UAT and SAT

06/23/2010 5:01 AM

Is it necessary to provide one UAT and SAT each for Generating unit? Say example, I have 5 generating units. Do I provide SAT and UAT each??

How can we dimension UAT and SAT?

S.O.S! HELP! Before you all scold me, I googled it and found no answer.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#1

Re: UAT and SAT

06/23/2010 11:02 AM

It would help if you told us what UAT and SAT mean. Giving acronyms with no definition leads to confusion and lack of good answers. Many times acronyms are different depending on where in the world you are located.

__________________
To get the right answers, first you need to ask the right questions.
Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#2
In reply to #1

Re: UAT and SAT

06/23/2010 3:24 PM

I assumed, UAT – User Acceptance Test and SAT – Site Acceptance Test

UAT and SAT are ideally same category of tests, some people call it UAT, and other people call it SAT. These are the tests which are done to see the equipment works what they are specified for. Until this test is completed successfully, the buyer does not accept the equipment and the job is not completed. On successful completion, the buyer accepts the equipment and signs the handover certificate.

There is another important test which is done in the factory on site, generally in the presence of buyer and/or the third party appointed by the buyer. It is called FAT (Factory Acceptance Test). Until this test is passed, the equipment is not allowed to ship to the buyer.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Reply
Anonymous Poster
#3
In reply to #2

Re: UAT and SAT

06/23/2010 4:05 PM

UAT also means unit auxiliary transformer for e.g a transformer which supplies power to auxiliaries of a generator.Kindly specify clearly what do you want to know?

Reply
Anonymous Poster
#4
In reply to #3

Re: UAT and SAT

06/23/2010 11:21 PM

By UAT and SAT, I mean Unit Auxiliary Tranformer and Station Auxiliary Transformer.

Thanks everyone. Now help me.

Reply
Power-User

Join Date: Jun 2010
Posts: 348
Good Answers: 10
#5
In reply to #4

Re: UAT and SAT

06/24/2010 8:32 AM

Unit transformer, Station transformers, Auxiliary supplies, Black start transformers and Black start DG sets are there only in large power stations.

There is nothing by way of any code requirement, you can use an emergency DG set or a properly sized industrial UPS, I mean it is for the designer to selet a suitable scheme.

__________________
Knowledge sharing is a WIN-WIN situation
Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#6

Re: UAT and SAT

06/25/2010 10:46 AM

UAT is one per generating unit and SAT can be one per station of many units.

Reply