MVAC Cooling to Shopping Mall Tenant

07/21/2010 3:53 AM

If I have 100 m2 shop (internal facing, not subject to outside thermal conditions), what is the simplest way to determine the amount of cooling that needs to be provided to the space.

Where do you start? Heat Load / TR Calculation / Energy Use at Kw/Hr?

I assume you begin with calculating how much heat the space will generate in order to determine the TR needed to meet the demand before adding equipment to fill the demand.

Can any assist with the mathematics in a layman's term.

Greatly appreciated.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: MVAC Cooling to Shopping Mall Tenant

07/21/2010 4:04 AM

If the building is "not subject to outside thermal conditions" then all the heat dissipated within the space has to be rejected outside it to maintain a temperature, otherwise the temperature will rise without limit. This is not a good starting point, so reject the assumption.

Simple ventilation may be all that is required. Try opening a few windows while the space is in use, perhaps?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Participant

Join Date: Jul 2010
Posts: 2
#2
In reply to #1

Re: MVAC Cooling to Shopping Mall Tenant

07/21/2010 4:14 AM

Space is in the internal of a shopping mall and tempeture of the adjoining common areas and rear corridors is maintained by the property (stated at 22 - 24 `C with 55% relative humidity). Cooling needs to be provided for any heat generated within the space so as not to effect the tempature of those common area.

I think once I can determine a baseline method of calculating the potential heat load I can then determine how much TR will be needed to cool the space in an unfitted state.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: MVAC Cooling to Shopping Mall Tenant

07/21/2010 9:04 AM

One might still duct it outside the building. One would need to do so were air conditioning plant to be installed, as well as a duct for the water that such a plant will generate.

What's the exterior temperature and how much heat is dissipated within the shop?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Anonymous Poster
#5
In reply to #2

Re: MVAC Cooling to Shopping Mall Tenant

07/22/2010 1:05 AM

even if the shop is internal facing, it has some internal heat generating substances, like lights, equipment, and people. You need to calculate the number of these and how much heat is generated bu these. refer ASHRAE if it is in your reach.

Register to Reply
Guru

Join Date: Apr 2006
Location: Cincinnati, Ohio, USA
Posts: 662
Good Answers: 49
#4

Re: MVAC Cooling to Shopping Mall Tenant

07/22/2010 12:31 AM

Some basic load factors (adjusted for easy calculation by non-engineer)-

Bodies in space- use 125 W/occupant

If ceiling plenum is used for return air, figure total wattage of lamps installed

If ceiling plenum is NOT used for return air, use 75% of wattage of lamps installed

ADD total wattage of ALL equipment in space (registers, display illumination, display equipment, etc.)

If space HVAC system is connected to outside air with fresh air duct (likely) add 2 watts per SF of "occupied" space for Outside Air load.

If known, add total HP of supply fans times 750 watts. If unknown, add 5% to sub-total of loads.

Total "load" in watts from calculations divided by 200 is approximate Cubic Meters per minute required.

Total "load" in watts divided by 0.7 is Total HVAC cooling load in Watts

Load divided by 1,000 equals total cooling load in kW.

Cooling load in kW x 0.285 equals "tons of Refrigeration" required.

__________________
NO MATTER HOW WELL YOU HAVE DONE SO FAR, ALWAYS TRY TO BE BETTER TOMORROW.
Register to Reply Score 1 for Good Answer
Register to Reply 5 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); energygod (1); mntnview76 (1); PWSlack (2)

Previous in Forum: 1" NB   Next in Forum: Design of Rubber Band Powered Air Plane
You might be interested in: Cooling Tunnels, Electronic Cooling Fans

Advertisement