VVVF Controlled Motor Tripping

07/16/2010 12:11 AM

Dear all

One of our cement mill separator motor 430 v 415 kw Delta connected VVVF controlled (ABB ACS 800) motor Tripping the reason showing unbalance.

ACS 800 having two nos of inverter module, we tested with one by one (separately) module then the motor running without any problem

If it with two inverter the problem is showing again anybody having any experience same these situations? Please be advice to us

With Regards

jcg

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: VVVF Controlled Motor Tripping

07/17/2010 12:59 AM

Based on your information it is ACS800 multidrive with two inverter module.

Does it show number of inverter causing current unbalance?

Check DC link votage going to Inverter Module a difference of few volt can also cause the problem.

Regards

Bharat

Register to Reply
Active Contributor

Join Date: Feb 2010
Posts: 24
#6
In reply to #1

Re: VVVF Controlled Motor Tripping

07/19/2010 7:26 AM

DC link voltage is same

I will give some more details of the drive

ACS800-04-0870-3+E205+V991

Inverter

Input U 513...587 VDC

I 889 ADC

Output U 3 ˜ 0...415 V

I 741 A

f 0...300 Hz

Line converter

Input U 3 ˜ 380...415 V

I 630 A

f 48...63 Hz

Output U 3 537.....587 Vdc

I 764 ADC

With regards

jcg

Register to Reply
Anonymous Poster
#2

Re: VVVF Controlled Motor Tripping

07/17/2010 9:30 AM

Maybe you can check ACS800 setting.

Register to Reply
Power-User
Engineering Fields - Petroleum Engineering - Rig Electrician United States - Member - the Oil Patch Engineering Fields - Power Engineering - Drives & Gen's Engineering Fields - Instrumentation Engineering - Drive Control Popular Science - Cosmology -

Join Date: Jan 2010
Location: Houston off/on-shore @ Oil Patch
Posts: 223
Good Answers: 2
#3

Re: VVVF Controlled Motor Tripping

07/17/2010 9:37 AM

if running with an encoder check it, try running open loop (without the encoder) and see if you get a trip

__________________
Why do they make manhole covers round? so they won't fall in [before asking "Who is John Galt?"]
Register to Reply
Anonymous Poster
#4

Re: VVVF Controlled Motor Tripping

07/18/2010 10:31 PM

Your both the drive units are individualy running ok, means the control going to both the Drives through APBU (DDCS Branching unit) may be the problem OR Optical cable missing the signal.

Thanks,

sukhvinder singh

JK-PAPER LTD, RAYAGADA

Register to Reply
Active Contributor

Join Date: Feb 2010
Posts: 24
#5
In reply to #4

Re: VVVF Controlled Motor Tripping

07/19/2010 3:01 AM

We replaced a working APBU from other units but the problem is showing again (tripping happening after some time of the motor running only )

With regards

JCG