07/04/2010 6:06 AM

What will happen if I use normal instrument cable instead of DYC signal cable for vortex tranmitter (between the detector and convertor remote type); Make: Yokogawa

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Anonymous Poster
#1

Re: DYC cable

07/04/2010 7:30 AM

Transmitter Will get Xploded, because of this Entire process vicinity will be in fire,if its haz area and You will be held accountable, then they will sent you to jail

Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#2
In reply to #1

Re: DYC cable

07/05/2010 12:09 AM

I don't know the exact reason why DYC cable is used for the connection between the Vortex Flowmeter and the converter but it seems this is a Yokogawa's special type (Model DYC) of instrument cable designed for the type of communication between them. I would suggest you to contact with Yokogawa for the correct reason.

See the link below:

http://www.yokogawa.cz/pdf/fl/gs1f6a0.pdf (page 2, 4 and 23)

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Reply
2
Power-User

Join Date: Nov 2009
Posts: 335
Good Answers: 63
#3

Re: DYC cable

07/05/2010 12:13 PM

The coils in a magtube need an excitation signal, which is generated in the converter. The resulting raw flow velocity signal in the magtube is a relatively low level signal, easily distorted by noise, ground loops, or electrical interference.

The converter, the electronics box, generates the excitation signal and it does the calculations on that low level raw signal to get a real-world flow rate value. The converter is sometimes mounted directly on the magtube (integral mount) or at some distance from the magtube (remote mount). Remote mounting requires wiring between the converter and the magtube.

To get an unadulterated excitation signal to the magtube and to get an unadulterated low level flow rate raw signal back from the magtube, ALL magmeter manufacturers offer a cable of specific wire gauge, capacitance and inductance ratings and specific shielding designed to provide optimal signal transfer between the converter and the magtube.

Some manufacturers publish specs on their cabling. This allows customers to provide cabling other than factory cabling that meets the factory spec. Here's a cable spec from Siemens:

Furthermore, some special functions, like "empty sensor" detection rely special cabling.

If you want factory performance from a magmeter, all the components. have to meet a factory spec.

Unless substituted wire cabling meets the factory spec, then diminished performance is the likely outcome.

Reply Good Answer (Score 2)
Anonymous Poster
#4
In reply to #3

Re: DYC cable

07/07/2010 5:31 AM

Thanks

Reply
Anonymous Poster
#5

Re: DYC Cable

07/10/2010 12:50 PM

Are you speaking of a vortex shedding, oscillating disk type flowmeter? If so, the

magnetic pickup input and ouput is very sensitive to noise.If so, the cabling should be as specified by the vendor..

Also be sure to maintain the proper twist of the cable all the way to the terminals.

Don't cut corners and be penny-wise and pound-foolish

Reply
Power-User

Join Date: Jul 2010
Posts: 136
Good Answers: 19
#6

Re: DYC Cable

07/10/2010 3:00 PM

I learned the hard way that common wiring does not provide a good signal between the flow tube and the electronics. Using the factory cable fixed all the problems seen on initial start-up.