Distance One Can Use for 4-20 mA Source

07/08/2010 12:50 PM

i want to carry 4-20ma signal around 75 meters to the PLC input

i plan to use 1.5 mm2 shelded cable is it will work ok ? i want to conform as other case i will loose the money for cable.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Instrumentation Engineering - New Member

Join Date: Dec 2009
Location: San Antonio, TX USA
Posts: 844
Good Answers: 29
#1

Re: distance one can use for 4-20 ma source

07/08/2010 1:08 PM

The answer is probably yes, but you could have been a little more specific regarding the transmitter type, PLC type, process---Gees---ANYTHING!

__________________
"Do not worry about your difficulties in Mathematics. I can assure you mine are still greater". - Albert Einstein
Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Jul 2010
Posts: 12
#3
In reply to #1

Re: distance one can use for 4-20 ma source

07/09/2010 11:09 AM

Dears

thanks for the fastest and strong teachnical backround help provided i am really feel happy seeing such a strong talents

i am using 5v to 4-20ma tranducer as i am going to mesure 1500A through Ct and send feed back to S7200 ( 224Xp) AI feedback

in manual of S7200 it stated internal resistence used 250 ohms so as support provided it must work

Register to Reply
2
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Distance One Can Use for 4-20 mA Source

07/08/2010 1:33 PM

It depends upon the overall loop resistance, including the input resistance, and the supply voltage.

Example:

If the Loop voltage is, oh, say 24.0VDC then the maximum loop resistance is 24VDC/20mA which is......<tap, tap, tap>.....er.....1200Ω.

The 1.5mm2 cable 75m long will have a there-and-back resistance of, oh, say a maximum of 5-10Ω, so that means if the PLC input resistance is below 1190Ω then everything will be just fine. Many PLC alnalog inputs will be rather less than this.

And if it isn't, then just turn the supply volts up until it is.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Good Answer (Score 2)
Anonymous Poster
#4
In reply to #2

Re: Distance One Can Use for 4-20 mA Source

07/10/2010 12:33 PM

I agree with your calculations.Most plc's designed for 4-20 milliamp inputs also have 250 ohm input resistance, to conform with the 4-20 milliamp, 1-5 volt standards.

GA for you.

Register to Reply
Member

Join Date: Oct 2010
Posts: 6
Good Answers: 1
#5

Re: Distance One Can Use for 4-20 mA Source

10/30/2010 11:18 AM

Yes it will go till 1000 meters

Register to Reply
Register to Reply 5 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); Fareed1974 (1); kailash (1); PWSlack (1); RDGRNR (1)

Previous in Forum: Pressure Measurement   Next in Forum: Measuring Contact Electrical Resistance (MIL-DTL- 81706)
You might be interested in: Utility Meters, Cable Laying Services, Flow Meters

Advertisement