Testing Of Surge Arrester

07/01/2010 11:17 AM

In testing of Lighting arrester, is it required to take the insulation resistance of LA?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#1

Re: Testing Of Surge Arrester

07/01/2010 11:25 AM

How do you intend to test it? Depending on the type, you may find that if it works correctly, you have to throw it away and buy a new one.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Reply
Power-User
Engineering Fields - Electrical Engineering - Not so new Member Popular Science - Weaponology - New Member Hobbies - Fishing - New Member, old hobby.

Join Date: Nov 2008
Location: Windhoek, Namibia, South west africa
Posts: 410
Good Answers: 23
#2
In reply to #1

Re: Testing Of Surge Arrester

07/02/2010 5:21 AM

attach +- 1m solid bare conductor to connection 1, attach hand length bare conductor to connection 2, have mother in law stand on rooftop in thunderstorm, hold on connection 2 hand-piece, lift and hold towards heaven, wait for test to occur.

__________________
tHe days of good inglisH haz wented.
Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#3

Re: Testing Of Surge Arrester

07/04/2010 9:51 PM

Guest,

Simple answer: Definitely NO.

Reasoning: Insulation resistance is tested by applying a "high" voltage DC supply (250V, 500V, or 100V) to the device and measuring the current flow. Lightning arresters use components that act like resistors until a particular voltage is reached, then they act like a short circuit while the voltage is above this threshold. Therefore, a typical insulation resistance tester will report failure. If you have a tester that can slowly ramp the applied voltage up to its rated maximum, you can graph the results and prove that a lightning arrester is working as designed.

Most people don't realize that in an AC circuit, the reported circuit voltage is its RMS or "root mean square" value. That is a weighted average that is the peak voltage divided by √2. Thus, a 120V-RMS circuit has an instantaneous peak voltage of about 120*1.414 ≈ 170V. Since the actual input voltage can vary, a safety margin is used, so the actual threshold voltage will be 190V or more. For other AC voltages, similar calculations can be used.

--JMM