Ring Main

07/19/2010 10:22 AM

Dear All

For 11KV feeders we have open ring main system and each feeder is provided with earthfault & overcurrent protection .In addition to this each section of the cable between ring main unit is provided with earth fault indicator(EFI). recently it is observed during fault at substation only Over current relay operted and at same time EFI operated up to the end cable is healthy.In this case I want to know why earth fault relay not operated at the substation. In most of the case cause for fault is cable being damaged by construction companys. In this case without damaging the cable armour(which is earthed) it is not possible to short curcuit the conductors. So why earth fault relay is not operating & EFI indicator operating ?

Rgds

Byju

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Ring Main

07/20/2010 3:36 AM

The problem can only be solved by local observations and testing.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#2

Re: Ring Main

07/20/2010 4:09 AM

As said by #1, observation of the site/fault will be essential to solve the question.

Also, the over-current will operate first if the fault condition to earth was not happening quicker and first:

if the cable damage happened in a way that the conductors shorted 1st, before the path to earth was fully established, then the over-current will trigger 1st. Then the earth fault would not have materialized.

Just a possibility...

Register to Reply
Commentator

Join Date: Mar 2009
Posts: 57
#3
In reply to #2

Ring Main

07/20/2010 1:20 PM

Dear Mr.Lucke,

Thanks for your reply. I have one more doubt. How the EFI indicator connected to the cable?. Will it operate during phase fault???.

Rgds

Byju

Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#4
In reply to #3

Re: Ring Main

07/20/2010 4:34 PM

EFI = Earth Fault Indicator ?

If yes, in your question you seem to have said that this did not operate! (Or I did not understand your english properly). I don't have a diagram of the connection of this EFI but as its definition suggests, it must be connected on the earth return line to detect an earth fault current only. Phase to phase fault will not normally trigger it unless the same fault produced an earth leakage current at the same time.

Register to Reply
Commentator

Join Date: Dec 2009
Location: Jakarta 12130 Indonesia
Posts: 76
Good Answers: 1
#5

Re: Ring Main

07/24/2010 9:02 AM

I assume the wiring is correct. Earth fault & EFI has a different CT (different input current) respectively.

Check the Current Transformer for Earth Fault. Is it Residual Connection or Current Balance Current transformer.

Please check the Over Current Relay and Earth fault current ampere setting and time setting. If the OCR time setting is faster than Earth fault protection, then the earth fault wil not operate because the fault already cleared by OCR.

If your EFI and earthfault has the same input current and the same relay please disobey this information, then the problem is in the relay.

__________________
RSM Elect Specialist
Register to Reply Score 1 for Good Answer
Register to Reply 5 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

byjuram (1); LAA_Lucke (2); PWSlack (1); rasam.syamsudin (1)

Previous in Forum: Power Consumption   Next in Forum: What Impact Will 2.6 MW Solar Have On My Demand Charge?

Advertisement