Sewer Line Slope

07/02/2010 10:33 AM

Lou have a 2% slope on a pipeline. That equates to a drop of 2 ft / 100 ft, = 0.02 ft / ft, = 0.24 in. / ft; correct?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster
#1

Re: Sewer line slope.

07/02/2010 10:51 AM

Yep. One-quarter inch per foot (approximately).

Register to Reply Score 1 for Good Answer
Power-User
United States - Member - New Member

Join Date: May 2008
Location: Arizona
Posts: 355
Good Answers: 4
#2
In reply to #1

Re: Sewer line slope.

07/03/2010 10:44 AM

Good morning Guest.

So, for in the US, in the earth under the floor of a single story building, carrying the waste of 3 WC's, a urinal, and 4 lavs, in DFU's of 6, 6, 6, 2, 1, 1, 1, 1, or a total of 24 DFU's, you'd specify a 4" size, because a 3" can only support 20 DFU's, per the IMC P62, correct?

And this pipe would be 4" SDR 35 (0.120"wt), 4.215" OD PVC, at 2% slope, or 1/4" / ft, and not 4" Sch 40, 4.5" OD PVC, correct?

It seems a little surprising the industry did not just specify the Sch 40 for the extra strength it would provide, but I guess the cost differential was enough to justify this thin-wall, special OD pipe and fittings.

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Analog and Digital Circuit Design Engineering Fields - Electromechanical Engineering - Transformers, Motors & Drives, EM Launchers Engineering Fields - Engineering Physics - Applied Electrical, Optical, and Mechanical

Join Date: Jan 2008
Location: NY
Posts: 1207
Good Answers: 119
#3

Re: Sewer Line Slope

07/04/2010 3:52 PM

The numbers I've typically seen for required drain slope are :

a minimum 1/4" per foot (2%) slope for 3" diameter or smaller
a minimum 1/8" per foot (1%) slope if larger than 3" diameter

however, please verify the correct numbers with your local plumbing inspector. He should be familiar with your local code requirements and will be the one who passes or fails your installation! Local and regional codes usually start with the larger UPC/IPC standards, but many supersede them with stricter requirements.

Register to Reply
Active Contributor

Join Date: Dec 2009
Posts: 12
#4

Re: Sewer Line Slope

07/06/2010 11:21 AM

you are correct! Figures don't lie only liers figure

Register to Reply
Register to Reply 4 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); flyinghigh (1); mjb1962853 (1); Robert Laurin (1)

Previous in Forum: Highway Safety   Next in Forum: Leslie E. Robertson Associates (LERA)

Advertisement