Prime power DG set

06/24/2010 1:50 AM

Is it true that prime power DG set to be loaded on average load of 70%.Why not full rated capacity

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Prime power DG set

06/24/2010 1:57 AM

For one reason, there should be some reserve capacity for starting any large motors that might be fed from the genset. This is similar to providing a safety factor for any well engineered system.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Power-User

Join Date: Jun 2010
Posts: 348
Good Answers: 10
#2
In reply to #1

Re: Prime power DG set

06/24/2010 8:12 AM

Besides that; rating of genset is in KVA and the load is in KW

__________________
Knowledge sharing is a WIN-WIN situation
Register to Reply
Power-User

Join Date: Feb 2010
Posts: 187
Good Answers: 11
#3

Re: Prime power DG set

06/24/2010 4:19 PM

check generator's kVA, p.f and kW and compare it to your load kW. Do some calculation and you will get the reason.