How to Charge the Spare Single Phase Main Transformer

07/09/2010 2:55 AM

I am using three single phase transformers as main step up transformer in a generating station. the forth single phase transformer is kept as spare. I think to keep ready the spare transformer i have to keep chagred its one winding so that the moisture will not enter in the insulating oil. what are methods to kept the winding charged continously.

Please suggest.

Sony

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: How to chrage the spare single phase main transformer

07/09/2010 3:34 AM

The question doesn't make sense yet. Transformers are, in the simplest of terms, coils of wire. They don't store charge; they convert AC power from one voltage to another. Please add more material to the question and re-post.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
3
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#2

Re: How to Charge the Spare Single Phase Main Transformer

07/09/2010 7:39 AM

Assuming that this spare transformer is not in service, you may short circuit the LV terminals and then apply a low percentage voltage to the HV so that some current flows in the windings and the windings and the oil are kept warm. Please monitor the LV current while doing this and do not exceed the rated LV side current. This is one way of drying out the transformer.

Reply Good Answer (Score 3)
Guru
United States - Member - Member Engineering Fields - Electrical Engineering - Electrical Construction

Join Date: Apr 2010
Location: Mid Western USA - The Corn Belt
Posts: 1439
Good Answers: 58
#4
In reply to #2

Re: How to Charge the Spare Single Phase Main Transformer

07/09/2010 8:37 AM

I concur with electricalexpert65. We have been doing this for years at the power plants where we have maintenance contracts.

GA to you sir!

__________________
The first 5 days after a weekend are always the hardest................................
Reply
Member

Join Date: Jun 2010
Location: chennai
Posts: 8
#5
In reply to #4

Re: How to Charge the Spare Single Phase Main Transformer

07/11/2010 1:16 PM

Dear Mr. KJK/USA,

This matter does not relate to this thread. Since I saw your name here and I did not have your mail Id., I did not know your mail to contact you.

The matter is that about 3 or 4 weeks you responded to my problem of restoring the CR4 DATA BASE, in CR4, and I could not retrieve, as suggested by you and I do not know at what step I made mistake.

Pl. suggest me how to retrieve the Data Base of my original link in CR4.

How to contact the MODERATOR, I searched different options nothing could succeed.

Please reply to me at sd610@rediffmail.com.

dhayanandhan

Reply
Power-User

Join Date: Mar 2010
Posts: 105
#3

Re: How to Charge the Spare Single Phase Main Transformer

07/09/2010 7:53 AM

Dear Guest,

your question is the least informative as Mr.Slack has pointed out.Please

clarify the following points :

(1) Moisture will not enter if the unit is filled with Ins.Oil , silica gel is good,and no

leakage thro' the bushing ,if stored in a good ventilated area. It will be a good

practice to megger the transformer before putting it on service.

(2) If you still insist connect a low voltage AC power with proper tripping fecility

and short circuit the secondary, limiting the secondary current to the full load

current. Take extra precautions like- no one will change the AC input voltage

with out proper authorisation.

(3) I feel if your place is utilisation is rainy always , more humid ( sea shore), or any

leaky roof above you can be worried.

Reply
Reply to Forum Thread 5 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

electricalexpert65 (1); KJK/USA (1); manroop (1); PWSlack (1); user-deleted-15 (1)

Previous in Forum: Full Load Copper Loss   Next in Forum: Continued 33kV Cable Fault

Advertisement