3 Phase to 1 Phase Transformer

07/11/2010 1:33 PM

Three phase to single transformer is used in UPS as a bypass supply where load current mentioned in Y phase is twice the current of R & B phases (both are equal). What type of connection is this? Primary is shown as Delta.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: 3 Phase to 1 Phase Transformer

07/11/2010 4:19 PM

Your post is a little hard to understand. You say the primary is delta. It realy does not matter. What is needed is

1. What is the secondary voltage?

2. The secondary could be wye or delta. Which is it?

3. What is the load current normally on the UPS?

Register to Reply
2
Power-User

Join Date: Oct 2008
Location: Jakarta Indonesia
Posts: 123
Good Answers: 7
#2

Re: 3 Phase to 1 Phase Transformer

07/11/2010 8:27 PM

Dear all,

Refer to EES 027 and 027.1 to see a "3 phase in 1 phase out" Transformer connection.

www.akihito-shigeno.com/files/EES_E026_030.zip.

Regards

__________________
Akihito Shigeno @ JGC-Indonesia
Register to Reply Good Answer (Score 2)
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#3
In reply to #2

Re: 3 Phase to 1 Phase Transformer

07/11/2010 9:50 PM

Your documents are very good - well answered with the vector diagram and calculations. GA from me.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#4
In reply to #2

Re: 3 Phase to 1 Phase Transformer

07/11/2010 10:46 PM

Excellent information. GA !

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Off Topic (Score 5)
Power-User
Fans of Old Computers - ZX-81 - New Member

Join Date: Feb 2008
Location: Beirut Lebanon
Posts: 197
Good Answers: 8
#5

Re: 3 Phase to 1 Phase Transformer

07/11/2010 11:54 PM

this is a "Open Delta " connection

http://cr4.globalspec.com/thread/55606,

I started a thread about 3 to 1 phases transformer and I got very helpful comments, you can check

__________________
dont say it, write it
Register to Reply
Power-User

Join Date: Oct 2008
Location: Jakarta Indonesia
Posts: 123
Good Answers: 7
#6
In reply to #5

Re: 3 Phase to 1 Phase Transformer

07/12/2010 12:31 AM

Dear all,

Yes, it is a sort of open delta connection.

Normally, open delta is used 3 phase to 3 phase conversion using two 1 phase transformers.

The subject of this thread is a 3 phase to 1 phase transformer, and the secondary connection is inverted against primary. This connection is not same as 3phase-3phase open delta.

Regards

__________________
Akihito Shigeno @ JGC-Indonesia
Register to Reply
Power-User
Fans of Old Computers - ZX-81 - New Member

Join Date: Feb 2008
Location: Beirut Lebanon
Posts: 197
Good Answers: 8
#7
In reply to #6

Re: 3 Phase to 1 Phase Transformer

07/12/2010 10:11 AM

Open Delta connection could also be used for single phase application at secomdary,

you have to calculate the correct ratio of the transformers.

I already use it, and current distrubution over the 3 phases at primary is 1-2-1

Regards

__________________
dont say it, write it
Register to Reply
Participant

Join Date: Jul 2010
Posts: 4
#8
In reply to #7

Re: 3 Phase to 1 Phase Transformer

07/12/2010 11:04 AM

Do you mean Scott connection? If so, the further question is: How do we provide earth fault protection? Simply sum up all three phases to get residual current as earth fault?

Register to Reply
Power-User
Fans of Old Computers - ZX-81 - New Member

Join Date: Feb 2008
Location: Beirut Lebanon
Posts: 197
Good Answers: 8
#9
In reply to #8

Re: 3 Phase to 1 Phase Transformer

07/13/2010 6:27 AM

No

Scott configuration output is 2 phases 90 deg phased and more complicated

Just an Open Delta

for the earth fault current you can earth one end at the secondary side and use any usual fault detection method

__________________
dont say it, write it
Register to Reply
Participant

Join Date: Jul 2010
Posts: 4
#10
In reply to #9

Re: 3 Phase to 1 Phase Transformer

07/13/2010 10:14 AM

when input is balanced, opendelta output will be showing zero volt isn't it? Does this transformer adopt different voltage ratios for different phases in order to achieve output voltage across open delta? How do you explain Y phase current is double of other two phase currents on primary side? In such cases, how do we adopt earth fault protection? Will the summation of all three phases in primary be still zero? Because, primary currents will be displaced by 120 degree. In order to make sum of three currents to zero, R & B phase currents should be co-phasal and 180 degree out of phase to Y phase current. Can I get a vector diagram?

Register to Reply
Power-User
Fans of Old Computers - ZX-81 - New Member

Join Date: Feb 2008
Location: Beirut Lebanon
Posts: 197
Good Answers: 8
#11
In reply to #10

Re: 3 Phase to 1 Phase Transformer

07/13/2010 11:26 AM

http://cr4.globalspec.com/thread/55606,

Check this thread, I initiated an I got valuable replies from forum members.

there you will find answers to your questions

__________________
dont say it, write it
Register to Reply
Participant

Join Date: Jul 2010
Posts: 4
#12
In reply to #11

Re: 3 Phase to 1 Phase Transformer

07/13/2010 11:44 AM

Dear Le_Noble, Thanks a lot for the reply. It clears my doubt... output is V connection and not open delta. Because, open delta calls for three phases which means sum is zero under balanced condition. Here it is two phases so sum is Line voltage. Now the question remains ... how to provide earth fault protection for the primary side when branch point of Y phase (middle phase) connection is not accessible outside.

Register to Reply
Register to Reply 12 comments