THHN Conductors and Cable Trays

07/12/2010 10:08 AM

Can I install electrical Conductors THHN in cable trays?. I read NEC and din't find that specification. Thank you for your attention..

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Instrumentation Engineering - New Member

Join Date: Dec 2009
Location: San Antonio, TX USA
Posts: 844
Good Answers: 29
#1

Re: THHN Conductors and Cable Trays

07/12/2010 10:50 AM

I routinely do. NEC will guide you as to capacity.

__________________
"Do not worry about your difficulties in Mathematics. I can assure you mine are still greater". - Albert Einstein
Register to Reply
Anonymous Poster
#4
In reply to #1

Re: THHN Conductors and Cable Trays

07/12/2010 1:46 PM

Thank you.

Register to Reply
Power-User
United States - Member - New Member

Join Date: Aug 2008
Location: KY, USA
Posts: 367
Good Answers: 18
#2

Re: THHN Conductors and Cable Trays

07/12/2010 1:28 PM

Table 392.3(A) covers types of cables and conduits that can be run in trays in most locations. This table mostly lists multi-conductor cables and communications cables. (No THHN.)

Article 392.3(B)(1)(a) of the NEC covers the use single-conductors in cable trays In Industrial Establishments:

(1) Single Conductors. Single-conductor cables shall be permitted to be installed in accordance with (B)(1)(a) through (B)(1)(c).
(a) Single-conductor cable shall be 1/0 AWG or larger and shall be of a type listed and marked on the surface for use in cable trays. Where 1/0 AWG through 4/0 AWG single-conductor cables are installed in ladder cable tray, the maximum allowable rung spacing for the ladder cable tray shall be 225 mm (9 in.).

Article 392.11(B) covers ampacities of single-conductor cables in cable trays. Article 392.11(C) deals with mixing multi- and single-conductor cables in a cable tray.

__________________
The most valuable of all talents is that of never using two words when one will do. ~Thomas Jefferson
Register to Reply Score 1 for Good Answer
Member

Join Date: Jul 2010
Posts: 5
#5
In reply to #2

Re: THHN Conductors and Cable Trays

07/12/2010 1:51 PM

I'm in Latin America. We use NEC like excellent guide. I'm using NEC 1999. I'll get NEC 2008. Thank you very much.

Register to Reply
Power-User
United States - Member - New Member

Join Date: Aug 2008
Location: KY, USA
Posts: 367
Good Answers: 18
#6
In reply to #5

Re: THHN Conductors and Cable Trays

07/12/2010 2:14 PM

Glad to offer some advice. Welcome to CR4

__________________
The most valuable of all talents is that of never using two words when one will do. ~Thomas Jefferson
Register to Reply
Member

Join Date: Jul 2010
Posts: 5
#3

Re: THHN Conductors and Cable Trays

07/12/2010 1:43 PM

Thank you for valuable attendance.

Register to Reply
Associate

Join Date: Jun 2010
Posts: 34
#7

Re: THHN Conductors and Cable Trays

07/13/2010 3:08 AM

You can't install THHN wires in cable tray or exposed, in other words exposed to mechancial injury. you can lay it in a closed containment like conduits or cable trunkings.

Register to Reply
Member

Join Date: Jul 2010
Posts: 5
#8
In reply to #7

Re: THHN Conductors and Cable Trays

07/13/2010 9:10 AM

I read specifications THHN 4/0 Phelps Dodge is for cable tray (CT) use. I suppose with cable tray installed out of mechanical injury.

Register to Reply
Active Contributor

Join Date: Sep 2006
Posts: 15
#9

Re: THHN Conductors and Cable Trays

07/13/2010 1:12 PM

NO...........Not in cable tray single conductor THHN, it needs to be run in a seperate tray as a power conductor in a multiconductor cable , or shields put in as the same as keeping them seperated from the HV(480) and 24vdc plc or DCS cables . I have seen some plants that have done this (due to the older multiconductor cable shorting out as a temporary (bandaid fix) to keep the process going, after hours of determing which conductor was bad in the cable. It is certainly not an engineering pratice by any means. Conduit and THHN is the only way to go. Always pull extra when you do pull it, and think of future needs. As far as I am concerned thats should be in any country.

Register to Reply
Member

Join Date: Jul 2010
Posts: 5
#10
In reply to #9

Re: THHN Conductors and Cable Trays

07/13/2010 1:37 PM

According NEC 2005 Section 392.11(B) a group of single conductors installed in triangle or square config. can be used. But your observation and recommendation are very important./p]

Register to Reply
Register to Reply 10 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); EElectrician (2); Humayun A Chaudhry (1); HxlA (4); Jak_Flash (1); RDGRNR (1)

Previous in Forum: High Reactive Power Import While Connected to Grid Resulting in Decreasing V?   Next in Forum: DTC Torque and Power
You might be interested in: Cable Trays, Cable Laying Services, Cable Bus Systems

Advertisement