Cable Selection for Feeder

07/20/2010 2:50 AM

Pl. suggest cable size calculation for underground cable feeder from power utility to plant in desert area.

Plant load of 25 MVA, feeder route length 5 KM, System volatge 33 KV? and suggested future margins in selected cable size

__________________
When was last time you did something for first time.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#1

Re: Cable Selection for Feeder

07/20/2010 8:05 AM

Please referv to Cable Manufacturers' Catalogues. Apply all de-ration factors. Also, give due consideration to Voltage Drops. Also, ensure the short time withstand rating of the cable.

Register to Reply
Power-User
India - Member - New Member

Join Date: Jul 2010
Location: India
Posts: 162
#2
In reply to #1

Re: Cable Selection for Feeder

07/20/2010 8:31 AM

Dose there exist standard for permissible voltage drop in feeder.

__________________
When was last time you did something for first time.
Register to Reply
Anonymous Poster
#3
In reply to #2

Re: Cable Selection for Feeder

07/20/2010 9:37 AM

Yes! Please refer to IS 1255.

Register to Reply
Commentator

Join Date: Jun 2010
Posts: 75
#7
In reply to #2

Re: Cable Selection for Feeder

07/22/2010 12:23 AM

Normally it is taken as 5-10%.

BB Raina

Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#4

Re: Cable Selection for Feeder

07/20/2010 12:39 PM

Happy

We don't like to do the work for the engineer. Do the following

1. Convert the load to amps from the info 25 MVA and 33 kv

2. Select a MFG for your cable

3. Select a cable based on the amperage requirements

4. Calcullate the VD using this cable to determine if it meets your requirements. If not

5. Select a bigger cable and repeat #4

I would like to see you work so please post it for us to see

Register to Reply Score 1 for Good Answer
Anonymous Poster
#8
In reply to #4

Re: Cable Selection for Feeder

07/22/2010 10:17 AM

How do you do

About item#2, please clarify "MFG" summery.

Kindest regard

AMIR

CR4 Admin – E-mail Address Removed

From the Site FAQ: Do not post phone numbers or email addresses. The CR4 Admin will delete all phone numbers posted in threads or comments, and we strongly urge you not to put up email addresses.

Register to Reply
Power-User
Fans of Old Computers - ZX-81 - New Member

Join Date: Feb 2008
Location: Beirut Lebanon
Posts: 197
Good Answers: 8
#10
In reply to #8

Re: Cable Selection for Feeder

07/24/2010 12:18 AM

Hi Amir,

Are you in Iraq?

If so, please write me a private message on this forum, I can help

thanks

__________________
dont say it, write it
Register to Reply
Commentator

Join Date: Jun 2010
Posts: 75
#5

Re: Cable Selection for Feeder

07/21/2010 7:17 AM

2X 630 mm2 Al cable runs per phase based on certain assumptions on derating factors short circuit time duration. This should suffice. You may like to check and come back and share with us your findings.

BB Raina

Register to Reply
Power-User

Join Date: Feb 2010
Posts: 187
Good Answers: 11
#6

Re: Cable Selection for Feeder

07/21/2010 8:01 PM

wareagle has given you an excellent comment please also consider the ambient temperature and the cable's max.operating temperature. There must be high temperature than normal places.

Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#9

Re: Cable Selection for Feeder

07/22/2010 11:08 AM

MFG = manufacturer of the cable

Register to Reply
Commentator

Join Date: Aug 2009
Posts: 91
#11

Re: Cable Selection for Feeder

07/24/2010 7:46 AM

Hi

1- Load current

2- all derating factors llike depth , temp , grouping ---

3- this will give you an approx cable rating for cable size

4- check voltage drop across cable

5-check short ckt capability for cable

make 2 sets of cable if permitted

rgds

__________________
Correct me if i am wrong i am learner
Register to Reply
Participant

Join Date: Feb 2010
Posts: 1
#12

Re: Cable Selection for Feeder

07/30/2010 9:30 AM

25MVA? 33KV? This sound like a major job. But to ask here listening to random answers with question like what is "MFG" is really mind boggling

Register to Reply
Register to Reply 12 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); BB Raina (2); electricalexpert65 (1); Hameedullah Ekhlas (1); Happy singh (1); ikhanuk (1); Le_Noble (1); leng48 (1); wareagle (2)

Previous in Forum: Power Transformer   Next in Forum: US Trimmer Adaptor in India

Advertisement