Anonymous Poster

broken neutral conductor and the protective conductor

06/28/2010 2:58 PM

Can one use the voltage between the broken neutral conductor and the protective conductor

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#1

Re: broken neutral conductor and the protective conductor

06/28/2010 3:38 PM

I presume one could use this for a broken neutral detection circuit. But short of this, I do not see any way one could reasonably and safely utilize this.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
Guru

Join Date: Jul 2008
Posts: 1688
Good Answers: 145
#2

Re: broken neutral conductor and the protective conductor

06/28/2010 3:38 PM

Always best to be both legal and safe. Therefore, the best answer is "no".

__________________
Few things limit our potential as much as knowing answers and setting aside questions.
Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#3

Re: broken neutral conductor and the protective conductor

06/28/2010 3:40 PM

Do you mean using the possible potential difference between the Neutral and Earth (or Ground) due (generally) to inductive coupling, which in many (if not most) electrical systems is supposed to be bonded together and at the same potential to prevent an electric shock?

In what way and why on earth would you want to (this is totally impractical and extremely unsafe and in many circumstances can can lead to electrocution)? You cannot power an electrical appliance for free of this if that is what you are thinking!

Can you please provide more information, including your country (electrical systems vary from country to country).

__________________
jack of all trades
Reply
Guru
Engineering Fields - Environmental Engineering - New Member APIX Pilot Plant Design Project - Member - New Member

Join Date: May 2007
Location: Anywhere Emperor Palpatine assigns me
Posts: 2774
Good Answers: 101
#4

Re: broken neutral conductor and the protective conductor

06/28/2010 7:22 PM

Alright, my latest victim.....

__________________
If only you knew the power of the Dark Side of the Force
Reply Off Topic (Score 5)
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#5
In reply to #4

Re: broken neutral conductor and the protective conductor

06/28/2010 10:57 PM

Vader, you may not be that far off. Look at what some students of my alma mater have done here

If this is done in this college, i do believe MIT, CalTech, Rennselaer etc ...must be doing far more ???

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply Off Topic (Score 5)
Guru
Engineering Fields - Environmental Engineering - New Member APIX Pilot Plant Design Project - Member - New Member

Join Date: May 2007
Location: Anywhere Emperor Palpatine assigns me
Posts: 2774
Good Answers: 101
#7
In reply to #5

Re: broken neutral conductor and the protective conductor

06/29/2010 8:08 AM
__________________
If only you knew the power of the Dark Side of the Force
Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6

Re: broken neutral conductor and the protective conductor

06/29/2010 2:59 AM

Practically no. This voltage varies with imbalance currents elasewhere on the distribution network.

According to national standards, no. Such a concept is certainly outside BS7671.

Morally, no. In the event of a disconnection in the neutral upstream, the neutral-to-earth voltage rises to the full phase voltage. Therefore there is a risk of equipment damage, fire and electrocution, and therefore a risk of prosecution. No-one wants that, surely?

If in doubt, consult a qualified electrician.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856