3 Paralleled Units Run Smooth - Adding 4th Creates Instability

07/15/2010 9:32 AM

A system has four 336 kW natural gas gensets A, B, C and D operating grid parallel.

Grid import set at 100 kW.

Load varies around 800 kW + 150 kW

With drop add percentages and building load are selected so that 3 units A, B and C run, the result is a very smooth balance grid/DG as defined by grid import steady = 100 kW.

Here is the problem:

With drop add percentages and building load are selected so that all 4 units run, the result is a widely swinging grid import level. The value of grid import runs wild. For example at every second sample time we see -15 kW to 0 kW to 65 kW to 5 kW to 45 kW 110 kW to 140 kW to 70 kW to etc. etc.

Also during the above 4 unit scenario the PF of the generator bus also runs wild from -0.98 to -0.4 to past 0 to 0.4 to 0.9 to etc. etc.

We have only seen the above fluctuations when "D" is the 4th generator to come on to the bus.

An upcoming test will let another generator, say "A" be the forth generator to come onto the bus.

The paralleling equipment is the Cummins Digital Master Control and the generator controllers are 3100.

Any early thoughts as to if the problem is the control system causing the fluctuations or if it may be a problem with generator D controls?

One link that I liked is below.

http://cr4.globalspec.com/thread/57066/Alternators

for paralleling 2 or more

1- RMS line voltages must be equal
2- The generator to be paralleled must have the same phase sequence. If the phase sequence is different, then even though one pair of voltages is in phase the other two pairs of voltages are 120 degree out of phase. If the generators were connected in this manner there would be no problem with phase a but huge currents would flow in phases b and c damaging both machines.
3- Generator output phase angles must be the same
4- The oncoming generator must have a slightly higher operating frequency as compared to the system frequency. This is done so that the phase angles of the incoming machine will change slowly with respect to the phase angles of the running system.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User
Fans of Old Computers - ZX-81 - New Member

Join Date: Feb 2008
Location: Beirut Lebanon
Posts: 197
Good Answers: 8
#1

Re: 3 Paralleled Units Run Smooth - Adding 4th Creates Instability

07/15/2010 12:34 PM

it is clear you have problem with your PCC3100 controller, try to exchenge with another gen set and see if the problem move from D to the other genset B/R

__________________
dont say it, write it
Reply
Power-User

Join Date: Jun 2010
Posts: 348
Good Answers: 10
#2

Re: 3 Paralleled Units Run Smooth - Adding 4th Creates Instability

07/16/2010 2:46 AM

Keeping aside the fact that all units have to undergo commissioning tests prior to putting in service, my advice is to carry out routine site tests on that particular unit, check the continuety of neutral earth conductor and provide for stand-alone (dummy) load testing.