KVar Calculations

06/29/2010 10:54 PM

Dear Sir,

We have following load in our factory.

150HP Crusher motor --- o1 no.

40 HP Crusher motor --- 02 nos.

10 HP electric motor --- 06 nos.

7.5 HP electric motor --- 02 nos.

Total load connected = 305HP

Present PF = 0.46

Please suggest me the Kvar value to improve PF upto 0.99

Regards,

Sanjay

Register to Reply
User-tagged by 1 user
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#1

Re: KVar calculations

06/29/2010 11:32 PM

Refer to the generic calculation (reply # 5) from the earlier thread

http://cr4.globalspec.com/thread/54230

You should be able to calculate your particular case from there.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: KVar calculations

06/30/2010 12:04 AM

A fully loaded motor tends to have a high PF, whereas a lightly loaded motor tends to have a low PF. Your dominant crusher motors will have wildly varying loads, and hence highly fluctuating PF. The average PF might be 0.46, but if you try to correct it to 0.99, you are likely to overshoot sometimes into leading PF. This may incur some instability. Neither individual capacitors for each motor nor a conventional switching capacitor bank is likely to handle this well. However, I think it is CR4 member "marcot" who knows of a kind of fast-response capacitor scheme that could manage this. Be alert for this source of advice.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Jun 2010
Posts: 348
Good Answers: 10
#3

Re: KVar calculations

06/30/2010 12:56 AM

Total capacity 425 kvar with a 12 stage automatic relay.

__________________
Knowledge sharing is a WIN-WIN situation
Register to Reply
Power-User

Join Date: Feb 2010
Posts: 187
Good Answers: 11
#4

Re: KVar calculations

06/30/2010 2:00 AM
Register to Reply
Register to Reply 4 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Hameedullah Ekhlas (1); mountk2 (1); msamad (1); Tornado (1)

Previous in Forum: I M: Is Power Liner Function of Current   Next in Forum: Different Cables

Advertisement