Dear All
my question is how to decide the rating of isolator and breakers for a 5 MW grid connected system at 33 KV voltage level. (Kindly explain in detail the designing aspect)
Is it mandatory to have a 33 KV LA on the 33 KV (H.V) side of the trafo or we can utilize a 11 KV LA as well.
Re: Design of a 5 MW system
08/02/2010 3:32 AM
5,000,000 ÷ (33,000 x √3) ≈ 87.5A. Perhaps a 100A breaker?
Good Answers: 11
08/02/2010 4:49 AM
Tornado has given you already how to determine the breaker size. If you are using NEC-Code please refere to this link and examples for sizing the breaker.
http://www.elec-toolbox.com/usefulinfo/xfmr-3ph.htm
Let me also give you some information about isolator.
The voltage rating and short circuit rating range of an isolator should be the same as that of the breaker. An isolator is selected based on the circuit current rating ( continuous current ), voltage, fault level( short circuit rating ) and BIL. The isolator provides safety during maintenance on the transformer. An isolator, when in series with the fuse, does not require short circuit rating. Isolator is an off load type dvice. The load switching is carried out by a breaker. The isolator can break the capacitive charging current of a cable and the no load inductive current of a transformer up to a certain magnitude.
08/02/2010 9:22 AM
This means that we should break at CB then use isolator to isolate circuit .?
Correct me if i am wrong i am learner
08/02/2010 9:36 AM
where did you get this idea " isolator to isolate circuit" ?
Reply Score 1 for Off Topic
08/03/2010 2:36 AM
yes u are right
08/03/2010 2:35 AM
guys i think we are deviating from the topic
my question is what should be the CB and isolator rating for a 5 MW system...
and whether we can use a 11 KV LA on the 33 KV side of the trafo.
08/03/2010 7:46 AM
for 33kV system minium available switchgear is of 630A you can use the same.