Commissioning an LCD Panel

06/22/2010 11:53 PM

When I commissioned one LCP panel I got one problem. Can you solve? Are there any
ideas, please share with me.

The LCP module is controlling the LT MCC module which is 350mtr away from the LCP panel.The control supply of 110v Ac.LCP having potential free contacts.


So we laid the cable of C&I i.e 8pairX0.5mm each pair is covered with plastic
cover for pair no. and on the cover armour and on the armour AL paper
cover from MCC to LCP.


Previously I didn't connect armour to the earth- at the time I found
that there is voltage in the armour and there is drop in the cable up 75V.
Than I connected armour to the earth I didn't get any drop in pair cable
and also in the cable I found full 110V. But when it connected to the
coil of a contactor the coil is not picking up and voltage is dropping to
44V in the cable.

Because of this I am unable to start the motor through LCP commands.


Please share the comments

__________________
tsk
Register to Reply
Pathfinder Tags: voltage drop problem
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#1

Re: C & I commissioning

06/23/2010 12:02 AM

Try this link, you will get many answers to the effect of long control cables.

Long control cable

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Power-User

Join Date: Mar 2010
Posts: 105
#2

Re: C & I commissioning

06/23/2010 2:48 AM

Dear skumara05,

Please check up the coil voltage of the contactor to which you want

to connect 110 V line. Also check up if the contactor coil pulls in immediately or you

have to push it in manually ,if so the pick-up voltage is not enough. Will be happy to receive your reply.

Manroop.Chennai.