Check My Math Please

07/07/2010 4:16 PM

So, I'm designing this gizmo that continually ignites oil well flares with a 30,000V spark from a HV coil. The control card (proprietary) fires the coil for 0.5 sec every 5 sec. The Card itself along with the associated circuitry draws 300ma when not firing. When firing total amperage is 3A. The entire package operates on solar power with a charge controller and battery for those pesky times when the sun goes down. Assuming 10 Hrs. of darkness I need to size the Amp/Hr capacity of the battery. So;

3*0.5/36000 + 0.3(32400)/36000 = 0.27 avg. amps

Capacity = amps * time

0.27 * 10 Hrs. = 2.7 Amp/Hrs

Did I miss much?

__________________
"Do not worry about your difficulties in Mathematics. I can assure you mine are still greater". - Albert Einstein
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Hobbies - RC Aircraft - New Member Hobbies - Automotive Performance - New Member Hobbies - DIY Welding - New Member

Join Date: Jul 2007
Location: Fort Lauderdale Florida
Posts: 5708
Good Answers: 123
#1

Re: Check My Math Please

07/07/2010 4:53 PM

Yes. Based on your math, your battery would be dead at sunrise. And the battery will lose a small amount of it's power every hour. By the 9th hour, your battery would be too low to power the charge. If you are designing a system, start with overkill, and delete when you are sure it produces no use. IMHO, I would use a group 31 battery designed for solar charging. good luck.

__________________
Bob
Register to Reply
Guru
Hobbies - Musician - Engineering Fields - Chemical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Instrumentation Engineering - New Member

Join Date: Jan 2007
Location: Moses Lake, WA, USA, Thulcandra - The Silent Planet (C.S. Lewis)
Posts: 4216
Good Answers: 194
#2

Re: Check My Math Please

07/07/2010 5:14 PM

Hi RR,

I approached it this way:

The draw is 3A firing 0.5s/5s or 10% of the time.

The draw is 0.3A the rest (4.5s/5s = 90%) of the time. This becomes (3)(0.1) + (0.3)(0.9) = 0.57A draw average.

So, for 10 hrs you need a 5.7 A-hr. battery. (I think).

Mike

__________________
"Reason is not automatic. Those who deny it cannot be conquered by it. Do not count on them. Leave them alone." - Ayn Rand
Register to Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#3
In reply to #2

Re: Check My Math Please

07/07/2010 5:28 PM

RDGRNR,

Yes, you badly missed something. You did the average over an hour (36000 seconds) but you didn't count the total number of 3A cycles throughout the hour. You can do average ampere calculation using either an hour or 5 seconds period. Here the calculations are for both cases:

(1) Over the hour (36000 seconds) period:

Total number of 3A pulse in an hour = 36000/5= 7200

Average current = (3*0.5*7200)/36000 + (0.3*32400)/36000 = 0.3 + 0.27 = 0.57 A

(2) Over the 5 seconds period:

There will be only one 3A pulse in 5 seconds and 0.3A for rest of 4.5 seconds

Average current = (3*0.5)/5 + (0.3*4.5)/5 = 0.3 + 0.27 = 0.57 A

Ampere-Hour for 10 hours = 0.57 * 10 = 5.7 AH

For both cases, the average ampere is same. The final unit should be AH (Ampere-Hour), not Amp/Hrs. This is the AH the flare ignition system will consume during the dark time. When you select the battery capacity in AH, select at least 50% more of this requirement.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Guru
Hobbies - Fishing - New Member

Join Date: Jun 2008
Location: Raleigh, NC USA
Posts: 13529
Good Answers: 468
#6
In reply to #3

Re: Check My Math Please

07/07/2010 6:09 PM

I just pulled out my calculator and it says there is 3600 seconds in an hour.

__________________
Those who would give up essential Liberty, to purchase a little temporary Safety, deserve neither Liberty nor Safety. Ben Franklin
Register to Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#7
In reply to #6

Re: Check My Math Please

07/07/2010 6:51 PM

Yes, you are right. In fact, the calculation (1) has been done for 10 hours period (36000 seconds). The calculation can be done using any time interval which is multiples of 5 seconds. However, 5 seconds calculation is simpler though. The result will be same all the times.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Guru
Hobbies - Fishing - New Member

Join Date: Jun 2008
Location: Raleigh, NC USA
Posts: 13529
Good Answers: 468
#11
In reply to #7

Re: Check My Math Please

07/08/2010 7:02 AM

Sorry, I was drinking and feeling really smart. Thanks for taking it easy on me.

__________________
Those who would give up essential Liberty, to purchase a little temporary Safety, deserve neither Liberty nor Safety. Ben Franklin
Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#4

Re: Check My Math Please

07/07/2010 5:53 PM

Also... the number of sun hours varies greatly by location. Make sure you have enough capacity for the worst case scenario... and that there will be enough sun hours to charge the batteries during the time available to do so.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru
Hobbies - DIY Welding - Don't Know What Made The Old Title Attractive... Popular Science - Weaponology - New Member United States - US - Statue of Liberty - 60 Year Member

Join Date: Apr 2009
Location: Yellowstone Valley, in Big Sky Country
Posts: 7425
Good Answers: 295
#5

Re: Check My Math Please

07/07/2010 6:00 PM

Others have worked the math.

I have an observation: "Assuming 10 Hrs. of darkness..." As my pessimistic nature kicks in, I wonder if that might be better as ten hours of usable light? Maybe less.

[edit] I see North of 60 voiced a similar opinion. Didn't mean to step on you.

__________________
Semper Ubi Sub Ubi
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Analog and Digital Circuit Design Engineering Fields - Electromechanical Engineering - Transformers, Motors & Drives, EM Launchers Engineering Fields - Engineering Physics - Applied Electrical, Optical, and Mechanical

Join Date: Jan 2008
Location: NY
Posts: 1207
Good Answers: 119
#8

Re: Check My Math Please

07/07/2010 10:52 PM

I would approach the problem more conservatively:

8 [hours] good sun
16 [hours] not enough sun
Use only 50% of battery capacity to extend life.
Assume 75% efficiency for all other conversions.

0.3 [A] x 0.90 + 3 [A] x 0.10 = 0.57 [A] average current

0.57 [A] x 16 [hours] / 0.50 = 18.2 [A-hours] battery capacity needed

Solar panels must be large enough to supply charge current AND ignitor current during sun hours.

Assuming a 12 [Volt] system...

Solar power needed to charge battery

12 [V] x 0.57 [A] x 16 [hours] / 8 [hours] / 0.75 = 18.2 [W]

Solar power needed to run ignitor

12 [V] x 0.57 [A] / 0.75 = 9.1 [W]

Average solar panel output during an 8 [hour] sunny day should be at least 30 [W].

Good Luck!

Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#9

Re: Check My Math Please

07/08/2010 5:35 AM

You have had many suggestions in the maths and etc.

In all cases, when you reach a conclusion about the exact required AH for the next 14 hrs or 16 hrs of darkness, double the battery capacity (at least) and make sure that the solar panel has enough power to run the Gizmo and charge the battery to full.

You can only draw 1/2 what you put into the battery (normally).

Register to Reply
Guru

Join Date: Aug 2005
Location: Hemel Hempstead, UK
Posts: 5826
Good Answers: 322
#10

Re: Check My Math Please

07/08/2010 6:20 AM

Mikerho has provided the easy way to look at the total current drain: it's 3A for a tenth of the time and .3 Amps for the rest of the time, about 0.6 Amps average (ignoring the sort of overlap which he has accounted for).

Lots of people have pointed out the foibles of batteries.

I'm more worried about your short estimate of night time. The best scenario from your point of view is having the equipment at the equator: 12 hours daylight, and 12 hours night. Any other part of the world you might get longer days in the summer, but, you also get shorter days/longer nights in the winter.

__________________
If you spend all your time looking for people and things to complain about: trust me, you will find plenty to complain about.
Register to Reply
Guru
Engineering Fields - Instrumentation Engineering - New Member

Join Date: Dec 2009
Location: San Antonio, TX USA
Posts: 844
Good Answers: 29
#12

Re: Check My Math Please

07/08/2010 8:17 AM

Thanks for the attention! FYI; I had already chosen a 30W BP Solar, a 26 AH Powersonic sealed LA Batt. and an ASC charge contoller. Test phase underway.

__________________
"Do not worry about your difficulties in Mathematics. I can assure you mine are still greater". - Albert Einstein
Register to Reply
Guru

Join Date: Feb 2008
Location: Large hole formally occupied by furry woodland creature.
Posts: 3385
Good Answers: 97
#13
In reply to #12

Re: Check My Math Please

07/08/2010 10:03 AM

Would the light from the flare produce any output from a solar panel?

Just asking,,,,,

__________________
CRTL-Z
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Analog and Digital Circuit Design Engineering Fields - Electromechanical Engineering - Transformers, Motors & Drives, EM Launchers Engineering Fields - Engineering Physics - Applied Electrical, Optical, and Mechanical

Join Date: Jan 2008
Location: NY
Posts: 1207
Good Answers: 119
#14
In reply to #12

Re: Check My Math Please

07/08/2010 10:33 AM

I believe you are on the right track and some empirical testing should confirm operation at your location.

Probably too costly and not worth the effort (you have to run the numbers on your end), but what about using the waste heat and a thermoelectric generator to augment the solar panel and battery backup?

Register to Reply
Active Contributor

Join Date: Jun 2010
Posts: 10
#15

Re: Check My Math Please

07/08/2010 1:36 PM

RDGRNR,

I am very interested in your project. Are you an end user or are you designing this product for the oil and gas industry? I would be interested in speaking with you. You can reach me at ***-***-****. My name is Andy.

---

Comment edited: It's probably not wise to leave your phone number on a public forum. One of you should private message the other to obtain contact info.

CR4 Admin

Register to Reply Off Topic (Score 5)
Guru
Engineering Fields - Electrical Engineering - Analog and Digital Circuit Design Engineering Fields - Electromechanical Engineering - Transformers, Motors & Drives, EM Launchers Engineering Fields - Engineering Physics - Applied Electrical, Optical, and Mechanical

Join Date: Jan 2008
Location: NY
Posts: 1207
Good Answers: 119
#16
In reply to #15

Re: Check My Math Please

07/08/2010 2:05 PM

Andy,

FYI, there is a private mail response option you should be able to use to contact the OP (or any other registered poster) to exchange contact information. Click on a username and look for a "Send username a Message" icon near the upper right corner of the new window.

While none of the "regulars" here would abuse the contact information you post publicly, there are many unregistered opportunistic surfers and bots which might cause you grief.

Register to Reply Off Topic (Score 5)
Active Contributor

Join Date: Jun 2010
Posts: 10
#17
In reply to #16

Re: Check My Math Please

07/08/2010 3:49 PM

Great information. Thank you!

Register to Reply Off Topic (Score 5)
Register to Reply 17 comments
Copy to Clipboard

Users who posted comments:

Andy@E&MSales (2); bob c (1); Doorman (1); kramarat (2); LAA_Lucke (1); Mikerho (1); mjb1962853 (3); msamad (2); North of 60 (1); Randall (1); RDGRNR (1); Unredundant (1)

Previous in Forum: Factors Affecting V/F Ratio   Next in Forum: Variable Speed Step Motor

Advertisement