I M: Is Power Liner Function of Current

06/29/2010 1:19 PM

I have a confusion regarding power measurement of Induction motors in industrial units. Please clarify it to me

26 KW, 400 V, 50 Hz, Y, 48.7 A, P.F 0.84, 1460 RPM.

This name plate means the motor will provide 26 KW of Mechanical power at 400 V and draws 48.7 A at Full Load and P.F will be 0.84 and Efficiency will be 91.73 %

Now what I thought about measurement system is that only current is measured. This current valu is converted into mA (4-20 mA) value and against this mA value KW are being shown in the control room.

Let take an example. (I am mentioning some values of above nameplate)

(0 A, 4 mA, 0 Kw), (9.14 A, 7 mA, 4.87 KW), (18.26 A, 10 mA, 9.75 Kw), (24.35 A, 12 mA, 13 Kw), (33.48A,15 mA, 17.87 KW), (42.61 A, 18 mA, 22.75 Kw), (48.7 A, 20 mA, 26 Kw)

(18.26 A, 10 mA, 9.75 Kw): It means when motor draw 18.26 A, transducer generates 10 mA signal and controller (PLC) show 9.75 KW against.

Now my question is that

1. Motor efficiency and P.F are the function of % of rated Load. They are different at different Loads.

2. Below 50 % of the rated load motor have Poor efficiency and P.F. Does this kind of measurement compensate for this Low efficiency and P.F?

3. Motor Power is P = 1.732 *V*I*P.F*Efficiency. Consider Voltage to be constant. if we look at above measurement approach, it take P.F and Efficiency to be constant and take the current only to be variable.

Waiting for Ur Reply

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#1

Re: I M: Is Power is Liner function of Current

06/29/2010 2:40 PM

For the power measurement, not only the current is used, but the voltage is also used as input. The Watt meter (power meter) uses both current and voltage and it shows the value of √3 x V x I x P.F from the voltage and current input values. If the transducer is used, it generates the mA corresponding to the value of √3 x V x I x P.F. If the power meter is used for measuring the motor load, it measures the motor input power, so efficiency is not a factor here.

Your concept about measuring the power ("what I thought about measurement system is that only current is measured") is not correct.

See this link for the single phase and three phase wattmeter wiring connection.

http://www.panasonic-electric-works.com/peweu/en/downloads/sf_x630_en_eco_powermeter_kw4m.pdf (see the wiring diagram at the last page)

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Associate

Join Date: May 2010
Posts: 31
Good Answers: 3
#2
In reply to #1

Re: I M: Is Power is Liner function of Current

06/29/2010 10:13 PM

Thank U very much for Reply.

Now I have a transducer "CELSA Power Transducer Type CPNV Class 0.5 4 KV" it mentions the measurment principle as follows

1. Measure the Voltage 2. Measure the Current 3. Multiply both current and Voltage 4. perform Integration on their product 5. Generate a corrosponding mA signal

Now Voltage is constant, at Low Loads (Below 50 %) motor Efficiency and P.F changes (comes down ),Now We have three varibales, current, Power factor, Efficiency. This integration could only handle variation current but not the other two

Now look at the Motor characteristics Efficiency and P.F with respect to loads. Read the first two pages

http://www.p2pays.org/ref/40/39569.pdf

Now consider the voltage is (constant) 400 V when the motor is 37.5 % load (i-e 18.26 A, 10 mA, 9.75 KW) at this stage consider motor efficiency is 75 % and P.F is 0.65 (Approximate values are taken from the graphs)

now put in the motor power formula at 18.26 A

P = 1.732*400*18.26*.65*.75 = 6.167 KW while above method will show power of 9.75 Kw.

Waiting for Ur reply

Thanks

Register to Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#6
In reply to #2

Re: I M: Is Power is Liner function of Current

06/30/2010 12:01 AM

All these steps are done within the transducer using the instantaneous power eqauation.

The average electrical power equation:

Where v(t) and i(t) are, respectively, the instantaneous voltage and current as functions of time.

T is generally considered the 1/2 cycle time period.

The transducer generates the mA corresponding to the value of P.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Associate

Join Date: May 2010
Posts: 31
Good Answers: 3
#7
In reply to #6

Re: I M: Is Power is Liner function of Current

06/30/2010 4:20 AM

What U r mentioning is the measurement of Electrical power consumed by the motor.

What I want to say about the measurment of Mechanical Power (Name Plate Mentioned power) generated by the motor.

Electrical input power is the function of Voltage, current and P.F

Output power Power of a motor (Mechanical Power) depend on another factor called Efficiency.

Simens Simocode (In LV Switch gears) measure the current of each phase and according to the current drawn they give the output power (Mechanical) of the motor.

What I think that if motor is operating below 60% load, values of Mechanical power given by Simocode have error to the actual values based on the graph in the report I mention in previous post

Register to Reply
Anonymous Poster
#10
In reply to #7

Re: I M: Is Power is Liner function of Current

06/30/2010 9:01 AM

The currents given in your first post are actual currents as measured?

The linear relationships that case are not correct. Since the pf, which is highly load dependant is not accounted for.

However the usual power transducers (active/ or reactve- both are there) work no vector multiplication of the V & I and not multiplication per se

So the output current will be proportional to power directly (electrical) - however since it is on electrical side, it can not account for the efficiency, which will be highly architectural dependant.

Register to Reply
Associate

Join Date: May 2010
Posts: 31
Good Answers: 3
#3
In reply to #1

Re: I M: Is Power is Liner function of Current

06/29/2010 10:43 PM

We are measuring the Output Power ( Mechanical) of a Motor. We are not measuring the power of a utility. The meter mentioned measures the input power (Electrical) of a motor very well but output power have a factor known as efficiency and this factor depend on the load

Register to Reply
Guru

Join Date: May 2007
Location: Geelong, Australia
Posts: 1084
Good Answers: 54
#5
In reply to #3

Re: I M: Is Power is Liner function of Current

06/29/2010 11:10 PM

I don't really understand your question but perhaps this will help.

Electrical power is (in principle) easy to measure. It's instantaneous voltage * instantaneous current. This is usually done using RMS volt * RMS current * power factor (to account for the phase difference between V & I). There are other formulas that assume constant voltage etc, no harmonics etc.

Mechanical power is a bit more complicated. It's possible to ESTIMATE the power using the electrical input, allowing for resistive, magnetic & friction losses. this usually takes the form of an "efficiency factor". Mech power = elec power * efficiency

Naturally, this is only approximate. If you really want mech power you'll need a rotary torque sensor and a tacho, then use P = 2∏RPM/60*Τ

Ask an engineer, he/she will be able to help.

__________________
If there's something you don't understand...Then a wizard did it. As heard on "The Simpsons".
Register to Reply Score 1 for Good Answer
Power-User
Belgium - Member - New Member

Join Date: May 2007
Location: Flanders (Belgium)
Posts: 343
Good Answers: 21
#9
In reply to #3

Re: I M: Is Power is Liner function of Current

06/30/2010 6:23 AM

Why not measuring the difference in speed? (no load speed against actual speed ).

The relation speed difference against mechanical output power is much more lineair than the relation current against mechanical output power.

Register to Reply Score 1 for Good Answer
Associate

Join Date: May 2010
Posts: 31
Good Answers: 3
#11
In reply to #1

Re: I M: Is Power is Liner function of Current

06/30/2010 10:06 PM

We have Simocodes (Siemens) in case of LV switch gears. In simocode there are three C.T one for each phase. There is no P.T.From all these discussion I came to the conclusion that power is not shown in the control room but the percentage of current.

If the motor take 75 % of the rated current, operator sitting there often tell us the it is operating at 74 % load which we consider that the output power of the motor is 74 % of the rated Power mentioned on the nameplate.

Thanks for Ur participation

Register to Reply
Guru
Panama - Member - New Member Hobbies - CNC - New Member Engineering Fields - Marine Engineering - New Member Engineering Fields - Retired Engineers / Mentors - New Member

Join Date: Dec 2006
Location: Panama
Posts: 4273
Good Answers: 213
#4

Re: I M: Is Power is Liner function of Current

06/29/2010 11:02 PM

Power is not going to be linear with current. From Ohm's Law, we have that V=I*Z, Z being the impedance of the motor, and the point at which the power factor enters the equation. Power is given as P= V*I, therefore P= Z* I². Power is a function of the square of the current, not linear with current.

Register to Reply
Power-User
Belgium - Member - New Member

Join Date: May 2007
Location: Flanders (Belgium)
Posts: 343
Good Answers: 21
#8
In reply to #4

Re: I M: Is Power is Liner function of Current

06/30/2010 6:19 AM

What you are saying is correct, but is has not much to do with electrical motors.

These formule is used when calculating the electrical power of one phase systems.

Register to Reply
Register to Reply 11 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); cwarner7_11 (1); ffej (1); msamad (2); rudy.leurs (2); Salar (4)