PLC and SCADA Systems

06/21/2010 9:01 PM

Hello All,

I have Control Systems Designing background and am currently working in a process plant. While I was designing systems, we had a very simple way to integrate PLCs with SCADA in a Process Plant. I know it will annoy some people but we use to run individual dekoron cables to almost all the instrumentation, valves, switches etc from the PLC I/O cards. We never implemented any hardware interlocks. All the interlocks were in PLC. We designed systems which were very easy to troubleshoot and maintain. By looking at the PLC bit one could easily tell the wire number of a particular instrument. It was really a simple startergy we applied. I know the construction cost will be more for such a systems but the client was happy that they were saving enough money in the long term.

Now I am working for an operator of a process plant. They call it a new plant but, the systems are made too complex. There have been times when the technicians cant find the problem for days and causing unnecessary downtimes. They have implemented MODBUS for reading data from the field (not for control). But most of the times there are breakdowns related to loss of MODBUS comms. They may have saved money by not running individual cables but in that process they made the systems complex. I believe complex systems cost more in the long term.

My question is which stratergy is better in terms of saving money no matter long or short term?

Experience shared will be appreciated.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster
#1

Re: PLC and SCADA Systems

06/22/2010 12:28 AM

can You please elaborate more

Reply
Anonymous Poster
#2

Re: PLC and SCADA Systems

06/22/2010 3:11 AM

We had a Rewinder which was using the Mode bus. It was replaced with Simens ET200 distributed IO. No downtime since then.

Reply
Member

Join Date: Dec 2007
Posts: 5
#3

Re: PLC and SCADA Systems

06/22/2010 10:26 PM

Sounds interesting !! KIS - Keep It Simple is the best bet...

Appreciate more details please.

Reply
Member

Join Date: Feb 2010
Posts: 9
#4

Re: PLC and SCADA Systems

06/22/2010 10:42 PM

Hard to answer but

keep it simple is rule numer one

the smaller amount of information in one wire the easier to fault find

therefor if using any network comms of any type i.e. modbus, then you complicate fault finding...but you said this is not being used for control so why is a comms fault stopping the plant? (this to me is the question that needs answering)

on the other side of the coin you could always

improve system diagnostics to show what the real fault is...i.e. filter alarms so when plant stops due to comms fault only the comm fault alarm is shown.

good luck

Reply
Participant

Join Date: May 2010
Posts: 2
#5

Re: PLC and SCADA Systems

06/22/2010 10:55 PM

CR4 Admin: Deleted Post #5

This post was deleted because it contained advertising outside the Commercial Space forum. Please review Section 14 of the CR4 Site FAQ about advertising.

Reply
Anonymous Poster
#6

Re: PLC and SCADA Systems

06/23/2010 2:54 AM

Guest,

Perhaps if the technicians had been properly trained then the downtime would not have been so long. Proper training is typically the first thing to be cut back on, you need to look at the quality of the training and the aptitude of those being trained.

Reply Score 1 for Good Answer
Anonymous Poster
#7

Re: PLC and SCADA Systems

06/23/2010 3:02 PM

Keeping it simple is the best policy. I would advise you to have a programmer develop a life-like screen model(in color like panelview) of your process with permissives and when the systems faults, have the life-like screen model pinpoint the faulted part and area. This will make the troubleshooting a lot easier and reduce the production downtime.

Reply
Anonymous Poster
#8

Re: PLC and SCADA Systems

06/23/2010 3:57 PM

I to maintain a pollution plant that has been individually cabled and numbered to each field device ,the company has NO drawings for the system at all and yet because of the way it has been done I can find any device or fault that occurs on the system so I am very much in favour of the KIS method especially in a plant where the corrosive fumes are even eating the concrete floor.

Reply
Power-User
Engineering Fields - Control Engineering - Control Engineering Technical Fields - Education - Industrial Training Engineering Fields - Manufacturing Engineering - Manufacturing Training Engineering Fields - Electrical Engineering - Electrical engineering Training Engineering Fields - Instrumentation Engineering - Instrumentation Engineering United States - Member - New Member Engineering Fields - Energy Engineering - Become part of the larger group, change your world.

Join Date: Apr 2005
Location: Las Vegas, NV
Posts: 266
Good Answers: 1
#9

Re: PLC and SCADA Systems

06/29/2010 8:19 AM

Actually it does not matter if you have hardwired, Modbus, Devicenet or wireless sensors as far as troubleshooting time goes. (although any of the above can add to number of problems to be found. Like Modbus communication going out.)

The two primary factors in troubleshooting with a PLC is training and documentation. Using a PLC, it typically takes 5-10 minutes for a properly trained technician with discriptored ladder logic and an electrical layout diagram, to find a problem, no matter how complex the system. Time to fix varies on actual problem found.

Items that can increase troubleshooting time in order of most negative effect are ...

· Lack of proper training.

· Lack of proper PLC program documentation.

· Over complicated PLC ladder logic.

· Lack of electrical layout and schematics.

System Designs in order of most timely to troubleshoot are ...

· DCS (Mostly proprietary and designed for only OEM to use.)

· SCADA (Often proprietary, non-user friendly and training deficiencies. Seek Wonderware® and Factorytalk® training.)

· PAC (Ladder Logic easy, but function block diagram is not always, structured text is a more complex computer programming language.)

· PLC (Ladder Logic, easy for electricians and mechanics too if tought properly.)

The bottom line is that all the above systems could be easy (quick) to troubleshoot if one is constantly trained, the system is well documented and designed for the laymen to easily understand.

__________________
AB PLC Training onsite, On-Line, training software and more. BIN95.com
Reply
Power-User
South Africa - Member -

Join Date: Nov 2008
Location: Johannesburg
Posts: 295
Good Answers: 12
#10

Re: PLC and SCADA Systems

07/02/2010 1:20 AM

Hi all,

This is going to open up a huge can of worms.

There are many reasons and standards that will require the use of hardwired interlocks esd's etc.

You say that you are working in a process plant - that unfortunately does not give us much information. A refinery is a process plant - and you will not be able to get away with your current method of design in that environment.

If your drawings and documentation are up to scratch - your technicians should have no problem with the fault finding - provided they are competent in what they do.

Utilising bus systems etc is not necessarily more complex. There are many rules that govern the methods for selecting the correct bus system for the correct application, environment and the installation of this bus.

If done correctly, the amount of information that is made available from smart transmitters is invaluable and will save you many $'s in the long run.

I have come across many bus installations where they have had problems because of installation issues. In all of the cases - the people who designed the initial system had no idea what they were doing.

A bus is not evil, and neither is conventional wiring. Both have their place in the system. Sometimes they have to be combined to complete the overall system.

So my short answer to you - there is no "better" strategy. You need to understand the legal requirements of your "process" plant to determine the type of system to put in place.

Regards,

Craig

Reply
Reply to Forum Thread 10 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (5); AORAN-LCD (1); BIN95 (1); craigza (1); ellisamatt (1); Instru (1)

Previous in Forum: Float Type Level Indicator   Next in Forum: High speed actuator for Lab applications

Advertisement