Replacing Cables

07/05/2010 1:55 AM

Hi All, We have an existing system where we have 12 runs (4 runs / phase) of 11KV 1C x 630sqmm Al. cables laid between the source and the load. We are in the process of replacing these with copper cables of same size but 6 runs (2 runs / phase). Is 6 runs sufficient or should we go for 9 runs (3 runs / phase)?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Commentator

Join Date: Aug 2009
Posts: 91
#1

Re: Replacing Cables

07/05/2010 3:12 AM

Dear it depends on the conditions like temp depth cable formation then finally if the cable rating is safe for this option go ahead .

__________________
Correct me if i am wrong i am learner
Reply
Power-User

Join Date: Feb 2010
Posts: 187
Good Answers: 11
#2

Re: Replacing Cables

07/05/2010 5:39 AM

Engineering is based on calculation not on assumption. So, do calculation and judge.

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: Replacing Cables

07/05/2010 11:17 AM

→ British Standard 7671.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply Score 1 for Good Answer
Anonymous Poster
#4
In reply to #3

Re: Replacing Cables

07/06/2010 2:45 AM

PWSlack, Is British Standard 7671 used through out Europe and if not where would I find the european country specific equivalents. It seems that everyone always quotes BS7671 but I never see the one for Luxemburg or Denmark being quoted. Thanks in advance for you assistance.

Thomaz

Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#5
In reply to #4

Re: Replacing Cables

07/07/2010 4:33 AM

You should check the Cable ratings for copper and aluminium and compare or calculate the amp load with the cable rating tables.

IF the previous Aluminium cables were satisfactory, why do you want to change them?

As a rule of thumb, Copper has 1/2 the resistance coefficient than Alu. Therefore, the 2 run per phase should do. BUT IF the CHANGE is required because of not being satisfied with the ALU cables (were heating etc), then 3 runs will sort your problem out.

Still, re-work the calculation and use the cable rating tables from the cable maker.

Reply
Commentator

Join Date: Jun 2010
Posts: 75
#6

Re: Replacing Cables

07/07/2010 8:08 AM

Hi!

Please furnish the details of load and laying of cables. How you propose to lay the cable.

BB Raina

Reply
Member

Join Date: Jun 2010
Location: chennai
Posts: 8
#7

Re: Replacing Cables

07/08/2010 1:06 AM

ADOPT THE RELEVENT STANDARDS and apply the de-rating factor and you can arrive at the solution

Generally copper cable can carry 1000 Amps/Inch.Square and aluminium Cable can carry 625 Amps/Inch.Square (One Inch Square is equal to 645 Sq. MM) and arrive at the cable cross section required and choose the requirement. Then the relevent DE-RATING FACTOR TO BE APPLIED ON THIS VALUE and increase the cable size or run.

This excercise should solve your doubt and problem

sdr710

Reply
Reply to Forum Thread 7 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); BB Raina (1); Hameedullah Ekhlas (1); ikhanuk (1); LAA_Lucke (1); PWSlack (1); user-deleted-15 (1)

Previous in Forum: Capacitor KVAR Rating   Next in Forum: Power Transformer
You might be interested in: Patch Cables and Cords, Flat Cables, Computer Cables

Advertisement