Anonymous Poster

Earth and Neutral

07/15/2010 9:29 AM

What is the standard resistance value between the neutral and earth?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United States - Member - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Jul 2008
Posts: 1149
Good Answers: 36
#1

Re: Earth and Neutral

07/15/2010 9:45 AM
Reply
Guru

Join Date: Jan 2010
Posts: 2446
Good Answers: 60
#2

Re: Earth and Neutral

07/15/2010 10:43 AM

depends on the cable used and the lenth.

and where the earth is bonded to the nuetral wire in the installation

Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#3

Re: Earth and Neutral

07/15/2010 3:27 PM

It varies depending on local electrical regulations, but should be clearly indicated in your local electrical standards and regulations which (given the likely nature of the question) you should be working to.

As for the standard resistance, it seriously depends on where you take the measurement. A common standard resistance of 0.0 ohms should be present when measuring across the earth-neutral link bar of a residential home switchboard on a MEN electrical system when testing to AS/NZS 3000.

__________________
jack of all trades
Reply
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#4

Re: Earth and Neutral

07/16/2010 12:20 AM

There is NO standard value of resistance between neutral and earth. It can be infinite to ZERO, depending on what you mean. (Dry sand is used in some fuses, just because of its high isolation). Somehow you will need to get some moist earth, a little below the surface.

A generator can be used without grounding or earthing the neutral - .

If you refer to codes, it is different from code to code and also different whether you apply safety fault current switching gear or not, and the set point (value) of these.

Here in our house 7 ohms or less is what the code says.

With very sensitive fault disconnects in some parts of the world 100 ohms and more is allowed. (0.2mA - 0.5 mA).

But with such sensitive gear your loads must have a very good isolation, or they trip.

__________________
Plenty of room here
Reply
Member

Join Date: Jul 2010
Location: India
Posts: 8
#5

Re: Earth and Neutral

07/16/2010 3:24 AM

The standard resistance value between the neutral and earth should be zero

.It accaptable maximum upto 0.4 ohm

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6
In reply to #5

Re: Earth and Neutral

07/16/2010 4:46 AM

<...maximum upto 0.4 ohm...>

Not true for an IT earthing system; it could be megohms!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Member

Join Date: Jul 2010
Location: India
Posts: 8
#7
In reply to #6

Re: Earth and Neutral

07/16/2010 6:03 AM

Can you tell more about IT earthing system.

I don't understand,how it could be megaohms ?

Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#9
In reply to #7

Re: Earth and Neutral

07/18/2010 3:57 PM

Not every country uses the same earth and protection scheme.

Have a look at the following link as it explains IT (isolated earth) nicely and simply.

http://en.wikipedia.org/wiki/Earthing_system

__________________
jack of all trades
Reply
Guru

Join Date: Jan 2010
Posts: 2446
Good Answers: 60
#8
In reply to #6

Re: Earth and Neutral

07/16/2010 6:58 AM

i take you mean for anti static purposes

Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#10

Re: Earth and Neutral

07/20/2010 10:04 AM

It depends upon the method of system earthing. In solid earthing it should ideally be zero.