Anonymous Poster

Clearance in Terminal Box of Motor

07/09/2010 1:12 AM

Could you please inform me about line to line and line to earth clearance in terminal box for HV (6.6kV) motor. Also please inform me the reference standard (IEC/IEEE).

Regards

Jaswant

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#1

Re: Clearance in Terminal Box of Motor

07/09/2010 7:44 AM

3 Inches Phase to Earth and 5 inches Phase to Phase as per BS 116-1952.

Reply Score 1 for Good Answer
2
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#2
In reply to #1

Re: Clearance in Terminal Box of Motor

07/09/2010 1:57 PM

For 6.6 to 6.9 kV motors, the minimum distance between the line to line terminals is 6 inches and line terminal to ground is 4 inches.

Reference: NEMA MG 1, Section 4.19.2.2: Terminal Housings for Large AC Motors.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Reply Good Answer (Score 2)