MCB rating mentioned as 100AF/160AT.Please explain the AF/AT?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#1

Re: AF/AT

05/23/2010 10:24 AM

AF – Ampere Frame (Frame size of the breaker)

AT – Ampere Trip (Breaker size)

AF should be greater or equal to AT. If AF greater than AT, the breaker can be easily replaced with a higher size for future expansion.

See also

http://cr4.globalspec.com/thread/44398

http://cr4.globalspec.com/thread/36609

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply Score 1 for Good Answer
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2

Re: AF/AT

05/23/2010 12:36 PM

Just because I am a semantics stickler...

MCB is now usually used to describe a Miniature Circuit Breaker, which would not have any designation of AF or AT. Are you referring to a Main Circuit Breaker? Most people have stopped using the term "MCB" for Main Circuit Breaker because of the confusion it can now create with the introduction of Mini-CBs in North America.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#3

Re: AF/AT

05/24/2010 9:13 PM

Jraef, I am more inclined to think midharpeer means "Molded-Case Circuit Breaker" in his question. Then it would make sense, especially at this frame size.

I am puzzled, however, by a trip rating higher than the frame rating. As others have said, trip rating is standardly less than or equal to frame rating, because the trip rating is only the minimum pickup value - the breaker will take a relatively long time to trip at that point. Please, midharpeer, can you verify that you really did mean those values?

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply
Register to Reply 3 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

JRaef (1); msamad (1); PeterT (1)

Previous in Forum: Network Study   Next in Forum: Acceptable Voltage Unbalance in Transformer Secondary; While Primary Constant

Advertisement