Cable Selection For 150A AC Drive to Motor

06/24/2010 2:45 AM

Dear all,

I selected 95 mmsq alluminium polycable make cable for 90 KW AC Drive & Motor & Distance between input MCC Panel to VFD Panel arround 60 to 70 Mtrs

cable has heated & we found that input current of VFD input side is going to 124 Amps & VFD output Side is going to 134 Amps.

Can any body give solution for same.

Register to Reply
Pathfinder Tags: automation solution
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Cable Selection For 150A AC Drive to Motor

06/24/2010 4:53 AM

→ British Standard 7671.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#2

Re: Cable Selection For 150A AC Drive to Motor

06/24/2010 9:56 AM

The cable is over heating due to harmonics.

Generally it suggested to provide an Output Reactor, if the distance between the VFD and the motor is above 30 metres.

Register to Reply
Power-User

Join Date: Jan 2009
Location: Townsville, Australia
Posts: 149
#3

Re: Cable Selection For 150A AC Drive to Motor

06/24/2010 10:54 PM

What country are you in.....? Different countries have different wiring codes, but generally speaking, the method in which the cable is run, and the type of cable employed, have a direct bearing on the current carrying capacity and indeed the volt drop.

Register to Reply
Associate

Join Date: Nov 2009
Posts: 34
#4

Re: Cable Selection For 150A AC Drive to Motor

06/25/2010 1:41 AM

In America we use HP (horse powers) for motors, not kWs. However, 90 kWts is about 120 HPs. The ampere rating of conductor depends on both power and voltage for any particular type of motor. For three phase motor we find FLC (Full Load Current) from the table in NEC (National Electrical Code). For 125 HP, 230V, 3-phase motor we have 312 Amperes of FLC. Your motor is working on different voltage, so whatever it is, multiply 312A by 230V and divide it by your voltage, and you will find your FLC. You should multiply your FLC by 125%; the result is the ampere rating of your wires. If you still have problems or questions, just let me know (my user name is my e-mail as well). It would be easier to determine wire current if I new the voltage and all about your motor. Good luck, Andrey.

Register to Reply
Commentator

Join Date: Jun 2010
Posts: 75
#5

Re: Cable Selection For 150A AC Drive to Motor

06/25/2010 3:23 AM

Hello Dear

Selecting 95 mm2 Al cable for 90 Kw motor is basically wrong. It is clear that you have not considered the derating factors that must be used to size the cable. The derating factors are: a) Ambient air temp b) Ground temp c) whether cable is laid on open racks in air or buried under ground d) whether cable is laid along with other cables in touched or speced configuration e) thermal resistivity of soil (for u/g laying) and f) depth of laying. Since you have not mentioned any of these factors in your query, I presume you have not used any of them in your cable sizing calculations. Assuming you have laid the cable under ground in touching configuration with other existing cables, my calculations tell me that you should have gone for 185 mm2 Al cable. Voltage drop is not the deciding factor here as the is distance is small. Please refer any cable manufacturer's catalogue for cable sizing.

Raina

Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#6

Re: Cable Selection For 150A AC Drive to Motor

06/25/2010 6:39 AM

Aluminium Cable of 95 mm2 will not take 150A and stay cool!

If the Cable was copper, then 190A should be maximum ( without derating for temperature etc) BUt for Aluminium, you must divide by 2 as a rule of thumb (or look in the cable rating table of the maker...). Therefore, 95A will be the max you can load the Al 95 mm2.

You are having 134A going thru ! Your Cable will Overheat whether harmonics or not!

Harmonics and wave shape: After the VFD, the shape of the voltage wave will not be sinusoidal like the mains voltage. Therefore, harmonics will appear. The length of the cable normally warants that you screen it so that it will not broadcast some high frequency voltage and interfere with other electrical cables nearby. The harmonics will contribute to the heating of the cable but if properly dimentioned, (and a choke... check with maker of VFD first if it should be recommended between the motor and the VFD...), it will not overheat the cable that much: Cable Size and being Al....

Register to Reply Score 1 for Good Answer
Anonymous Poster
#7

Re: Cable Selection For 150A AC Drive to Motor

06/25/2010 11:54 PM

while selecting cable please consider 1mm2/1A for AL cable and 1mm2/2.5A for cu cable for normal cable lengths. In ur case min size of AL able is 150 sqmm. & will be better to go for 185sq mm as derating factor is higher for bigger sizes cables

Er. Parmod Sharma,

rattanpk@ yahoo.com

Register to Reply Off Topic (Score 5)
Register to Reply 7 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); BB Raina (1); electricalexpert65 (1); LAA_Lucke (1); Normbourne (1); PWSlack (1); repnitskiya (1)