If CT's are not grounded what will be the effect on the circuits.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#1

Re: CT grounding

06/22/2010 9:27 AM

If your question is about the CT secondary side grounding, this thread may help:

http://cr4.globalspec.com/thread/51469

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#2

Re: CT grounding

06/25/2010 11:06 AM

No effect, whatsoever, on the secondary circuits. CT Secondary grounding is more a safety issue rather than a functional issue.