Voltage Unbalance - Alternator

07/12/2010 3:09 AM

Hi All,

We are manufacturing different Ratings of LV Alternators (5 kVA to 1010 kVA), we are struggling with one peculiar Problem of Generated Voltage Unbalance – This is 3 Phase STAR Connected Alternators.

We have done following -

1. The Phase Voltages of all 3 Phases are balanced.

2. The Line Voltages are unbalance by 4 Volts.

3. The Phase Angle of the Voltage Vectors measured as 0,119 & 240°.

4. The Total Harmonic Distortion Measured as Phase A - 1.5 %, Phase B - 1.3 % & Phase C -1.2 %.

5. We have Cut Opened the Armature Windings (Main Stator) to check the Basic Winding Specifications (No of Conductors, No of Turns etc) – All found OK.

We suspect following –

1. Can this Happen due to the Pitch Error of the Armature Stamping.

2. Can This Happen because of the Damper Winding Circuit of the Field ( Main Rotor) not Short Circuited Properly – e.g some blow Holes in the Brazed Joints of Damper Bar & Damper Lamination.

Please help..

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster
#1

Re: Voltage Unbalance - Alternator

07/12/2010 8:17 AM

How can you say phase voltages are balanced and line voltages are varied? In delta connection of stator/armature.

Register to Reply Score 1 for Off Topic
Guru
Panama - Member - New Member Hobbies - CNC - New Member Engineering Fields - Marine Engineering - New Member Engineering Fields - Retired Engineers / Mentors - New Member

Join Date: Dec 2006
Location: Panama
Posts: 4273
Good Answers: 213
#2

Re: Voltage Unbalance - Alternator

07/12/2010 11:53 PM

It would appear that you have slightly more resistance in one of the windings than in the other windings. Since you are star connected, I am assuming what you are referring to as "Line Voltages" are measured line to ground. A further clue is the slight difference in the phase angles. I would suspect the connections first- most likely at the common ground point. If as is common, you have each phase built from multiple windings in series, the connections between the windings can also cause such symptoms.

You need to check the resistance of each winding- use a four wire measurement technique for good measurements at low resistance. You also should measure the inductance of each winding.

It is also possible that you have some faulty insulation on one of the windings. You can look at the windings with a TDR, which will tell you if you have any impedance changes in the winding, and where such impedance changes occur.

Register to Reply Score 1 for Good Answer
Anonymous Poster
#4
In reply to #2

Re: Voltage Unbalance - Alternator

07/13/2010 11:27 AM

How line voltage is measured between line to ground ?it should be line to line know?

Register to Reply
Guru
Panama - Member - New Member Hobbies - CNC - New Member Engineering Fields - Marine Engineering - New Member Engineering Fields - Retired Engineers / Mentors - New Member

Join Date: Dec 2006
Location: Panama
Posts: 4273
Good Answers: 213
#6
In reply to #4

Re: Voltage Unbalance - Alternator

07/13/2010 5:51 PM

There is some ambiguity in terminology, and not being an electrical engineer, I may have it backwards.

In your star connection, you have three (assuming three phase power) sets of series-connected windings all connected on one end to a common point, which is your ground reference, and is generally connected to earth ground, and the load is connected to the free ends of each set, either in combination or between the end point and ground. It is the voltage between the end point of each series of windings and the common connection point of the three sets that I refer to as "line" voltage, and that is the measurement that seems imbalanced from the information you have provided. Here is a picture of a simple star configuration using only three windings:

Note that normal "neutral" connection for the return of each single phase is through the common point on ground. If you draw a vector diagram with your measurements, using your line voltage measurement and phase angle measurements, then inscribe a circle through the end points of the vectors, you will find that the center point no longer coincides with the center point of the vectors. The center point of the circle will have shifted toward or away from one of the end points of the vectors. This means that you do not have equal impedance (resistance plus inductance) in the three phases. Drawing the vector diagram will help you understand what the real issue is with the imbalance, and where to look.

Register to Reply
Commentator
India - Member - New Member Engineering Fields - Electrical Engineering - New Member Technical Fields - Technical Writing - New Member

Join Date: Dec 2009
Location: India
Posts: 68
Good Answers: 4
#7
In reply to #2

Re: Voltage Unbalance - Alternator

07/14/2010 12:08 AM

Dear All,

Thank you very much for the Great Response.

I would like to clarify -

This is STAR connected Alternator - Neutral Open ( Floating - Not Connected to Earth) - The Line Voltages are the Voltages measured LIne to Line & the Phase Voltages are the Voltage between Phase & the Neutral.

We have Measured the Resistances of each phase winding it is 40.02 milli Ohms Balanced for all Phases. We have also carried out the Impedance Matching Test with the Test Voltage of 2.5 kV ( Alternator Rated Voltage is 415 Volts), the Impedances are same.

Would also like to specify -

The Stator Laminations are not segmented - (48 Slots in the Main Stator Lamination).

It is 4 Parallel Path, Double Layer Lap Winding wound for 4 Pole (2 Pole Pairs) Design, No of Conductors in the Slot are ODD - 35-30-35-30 in sequence.

I suppose these would be as per your requirements.

Meanwhile we are also doing some experiments, I will post the observations as measured..

Register to Reply
Power-User

Join Date: Mar 2010
Location: BHOPAL, INDIA
Posts: 201
Good Answers: 20
#8
In reply to #7

Re: Voltage Unbalance - Alternator

07/14/2010 11:53 AM

Based on the information furnished, the possibility of error caused due to difference in slot pitches of various slots in core lamination seems to be higher. Are you staggering the laminations while core building? if not then staggering may eliminate the problem. You may also like to measure the voltages of various parallel paths and find the difference if any particular path is generating higher / lower voltage.

Register to Reply Score 1 for Good Answer
Anonymous Poster
#3

Re: Voltage Unbalance - Alternator

07/13/2010 8:12 AM

Good answer from Panama.

Register to Reply
Power-User

Join Date: Mar 2010
Location: BHOPAL, INDIA
Posts: 201
Good Answers: 20
#5

Re: Voltage Unbalance - Alternator

07/13/2010 2:41 PM

Kindly furnish further details of the generator Specially the following:

Type of stator core segments (full circle or part segments)

Overlap of the sore segments if it is part segment core.

Number of parallel path, number of pole, type of winding, turns per slot, Voltage of generator.

I may be able to help you after getting this information.

Register to Reply
Commentator

Join Date: Jul 2010
Location: South Windsor, CT USA
Posts: 67
Good Answers: 2
#9

Re: Voltage Unbalance - Alternator

08/02/2010 10:23 PM

Is this loaded or unloaded, do you have 3 phase voltage sensing

Register to Reply
Register to Reply 9 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!