User
Fans of Old Computers - ZX-81 - New Member

Join Date: Feb 2008
Location: Beirut Lebanon
Posts: 197
Good Answers: 8
#13
In reply to #12

Re: 60 hz to 50hz?

06/21/2010 2:00 PM

let's say it is a vibrator,

at 120v-60hz, he/she will get more power than 50hz any voltage, more vibrations

__________________
dont say it, write it
Register to Reply Off Topic (Score 5)
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#14
In reply to #13

Re: 60 hz to 50hz?

06/21/2010 2:43 PM

That depends on the cavity resonance.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Off Topic (Score 6)
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#30
In reply to #13

Re: 60 hz to 50hz?

06/22/2010 10:18 AM

That is a MASSIVE Vibrator, are you sure its not his thermos flask?

You could mix cement with that thing.......!!!

---------------------------------------------------

Polish Girl, speaking badly:-

"I'm sending the vibrator back, its defective!!!"

"Its broken all of my front teeth!!"

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply Off Topic (Score 6)
Guru

Join Date: May 2010
Location: in optimism
Posts: 4050
Good Answers: 130
#32
In reply to #30

Re: 60 hz to 50hz?

06/22/2010 11:45 PM

She doesn't seem to think it's funny - Andy

__________________
There is no sin except stupidity. (Oscar Wilde, Irish dramatist, novelist, & poet (1854 - 1900))
Register to Reply Off Topic (Score 6)
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#33
In reply to #32

Re: 60 hz to 50hz?

06/23/2010 8:49 AM

That wasn't the one!!! (She would not even need one either as she is seemingly quite a pretty lady......!)

She is not bleeding from the mouth!!!!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply Off Topic (Score 6)
Guru

Join Date: May 2010
Location: in optimism
Posts: 4050
Good Answers: 130
#37
In reply to #33

Re: 60 hz to 50hz?

06/23/2010 7:50 PM

Now you've got the 3rd sister thinking;

and contemplating what they are going to do to you;

Run Andy, run!

__________________
There is no sin except stupidity. (Oscar Wilde, Irish dramatist, novelist, & poet (1854 - 1900))
Register to Reply Off Topic (Score 6)
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#38
In reply to #37

Re: 60 hz to 50hz?

06/24/2010 6:58 AM

I get the feeling that you are not a male!!!! Am I right?

You have to learn to ignore jokes you don`t like......

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply Off Topic (Score 5)
Guru

Join Date: May 2010
Location: in optimism
Posts: 4050
Good Answers: 130
#39
In reply to #38

Re: 60 hz to 50hz?

06/24/2010 7:25 AM

Wrong again, but now I know who you've been 'taking advice from' - AND - where you've been lurking - Bad, bad, Andy!!!!

__________________
There is no sin except stupidity. (Oscar Wilde, Irish dramatist, novelist, & poet (1854 - 1900))
Register to Reply Off Topic (Score 5)
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#40
In reply to #39

Re: 60 hz to 50hz?

06/24/2010 12:42 PM

One complaint is for me a compliment, as the rest seem to either have liked it or it did not bother them either way!!

So thanks for the compliment!!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply Off Topic (Score 5)
Power-User
Fans of Old Computers - ZX-81 - New Member

Join Date: Feb 2008
Location: Beirut Lebanon
Posts: 197
Good Answers: 8
#41
In reply to #38

Re: 60 hz to 50hz?

06/24/2010 2:06 PM

Andy, 34.5

this is not the right place to revive the German-polish-Russian Rivalries.

open a new Forum and I will join it, keep this one to our dear Titan to resolve his issue with his nice sewing machine!!

cheers

__________________
dont say it, write it
Register to Reply Off Topic (Score 5)
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#42
In reply to #41

Re: 60 hz to 50hz?

06/24/2010 2:16 PM

Good move!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply Off Topic (Score 5)
Member

Join Date: Jun 2010
Posts: 6
#15

Re: 60 hz to 50hz?

06/21/2010 2:53 PM

its a sewing machine.... page 4 http://www.juki.co.jp/household_en/pism/img/tl98q/download/98pqsm.pdf is what i am referring to

Register to Reply
Power-User
Fans of Old Computers - ZX-81 - New Member

Join Date: Feb 2008
Location: Beirut Lebanon
Posts: 197
Good Answers: 8
#16
In reply to #15

Re: 60 hz to 50hz?

06/21/2010 3:12 PM

As per this catalog, the same machine can not be plugged on both 120v-60 hz or 220v-50 hz

these are 2 different units, 120V 60HZ unit part number is TL-98Q while the 5oHz 220/230V part number is TL-98P

Cheers

__________________
dont say it, write it
Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#17
In reply to #15

Re: 60 hz to 50hz?

06/21/2010 3:59 PM

Now I see what you have.

You have a very fine sewing machine here.

Reviewing the manual it appears that the only difference between the two different voltage models is the line cord plug assembly. This is not surprising since in Japan the power grid voltage and frequency will be different depending on location. So many machines are built to utilize both power distributions. I would verify this with a manufacturer's representative about my assumption before plugging the 120V model into 220V power grid though.

Now the reason that the power changes depending on which grid connection you happen to be using is that the dominant but not sole electric load is the electric motor. The motor on this model is likely an AC induction motor that gets only 100VAC after coming from your filter board assembly. In an induction motor the rotor's magnetic field is generated by inductive coupling like a transformer so there are no brushes required to connect to the rotor windings and also one less part to fail. The natural resonant speed of the motor will be related to the frequency of the AC source providing the power so the fastest speed this motor can produce will be with a 60Hz. This is part of the reason that more power will be drawn by a 60Hz usage. The compounding reason is that even though the rotor will spin faster, the amount of coupled current (to the rotor) will increase to be able to make a sufficiently large rotor magnetic field since the stator field is changing faster.

Now you may remember that I mentioned earlier that the angle between the current and the voltage will determine the real power that you use. So with a 120V and 1.4A with a 55° angle between these two you could still be producing the same real power of 95 watts.

I hope that this helps to explain what is going on here. As I said earlier, you have a very nice industrial machine with this sewing machine.

I hope that you didn't mind the gentle barbs to find out what machine you were using.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Score 1 for Good Answer
Power-User
Fans of Old Computers - ZX-81 - New Member

Join Date: Feb 2008
Location: Beirut Lebanon
Posts: 197
Good Answers: 8
#19
In reply to #17

Re: 60 hz to 50hz?

06/21/2010 10:40 PM

RedFred, Titan

I still believe the same unit rated 120V-60hz cannot be plugged into 220V-50Hz,

those are two different units.

If you get an answer from the representative, please post it here .

Titan, I add my voice to redfre

I hope that you didn't mind the gentle barbs to find out what machine you were using.

__________________
dont say it, write it
Register to Reply Score 1 for Good Answer
Guru
Australia - Member - New Member Engineering Fields - Mechanical Engineering - New Member

Join Date: Sep 2006
Location: NSW Australia
Posts: 1101
Good Answers: 23
#27
In reply to #17

Re: 60 hz to 50hz?

06/22/2010 9:16 AM

Hi Redfred,

When you read the manual did you see all the line diagrams as well?I only got script from a google translation.

If you have a link for pdf without translation I would like to see it .

Thanks Garth.

__________________
Dont get on to the roundabout if you dont know how to get off
Register to Reply
Power-User

Join Date: May 2010
Location: longo tempo dos macaco do pilas. Felizment.
Posts: 251
#18

Re: 60 hz to 50hz?

06/21/2010 5:10 PM

What device ?

Have you come from The american continent to Europe ?

__________________
I am a deeply religious nonbeliever - this is a somewhat new kind of religion. Albert Einstein
Register to Reply Score 1 for Off Topic
Guru
Australia - Member - New Member Engineering Fields - Mechanical Engineering - New Member

Join Date: Sep 2006
Location: NSW Australia
Posts: 1101
Good Answers: 23
#20

Re: 60 hz to 50hz?

06/22/2010 12:41 AM

The machine will require the same amount of wattage to run it whatever voltage you are using providing it is designed to use that voltage.

However 120V at 1.4A does not relate to 95W, so I do not see what the figures you have given have any relationship.

The power on maximum input to your motor will increase slightly when on 50Hz all other things being equal as the impeadance is lower, assuming it is a series brush motor.

__________________
Dont get on to the roundabout if you dont know how to get off
Register to Reply
Guru

Join Date: May 2010
Location: in optimism
Posts: 4050
Good Answers: 130
#21

Re: 60 hz to 50hz?

06/22/2010 12:55 AM

Whole sewing machine : 120V 1.4A 60Hz 220 to 230V 95W 50Hz

Lamp : 12V 3W (Halogen lamp)

Well, now we know it's this device - all above may be largely irrelevant as generally they use a 'universal motor' (which is frequency independent) (given such a small Hz difference).

So the power consumption "difference" is because the higher voltage enables more "amp turns" on the motor and a lesser resistance in the speed controller - so less Watts loss in the system.

So though the higher frequency brings a slight torque improvement, the lower voltage brings significantly greater losses.

Or "efficiency" in this 'device' is far more about motor and controller than Hz

__________________
There is no sin except stupidity. (Oscar Wilde, Irish dramatist, novelist, & poet (1854 - 1900))
Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#22
In reply to #21

Re: 60 hz to 50hz?

06/22/2010 1:44 AM

I'll buy that.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Power-User

Join Date: Nov 2009
Posts: 198
Good Answers: 18
#23
In reply to #21

Re: 60 hz to 50hz?

06/22/2010 2:08 AM

It cannot be a universal motor as a previous poster have already pointed out two different catalogue entries for the different voltages

__________________
Always learning
Register to Reply Score 1 for Off Topic
Guru

Join Date: May 2010
Location: in optimism
Posts: 4050
Good Answers: 130
#24
In reply to #23

Re: 60 hz to 50hz?

06/22/2010 5:19 AM

Good grief - and you got 2 votes?

"universal" is a configuration that applies to all the AC brush motors that run like a DC motor because the armature and field are frequency synchronous.

It was clear in my post, by "more "amp turns" on the motor" that the 120 Vac winding and the 240 Vac winding are different. As you cannot - to my knowledge - re-wind 'on the run' - logically they are separate motors and different controllers.

Further proof GA's misdirect.

__________________
There is no sin except stupidity. (Oscar Wilde, Irish dramatist, novelist, & poet (1854 - 1900))
Register to Reply
Power-User

Join Date: Sep 2009
Location: The asylum at the end of the road...
Posts: 143
#25
In reply to #24

Re: 60 hz to 50hz?

06/22/2010 8:49 AM

Guess parrots are a favorite breed here...

__________________
Welcome to Mariposa! We aren't on fire this week! Oh, wait...never mind...
Register to Reply Off Topic (Score 3)
Active Contributor

Join Date: Jun 2008
Posts: 17
Good Answers: 1
#26

Re: 60 hz to 50hz?

06/22/2010 9:14 AM

To the best of my knowledge, Power is function of Voltage & Current. It has nothing to do with frequency. Whereas, if frequency changes the speed of the motor. Synchronous speed of the Motor = 120*Freq. in Hz/no. of poles. So, if your equipment is of 50 Hz and you are using it in 60 Hz area then the motor speed will increase by 1.2 times (60/50). Now, the power rating of motor (HP) = 71620 * torque/r.p.m. This means that for particular motor, if r.p.m. increases, the torque reduces and power remains constant.

Register to Reply
Active Contributor

Join Date: Jun 2008
Posts: 17
Good Answers: 1
#28

Re: 60 hz to 50hz?

06/22/2010 9:20 AM

Please NOTE in my previous e-mail: Motor HP = 71620 * torque (kg.cm.) / rpm. This is same as HP = Force (kg) * velocity (m/sec)/75.

Register to Reply
Anonymous Poster
#29

Re: 60 Hz to 50Hz?

06/22/2010 9:33 AM

From the wiring diagram in the manual at the link, it appears that either 120VAC or 230VAC goes from the cord, through a filter board to a transformer. The voltage of the transformer secondary is either 22 or 19.8 volts. There could be either one multi-tap transformer that must be rewired for depending on input voltage or the machine is built with one of two different transformers depending on the input voltage.

The difference in the secondary out put voltage accounts for the difference in input power, there is simply more power available at the 120VAC input voltage due to the turns ratio of the transformer creating a higher available voltage for the motor. The motor overcurrent protection appears to be the same for either input voltage since the main control board is common to both voltages. The motor is most likely a DC motor given the low voltage and wide RPM range.

Do not plug the 120V version of this machine into 230V without doing something with the transformer, maybe you would just blow the internal fuse, or maybe you would fry the control board. Either way would not be good.

Jim

Register to Reply
Power-User

Join Date: Jun 2010
Posts: 344
Good Answers: 17
#31

Re: 60 hz to 50hz?

06/22/2010 6:56 PM

Depends.

If it has a transformer at the input, which you have to reconfigure for the different voltage, this may be a warning not to make the device consume as much when run on 230V 50Hz. The transformer will run hotter at 50 Hz, because the transformer core magnetising current is higher, and may need to run with a lower rating.

Otherwise, no idea.

Register to Reply
Power-User

Join Date: May 2010
Location: longo tempo dos macaco do pilas. Felizment.
Posts: 251
#34

Re: 60 hz to 50hz?

06/23/2010 3:18 PM

Still do not know what the device is but if the spec sheet say's it will run on these voltages it probably will maybe it is just a switch mode device.

V=I.R and W=I.V

__________________
I am a deeply religious nonbeliever - this is a somewhat new kind of religion. Albert Einstein
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#35
In reply to #34

Re: 60 hz to 50hz?

06/23/2010 4:55 PM

Sigh. This relationship is true only when the load is purely resistive with an Alternating Current (AC) source. Since this entire thread is about the power difference that happens with a change in the AC source then this law cannot be applied. Instead one should use the equation for real power of P=V*I (Bold variables are vectors) → |P|=|V|*|I|*cosφ. (φ is the angle between current and voltage.) To calculate the current one must use the complex impedance equations instead.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Score 1 for Off Topic
Guru

Join Date: May 2010
Location: in optimism
Posts: 4050
Good Answers: 130
#36
In reply to #35

Re: 60 hz to 50hz?

06/23/2010 7:31 PM

You may need some more accurate measurements for the device than the manufacturers rating plate averaged maximums too.

Perhaps the question could be; will the 3 Watt lamp be brighter or duller?

(assuming a transformer, the taps are V perfect and the iron ratio is say for 55 Hz)

(the other question, of why people comment having not read the thread, I suspect is forever un-answerable)

__________________
There is no sin except stupidity. (Oscar Wilde, Irish dramatist, novelist, & poet (1854 - 1900))
Register to Reply
Power-User

Join Date: May 2010
Location: longo tempo dos macaco do pilas. Felizment.
Posts: 251
#43
In reply to #35

Re: 60 hz to 50hz?

07/31/2010 7:03 PM

I am afraid that you have made an error.

As you say V=IR and W=IV are laws.....not theories or concepts.

You can point me in the direction of whatever internet site you want but I do not believe everything I read anyway.

Just because you introduce complex mathematics does not defeat the law of V=IR and W=IV.

All of the variables will still give V=IR and W=IV.

reactance , eddy currents and anything unknown will still be expressed as V=IR and W=IV.............It is the law and it is undefeatable at the moment by humans.

__________________
I am a deeply religious nonbeliever - this is a somewhat new kind of religion. Albert Einstein
Register to Reply Off Topic (Score 5)
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#44
In reply to #43

Re: 60 hz to 50hz?

07/31/2010 11:54 PM

I debated with myself if I should answer this. I'm still not sure I should answer your reply as I type this but I feel compelled to answer.

One of the things that I enjoy of CR4 is the open, free nature of discussions where I can learn from others who have much more experience, theoretical and practical knowledge in an engineering field than I have. I also enjoy imparting my own hard fought wisdom and knowledge in the few engineering regions that I have sufficient confidence in my knowledge.

But now you not only believe that I'm in error in the field that is my profession, you boast that any citation or argument I might come up with cannot satisfy your objections. Well I enjoy discussing and explaining my ideas with the brilliant, curious people I've found here who just happen to be ignorant on a topic I'm familiar with. I even have been humbled by those who demonstrate that they have more knowledge than I do on any field. But you have baffled me here. If you refuse to listen to any discussion here, why do you post any comment at all? Why don't you just leave us alone?

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Off Topic (Score 5)
Guru

Join Date: May 2010
Location: in optimism
Posts: 4050
Good Answers: 130
#45
In reply to #44

Re: 60 hz to 50hz?

08/01/2010 1:14 AM

I debated too, but in the end I was just so delighted that we now have no need for any concept those annoying Maxwell, Henry, Faraday, Gauss, Coulomb, Hertz, Joule, Siemens, Gibbs, Ørsted people and that damn Euclid thought up.

I guess W= I2R - falls into "too complex"

So Yea! & damn ................... - well - some algebra dude!

__________________
There is no sin except stupidity. (Oscar Wilde, Irish dramatist, novelist, & poet (1854 - 1900))
Register to Reply Off Topic (Score 5)
Power-User

Join Date: May 2010
Location: longo tempo dos macaco do pilas. Felizment.
Posts: 251
#50
In reply to #44

Re: 60 hz to 50hz?

08/01/2010 4:40 PM

I am just trying to learn.

If I am wrong then tell me why and if I think you are correct I will have learned something.

I have found that V=IR is a law ac or dc reactive / capacitive / inductive whatever.

I think I shall reply to your other comments if they continue to be of a personal nature.

I am listening to all discussion here and not refusing to listen.

I will start another topic quite happily about anything you think I am not listening to.

__________________
I am a deeply religious nonbeliever - this is a somewhat new kind of religion. Albert Einstein
Register to Reply Off Topic (Score 5)
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#53
In reply to #50

Re: 60 hz to 50hz?

08/01/2010 5:39 PM

If you read back what you originally wrote, you were not very friendly.....I think that is what sparked off the opposition.....

You must know that you are not trained/educated with regard to AC.....surely? So why jump down our throats.....? It only upsets people.....

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply Off Topic (Score 5)
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#47
In reply to #43

Re: 60 hz to 50hz?

08/01/2010 4:39 AM

You are not right in your viewpoint, sorry, but still true.

The maths are slightly different for AC......thats the law!!

Unless its a purely resistive load as Redfred mentioned......few AC loads are PURELY (100%) resistive......its usually inductance.....a coiled heater element for example.....

Motors and transformers for example have quite large and important inductances relative to the power used....

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Power-User

Join Date: May 2010
Location: longo tempo dos macaco do pilas. Felizment.
Posts: 251
#49
In reply to #47

Re: 60 hz to 50hz?

08/01/2010 4:27 PM

V=IR is a law if it's R is not 100% then the mathematics will change.

Inductance can be expressed as a voltage , current and resistance surely.

So surely V=IR will still be valid.

If not I will post a new question as I must have missed something.

Thanks.

__________________
I am a deeply religious nonbeliever - this is a somewhat new kind of religion. Albert Einstein
Register to Reply Off Topic (Score 5)
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#51
In reply to #49

Re: 60 hz to 50hz?

08/01/2010 4:51 PM

I do give credit where it is due. You very masterfully express both defiance and ignorance.

Now let me ask you a question. With your electrical and mathematic laws, how would you assemble a low pass filter using just inductors and resistors?

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Off Topic (Score 5)
Power-User

Join Date: May 2010
Location: longo tempo dos macaco do pilas. Felizment.
Posts: 251
#54
In reply to #51

Re: 60 hz to 50hz?

08/01/2010 9:59 PM

Low pass filter.

Resistor to reference and inductor to feed.

A winding will delay the high frequencies as the voltage must arrive before the current can flow introducing phase shift between the 2 components...you can achieve the same thing with "just a condenser and resistor" but you swap round the components for your reference that would be condenser to reference and resistor to feed.

Do let me know how you are getting on with fixing a fridge to a resistor to make your filter....I guess you are a bit dim...as you ask for a low pass filter using 2 components , when it gets to 3 components it gets more complex but we won't go into that as that will be way above your level of knowledge / understanding of the basics.

Now you appear to be a someone who knows everything.

But so far you have just displayed that you are not an engineer and that you know very little about anything other than avoiding questions....are you a politician by any chance ?

You are showing that you are just a bad word-smith.

I am surprised they let you use a computer...your doctor must be more careful when it comes to day release.

__________________
I am a deeply religious nonbeliever - this is a somewhat new kind of religion. Albert Einstein
Register to Reply Off Topic (Score 5)
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#52
In reply to #49

Re: 60 hz to 50hz?

08/01/2010 5:36 PM

You need to read up on AC electrics a lot more.......

Leading and lagging currents - out of phase with the voltage, wattless power etc etc etc....

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru
Australia - Member - New Member Engineering Fields - Mechanical Engineering - New Member

Join Date: Sep 2006
Location: NSW Australia
Posts: 1101
Good Answers: 23
#46
In reply to #34

Re: 60 hz to 50hz?

08/01/2010 4:04 AM

The specs that the OP gave actually relate to two different motors that can be fitted to the sewing machine.

The proposition that it is a dual voltage motor has given rise to most of this forums speculation.

__________________
Dont get on to the roundabout if you dont know how to get off
Register to Reply Score 1 for Good Answer
Power-User
Fans of Old Computers - ZX-81 - New Member

Join Date: Feb 2008
Location: Beirut Lebanon
Posts: 197
Good Answers: 8
#48
In reply to #46

Re: 60 hz to 50hz?

08/01/2010 10:29 AM

EXACTLY!!!

GA from me!!!

All these comments are nothing than speculations

The specs talk about two different models with two different motors for 2 different suply voltage....

__________________
dont say it, write it
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#55

Re: 60 hz to 50hz?

08/02/2010 5:08 AM

I thing you boys have "Bad mouthed" each other enough.

Portugal Phillip and Redfred.

We all need both of you on CR4 but for different reasons, so please just agree to not agree, OK?

No need to reply, just both stop posting right now on this particular blog please.

Hopefully something new will come up on CR4 where you are both of the same opinion!

(AND I WILL BE THE ONE WITH AN OPPOSITE OPINION AND A LOUD BAD MOUTH, AS IT WILL BE MY TURN TO BE A BIG KID!! OK???)

So please forgive me if and when that happens!!

Have a great day Guys in spite of me......

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply Score 1 for Good Answer
Register to Reply 55 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

34point5 (8); Andy Germany (9); Anonymous Poster (1); garth (3); jvrj (1); Le_Noble (7); Mrs.Rabbit (1); nitin47 (2); Phaddy (1); portugalphilip (6); redfred (10); titan01 (5)

Previous in Forum: Invertor   Next in Forum: Switchboard Closed Transition Return to Normal Power Source

Advertisement