question about Ampere Frame

04/19/2009 9:40 PM

Hi,

Is it true, that AF has its own S/C capacity ? for example :

1. 14 kA --->AF = 60,80,90,100,110

2. 22kA ---->AF = 175,200,225,250

etc..

Or there is no relationship between AF and S/C capacity. Isn't it?

for ex : AF 60,80,90,100,110 ,we can make its s/c capacity become 22kA.

tx...

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Power-User

Join Date: Oct 2008
Location: Jakarta Indonesia
Posts: 123
Good Answers: 7
#1

Re: question about Ampere Frame

04/20/2009 6:58 AM

Dear All,

There is such tendency that higher frame size has higher interuping current.

But it all depends on manufacturerer, model and type.

Every time we must check the maximum interupting current of MCCB or MCB in a catalog.

Regards

__________________
Akihito Shigeno @ JGC-Indonesia
Register to Reply
4
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2

Re: question about Ampere Frame

04/23/2009 12:28 AM

AF just means "Amp Frame". It is only used as a short hand way of describing the way a particular manufacturer has designated the frame size they chose to use for the trip value you are wanting. The trip value is referred to as "Amp Trip" or AT. Here is an example;

Siemens makes a line of breakers called the 3VL. They have several different Frame Sizes: 150A, 250A, 400A, 600A, 800A etc. If you need a 400A breaker, you can order that as a 400AT 400AF, but you can also order a 400AT 600AF, or even a 400AT 800AF breaker. All of them have 400A trip settings, but the 400AT 400AF version can never be replaced with a larger trip, because you are already at the maximum rating of that frame (400AF). If there is a chance that your application may require a larger circuit some day in the future, you can buy the 600AF 400AT breaker and if you need 500A next year, you can replace the Trip Module with a 500AT unit without exceeding the 600AF rating.

None of this has ANYTHING to do with the Short Circuit rating capacity. However, each manufacturer has economies of scale to contend with when making breakers. So when they make a 150AF breaker, there may be plenty of applications where 22kA is adequate. But in a 600AF breaker, MOST of the applications are likely ones where there will be at least 50kA available, so to avoid having to make and maintain inventory on 22kA 600A breakers that few people will buy, they only offer it in a 50kA version. There is nothing more to it than that.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 4)
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#3
In reply to #2

Re: question about Ampere Frame

04/26/2009 10:52 AM

The answer is very good (should have GA).

-MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)