What is LCS2A clasification as defined in IEC 62271-200.
Rajesh
Pathfinder Tags: switchgear
Good Answers: 244
Re: HV Switchgear Classification
06/30/2010 3:03 PM
I think it should be LSC2A (not LCS2A). LSC is for the Loss of Service Continuity. IEC 62271-200 describes it in section 8.2.3 with the example as
"LSC2A: When accessing components of one functional unit, the other functional units of the switchgear and controlgear may be kept in service.
Example LSC2A for withdrawable designs : In practical terms, this means that the incoming HV-cables of that functional unit shall be made dead and earthed and the circuit shall be disconnected and separated (physically and electrically) from the busbars. Busbars may be kept live."
See also http://www.anie.it/browse.asp?goto=1628&livello=3&IdDocumento=34206&IdRevisione=72222
- MS
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
06/21/2022 10:38 AM
It's a typing mistake, more than anything.