Motor Start/Stop - Soft and Hard

07/26/2010 2:00 PM

What is the difference between motor hard start/stop and soft start/stop?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - Member Engineering Fields - Electrical Engineering - Electrical Construction

Join Date: Apr 2010
Location: Mid Western USA - The Corn Belt
Posts: 1439
Good Answers: 58
#1

Re: Motor start/stop - Soft and Hard

07/26/2010 2:30 PM

Hard start/stop - contacts close, motor starts "hard" and comes up to speed immediately

Soft start/stop - a series of contacts (within the starter cabinet) close in secession (or through the use of a VFD) and the motor ramps up slowly and comes up to speed slowly.

__________________
The first 5 days after a weekend are always the hardest................................
Reply Score 1 for Good Answer
Power-User

Join Date: Oct 2007
Posts: 397
Good Answers: 3
#8
In reply to #1

Re: Motor start/stop - Soft and Hard

07/27/2010 8:31 AM

KJK;

You are right on. This is exactly what is ment by soft start. I have a router that uses a soft start . You don't get that jerk as You would when using a fast start machine. Really works nice especially when doing delicate inlay work.

oilcan13

Reply
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#9
In reply to #1

Re: Motor start/stop - Soft and Hard

07/27/2010 10:10 AM

Allen Bradley soft starts are just gated paired SCR's that slowly ramp up to speed by slowly varying the gating until full phase current can flow. I don't believe this soft start ever converts the incoming power to DC (semi-half weave rectification in the SCR does occur, but both the high and low swing of the phase is passed by the paired arrangement) as a VFD does. This arrangement will not allow a single phase input to power a three phase load as some VFD's can. I know - the theory is basically the same as a VFD.

What I would like to know is why a solid state soft start that handles a given HP (KW) is usually twice the cost of a VFD with the same ratings. Who buys a soft start instead of a VFD?

__________________
Remember when reading my post: (-1)^½ m (2)^½
Reply
Guru
United States - Member - New Member Engineering Fields - Control Engineering - New Member

Join Date: Mar 2006
Location: Washington USA
Posts: 566
Good Answers: 53
#2

Re: Motor Start/Stop - Soft and Hard

07/26/2010 11:27 PM

Soft stop - power removed, motor coasts to a stop.

Hard stop - while running at full speed a large steel rod penetrates the motors fan shroud becoming lodged btween the armature and the rotor.

Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3
In reply to #2

Re: Motor Start/Stop - Soft and Hard

07/26/2010 11:48 PM

I guess it's all relative...

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
Anonymous Poster
#4

Re: Motor Start/Stop - Soft and Hard

07/27/2010 12:50 AM

starting and stopping when you are hard, same as starting and stopping when it is soft.

Reply Score 1 for Good Answer
Associate

Join Date: Jul 2008
Location: India, Kuwait
Posts: 31
#5

Re: Motor Start/Stop - Soft and Hard

07/27/2010 2:34 AM

I guess....

Hard Start/Stop: When the motor is hardwired directly to start/ stop switches.

Soft Start/stop: When you are starting/ stopping the motor via DCS, PLC or any other control systems. These system commands are routed through relays and MCCs to start or stop the motor.

Reply Score 2 for Off Topic
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6

Re: Motor Start/Stop - Soft and Hard

07/27/2010 5:29 AM

In the case where a user is billed on a peak demand kW tariff, it could be a lot of money each year.

In the case where lighting is fed from the same supply, the difference between lights dimming slightly and going completely off while the motor runs up.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#7
In reply to #6

Re: Motor Start/Stop - Soft and Hard

07/27/2010 6:21 AM

Hello PW

Not sure about the money saving. I believe peak demand tariffs use maximum demand averaged over 20 minutes or so (I can't remember exact time), not instantaneous, so choce of starting method makes very little difference to the electric bill.

Cheers.........Codey

__________________
Give masochists a fair crack of the whip
Reply
Guru

Join Date: Jul 2006
Location: CA (Central Arkansas, USA)
Posts: 599
Good Answers: 10
#10

Re: Motor Start/Stop - Soft and Hard

07/27/2010 12:08 PM

With soft start the motor comes up to speed slowly and so inrush current can be lower than with a plain contact. This can allow a motor to start on when powered by a generator that would not handle the inrush current. A hard start can also be a start relay-capacitor combination that will start a motor with more of a load on it than normal. -- JHF

__________________
If it's too good to be true, it probably isn't
Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#11
In reply to #10

Re: Motor Start/Stop - Soft and Hard

07/27/2010 7:18 PM

While the answer provided by KJK/USA (comment # 1) makes more sense in terms of the use of soft starter but, in reality, the answer provided by Gkishorenair (comment # 5) is more correct.

The hard start/stop and soft start/stop are all about the sort of start/stop signals applied to the motor starter.

Hard start/stop: When the motor start/stop operation is done by using open/close contact with applying the electrical signal (generally voltage) directly to the starter contactor through the start stop mechanism (either by HOA or DCS or PLC system), it is called hard start/stop.

Soft start/stop: When the motor start/stop operation is done by using instrument signal (either from DCS or PLC system) applied to the digital relay (such as E3 Plus, Multilin etc.) of the motor starter through the Devicenet or Modbus or other sort of communication protocol, it is called soft start/stop. A soft start/stop doesn't really need of using soft starter or VFD.

The above definitions are written exclusively from my experience and I didn't see such definitions written anywhere but this is the way I found they are being used in many projects. However, the terminology may differ from project to project or industry to industry.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Reply
Guru

Join Date: Jul 2006
Location: CA (Central Arkansas, USA)
Posts: 599
Good Answers: 10
#12
In reply to #11

Re: Motor Start/Stop - Soft and Hard

07/28/2010 9:21 AM

What you are saying is correct. But the terms also apply as I said in my post. -- JHF

__________________
If it's too good to be true, it probably isn't
Reply
Reply to Forum Thread 12 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Ace Boeringa (1); Anonymous Poster (1); Circuit Breaker (2); Codemaster (1); gkishorenair (1); JRaef (1); KJK/USA (1); msamad (1); oilcan13 (1); Phys (1); PWSlack (1)

Previous in Forum: Drawing a Single Line Diagram   Next in Forum: Open Transition Transfer Switch In Hospitals

Advertisement