Full Load Copper Loss

07/09/2010 2:30 AM

Dear Sirs,

Can somebody please tell me the amount of " Full Load Copper Loss in KW" taking place in a Stanford make alternator of a 625 KVA Cummins DG Set?

Or is there any method by which we can calculate it?

Your help would be highly appreciated

Thanking You

Regards,

Rooney

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Full Load Copper Loss

07/09/2010 5:53 AM

Stanford can give that. Please telephone Stanford directly with the serial number of the alternator and ask for technical assistance.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User
Fans of Old Computers - ZX-81 - New Member

Join Date: Feb 2008
Location: Beirut Lebanon
Posts: 197
Good Answers: 8
#2

Re: Full Load Copper Loss

07/09/2010 8:08 AM

Only manufacturer can give you this data, check the alternator datasheet, or contact Stamford,

__________________
dont say it, write it
Register to Reply
2
Associate

Join Date: Mar 2009
Posts: 51
Good Answers: 4
#3

Re: Full Load Copper Loss

07/10/2010 4:23 AM

Below are the Formula for Alternator Losses:

You should have the necessary data to do the calculations:

The losses of the alternator are determined at various values of current I(alt) and alternator speed n. These losses consist of the copper, iron, bearing and windage losses. Following are variables affecting each of these losses:

The copper losses are affected by the change in temperature of the alternator which in turn affects the winding resistance R. The two terms in Equation (2) for the iron losses refer to the losses in the stator teeth and in the flux return-path, respectively. The flux-density in each of these two parts is Bt and Br. The bearing loss in Equation (3) is also a function of the rotor weight which can be calculated from the physical parameters of the alternator. The windage loss in Equation (4) is additionally a function of the physical parameters of the rotor.

Register to Reply Good Answer (Score 2)
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#4

Re: Full Load Copper Loss

07/10/2010 7:11 AM

Simply put:

Copper loss = losses due to the pure resistance of the copper wires in the winding, with the current flowing through them.

Cu losses = Resistance x I²

Since the temperature affects the resistance value, then you need to measure that resistance for each phase after running the unit at near full load for some time to stabilise the temperature, then measure each phase to neutral resistance. Then multiply that value by the square of the full load current in each phase (don't forget the √3 when getting the current value (unless on name plate). Then add the 3 values to obtain the watts... This is the nearest you can get on site without any sophisticated set up.

Otherwise get the info from the maker of the Alternator (the supplier of the set or OEM could do the same from a certificate test sheet in his possession usually).

Register to Reply
Power-User
Belgium - Member - New Member

Join Date: May 2007
Location: Flanders (Belgium)
Posts: 343
Good Answers: 21
#5
In reply to #4

Re: Full Load Copper Loss

07/10/2010 7:24 AM

You have to measure the winding resistance with a 'four wire' ohm meter ...

Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#6
In reply to #5

Re: Full Load Copper Loss

07/10/2010 6:28 PM

Rudy,

You are correct. I did not go into the details of how to measure very small resistance values because this will entail some knowledge of the delicate procedures to avoid substantial errors at these levels.

The OP could use a DC voltage source and measure the current flow then calculate the rsistance value of a phase winding. But then he should already be familiar with the topic. my object was to indicate what was meant by copper losses. there is also the losses in the field windings which I forgot to point out...

In any case he better get the values from the OEM or Manufacturer of the Alternator. They will probably give him a standard value of the losses for serially produced Alternators...

Thanks for pointing out.

Register to Reply
Register to Reply 6 comments