Different Capacity of DG Synchronization

07/14/2010 11:44 AM

I have 4 nos of 750, 1030 x2 nos and 1 no 1500 KVA LT Generators. Can it be synchronized in auto to share the load for better utilization and fuel cost?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Different Capacity of DG Synchronization

07/14/2010 11:47 AM

Yes, if they are all the same voltage, frequency, phase rotation, and phase angle (synchronized.)

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Anonymous Poster
#2

Re: Different Capacity of DG Synchronization

07/14/2010 11:51 AM
Register to Reply
Guru

Join Date: Sep 2008
Posts: 706
Good Answers: 32
#3

Re: Different Capacity of DG Synchronization

07/15/2010 10:18 AM

Assuming that your control system can handle the synchronization and maintaining the running in parallel there is a question of load sharing to keep in mind as well as the applied load. It would not be economical and fuel efficient if your applied load wasn't sufficient to keep all units at least at 75% capacity for example. Running at reduced capacities on all the units would be fuel inefficient. It would be better to remove a unit or two to maintain the running units at or near their full loads for best efficiency and keep a unit warmed up and ready to start and parallel for peak periods.

__________________
Spinco
Register to Reply
Power-User
Engineering Fields - Power Engineering - New Member

Join Date: Nov 2009
Location: Abuja, Nigeria.
Posts: 126
#4

Re: Different Capacity of DG Synchronization

07/16/2010 1:31 PM

Yes U can, but all the generators must be very healthy and able to speak the same language of equal frequency, equal voltage, equal PF and same phase sequence.

The issue of utilization and fuel saving depend on the healthy nature of the generators and how the automatic controlling function responds to increase and decrease load demand. Usually the controller will start up and switch in more generators during increase load demand. During off pick periods, the controller shots down some of the generators and place them on stand by.

The above can also be done manually.

DICKSON

__________________
There is peace in silence and achievement in plans.