We have a new Hospital attached to our old Hospital
Newly installed transfer switches are open transition with a sync feature.
Critical and Life Safety transfer switches will not transfer within the 10 seconds, during a test due to this sync feature. We can bypass if we choose to, but this will cause some issues during transfer to emergency.
Even though it has been proven that the transfer switches will transfer over within 10 seconds during a power outage we can not prove this during our monthly test.
I have bounced this off of some of our third party engineers with two different opinions. One states that the commissioning documents prove that they already transfer over within ten seconds and there is no need to prove it during the monthly test. The other opinion states that you have to prove the 10 seconds monthly
I agree with the later opion, NFPA 110 does not come out and say ten seconds monthly with out doing some digging between chapters.
The loads on these two branches are typical of Chapter 517 of NFPA 70. Our servers do have there own UPS systems but we still have personal computers and patient monitoring systems on these branches as well.
The old Hospital still has critical areas that are served by older open transition switches in which we do have issues with equipment shutting down during the test.
Two ways I could go with this. Disable the sync feature and by a bunch a small UPS's
Or keep the sync feature and possibly be in violation of NFPA 110 and all other applicable codes
My Facilities manager is concerned about this issue as well. We are open for suggestions.
I hope this makes sense