Re: Maximum Acceptable Tan Delta Value of 132KV SF6 Circuit Breaker
07/05/2010 7:38 PM
If I recall correctly, calculating a tan-delta (or insulation power factor) value of an SF6 circuit breaker means very little, because the leakage currents (usually in microamps!) are usually so small small that even slight measurement errors cause large variation in calculated results. The better measure of condition is to compare test values between the poles of the breaker, and with values from comparable breakers.