3-Phase High KA Reading

07/04/2010 12:13 PM

I have installed an 8-way board which supplies numerous other boards, the main breaker is 100amp 3-phase mccb and at the first board I have a KA reading of 11KA on 3-phase.

1. Does the 3-phase mccb compensate the high KA reading?

2. Where do I find the charts to show the NIC EIC Inspectors?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User

Join Date: Feb 2010
Posts: 187
Good Answers: 11
#1

Re: 3-phase high KA reading?

07/04/2010 4:20 PM

what do you mean by kA reading on three phase. I could not understand well but I will tell that breaker has normal operation ampere capacity like your main breaker 100 ampere and the other is kA capacity which is for fault. We only take consideration of kA for shortcircuit calculation.

see also these about breaker ampere.

http://cr4.globalspec.com/thread/51322#comment536297

http://cr4.globalspec.com/thread/54902#comment570191

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: 3-Phase High KA Reading

07/04/2010 8:30 PM

How are you getting 11ka (11,000 amps) downstream of a 100a MCCB? What are NIC and EIC?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Power-User
Fans of Old Computers - ZX-81 - New Member

Join Date: Feb 2008
Location: Beirut Lebanon
Posts: 197
Good Answers: 8
#3

Re: 3-Phase High KA Reading

07/05/2010 1:33 AM

Are you talking about 11KA short circuit breaking capability??

if it is so, yes, 11KA BC is common for a 100A MCCB for the charts, check the breaker catalogue, you should find them there!!

__________________
dont say it, write it
Register to Reply
Associate

Join Date: Jun 2010
Posts: 34
#4

Re: 3-Phase High KA Reading

07/05/2010 2:53 AM

1- KA kiloAmps is a capacity of the electrical componants to withstand first spikes of current in the event of a short circuit for a period of 1 sec to 3 sec.

2- The value of KA depends upon the location of the componants either installed directly after the transformer or downstream for final circuits.

3- You have to include in ordering data the KA rating required for your componants according to thier location in the network. For example for a final Distribution Board at 3 phase, 415 volts the outgoing MCCBs will be acceptable if the rated for 9KA short circuit withstand for 1 sec.

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#5
In reply to #4

Re: 3-Phase High KA Reading

07/05/2010 7:54 AM

>For example for a final Distribution Board at 3 phase, 415 volts the outgoing MCCBs will be acceptable if the rated for 9KA short circuit withstand for 1 sec.<

Excuse me, but in the final distribution, one needs instant cut-off of short-circuit. Not wait for 1 sec (this 1s rating is usually required by upstream ACBs for discrimination). MCCBs are usually current-limiting, and do not have 1s rating. Final distribution is usually MCBs.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Associate

Join Date: Jun 2010
Posts: 34
#8
In reply to #5

Re: 3-Phase High KA Reading

07/06/2010 3:24 AM

Excuse me, but in the final distribution, one needs instant cut-off of short-circuit. Not wait for 1 sec (this 1s rating is usually required by upstream ACBs for discrimination). MCCBs are usually current-limiting, and do not have 1s rating. Final distribution is usually MCBs

Neither 9 KA is a tripping current nor 1 Sec is tripping time. Tripping characteristics are different to short time withstand. Final circuits are MCBs and not MCCBs as it is a typing mistake.

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#9
In reply to #8

Re: 3-Phase High KA Reading

07/06/2010 4:28 AM

i am not sure what you are trying to say here...

MCBs and MCCBs DO NOT have 1sec ratings. They are current-limiting by design. The trip time at full SC is less than 10ms. Only ACBs upstream of the whole distribution board will have a 1s rating, with an appropriately delayed trip to allow the downstream MCB/MCCB to clear the fault.

The OP is saying 11kA. Which is also non-standard.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Active Contributor

Join Date: Sep 2007
Posts: 21
#6

Re: 3-Phase High KA Reading

07/05/2010 11:02 AM

The 100 amp 3-phase mccb on the main board represents the maximum rated current of the board given the load from 'numerous other boards' - total load current should not exceed 100A. This is different from short circuit current (usually in Kilo Amperes) which represents fault current, that can flow through the circuit safely over a specified time (e.g 1 sec, etc), during which the protective device (mccb, mcb, fuse, etc) should trip and disconnect from supply.

Discrimination in selecting protective device means that a fault on downstream can be handled and trip by the downstream protective device while the upstream device is still up feeding other healthy circuits. However, if downstream device does not trip on a fault, the upstream device will then trip and cut off the supply - this could take slightly longer time e.g 1.5 secs.

Thus the 3-phase mccb's fault current rating is slightly higher than downstream mcb's.

Check time current characteristics of your selected device (mccb, mcb, fuse, etc) for charts.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7

Re: 3-Phase High KA Reading

07/05/2010 11:25 AM

<...Where..the charts to show the NICEIC Inspectors?...>

NICEIC is a trade body that assesses the competence of installation and maintenance contractors throughout the UK. It does not, routinely, assess individual installations as they are done, for that is the role of the NICEIC-accredited electrician that certifies them as safe. However, NICEIC accreditation is open to periodic review, and the assessor will want to look at a (small) number of recently-completed installations to ensure that the accreditation can remain current. A NICEIC-accredited individual or operation will issue documentation attesting that the installation was safe when they left it.

Charts may be found within British Standard 7671 and it is to the current edition of this Standard that the NICEIC-accreditation refers.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Register to Reply 9 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Hameedullah Ekhlas (1); Humayun A Chaudhry (2); kvsridhar (2); Le_Noble (1); PWSlack (1); shayre (1); Tornado (1)