Previous in Forum: Ammonia Storage Horton Spheres   Next in Forum: Flexible Tubesheet for S&T Exchanger
Close
Close
Close
8 comments
Rate Comments: Nested
Active Contributor
Jordan - Member -

Join Date: May 2008
Location: Jordan
Posts: 11

Fan Coil Unit

07/13/2010 9:38 AM

Hi, what is the difference between air handling units and fan coil units, and why in some chilled water AC systems they connect the AHU to a FCU?

__________________
All men dream,but not equally,Those who dream by night in the dusty recesses of their minds,wake in the day to find that it was vanity:but the dreamers of the day are dangerous men,for they may act on their dreams with open eyes,to make them possible
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Fan Coil Unit

07/13/2010 4:48 PM

I'm not sure that terminology is the same everywhere. In my experience, AU (air unit) is synonymous with FCU (fan coil unit), "coil," or "evaporator." Such a unit usually controls (and is controlled by temperature), and the RH (relative humidity) of the room "floats" according to the coil size and the chilled fluid temperature within the tubes.

An AHU (air handling unit) typically incorporates more features, such as preheat, reheat, air mixing from external supply, or air exhaust. Such units can be capable of controlling (and being controlled by) both room temperature and RH.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Anonymous Poster
#2

Re: Fan Coil Unit

07/13/2010 5:57 PM

A FCU is nothing more than a radiator; coils of tubing separated by fins in an enclosure. It is used with a supply of chilled water The FCU is inserted into the air stream of a ducted ventilation system. A thermostat control valve adjusts the flow of chilled water. An air handler (AHU) is a self contained unit that contains a FCU, a heat unit and a circulating fan or blower. It has connections for chilled water and hot water and is controlled by thermostatic valves. Both types are used onboard ships and can be used commercially.

Register to Reply
3
Guru

Join Date: Jun 2008
Location: Oman
Posts: 612
Good Answers: 14
#3

Re: Fan Coil Unit

07/13/2010 11:47 PM

FCU is the smaller version of AHU . In AHU you can carry out many process of psychrometry but in FCU mostly we can carry out cooling and dehumidification or heating. You can install FCU with or without duct. Individual control is flexible in FCU. Generally FCUS are used in hotels and other similar places. IT can be of DX type or chilled water type. Limited filter application in FCU.

Register to Reply Good Answer (Score 3)
Active Contributor
Jordan - Member -

Join Date: May 2008
Location: Jordan
Posts: 11
#5
In reply to #3

Re: Fan Coil Unit

07/14/2010 2:56 AM

Hi sir, depending on what you said may i say that FCU can be used insted of the split unit? and for what "must likely" AC loads can i use the FCU?

__________________
All men dream,but not equally,Those who dream by night in the dusty recesses of their minds,wake in the day to find that it was vanity:but the dreamers of the day are dangerous men,for they may act on their dreams with open eyes,to make them possible
Register to Reply
Guru

Join Date: Jun 2008
Location: Oman
Posts: 612
Good Answers: 14
#6
In reply to #5

Re: Fan Coil Unit

07/14/2010 5:22 AM

For small rooms ( such as rooms in hotels where each room has to be provided with independent On/Off control, prevention of transmission of noise, transmission of odors etc) for the indoor unit of the split a.c we have fan coil unit. IN FCU coil and fan unit all assembled in a compact casing. Electric two way solenoid valve or three way diverting valve is provided on the chilled water supply line to the coil. As I already mentioned we cannot carry out many psychrometric process in FCU due to its limited space. In such cases AHU is preferred. For example operation theater of a Hospital needs special air treatment ( HEPA filters), there FCU cannot be used. Generally it is used for small room comfort applications and not for process applications.

Register to Reply
Power-User

Join Date: Apr 2010
Location: Where no man should ever live
Posts: 195
Good Answers: 6
#4

Re: Fan Coil Unit

07/13/2010 11:49 PM

In tradesman language in America a fan coil usually can refer more to an individual room air conditioner, heating and/or cooling, as is seen in many hotel rooms and some offices.

An air handler might be something that is more used for distribution of air. It would likely have air conditioning features the same as a fan coil, but be connected to terminal units in the spaces served through ducts and connectors.

__________________
Who is so ignorant as not to know that knights-errant are beyond all jurisdiction, their only law their swords, while their charter is their mettle and their will is their decrees? Don Quixote
Register to Reply
Associate

Join Date: Dec 2007
Posts: 42
Good Answers: 1
#7

Re: Fan Coil Unit

07/14/2010 10:42 AM

AHU - Air Handling Unit, FCU - Fan coil Unit.

Generally for higher capacities for more functions they named as AHU, For lower capacities for lesser function they named as FCU ( It may be Ductable split indoor unit or for Chill Water System).

Gererally the capacities given in terms of Air Flow rate( cfm, cmh, lps).

For example say less than 2000 cfm, named as FCU. It will vary depend upon the Manufactures.

Register to Reply
Power-User

Join Date: Feb 2010
Posts: 103
Good Answers: 2
#8

Re: Fan Coil Unit

07/14/2010 11:37 AM

A fan coil unit is actually an air handling unit although normally smaller in size. They both have a fan and coils inside a casing. Fan coil units are usually 1,000 CFM of air capacity and smaller but some can exceed this. Air handling units are available in about any capacity you might need and available in many configurations and supplied with many different attributes. The particular application being considered will determine which catalog you reach for.

Register to Reply
Register to Reply 8 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); Coldspot (1); lolomechanic (1); Lou Bindner (1); maglak (1); mrswamy (2); Tornado (1)

Previous in Forum: Ammonia Storage Horton Spheres   Next in Forum: Flexible Tubesheet for S&T Exchanger

Advertisement