Problem With Pilot Operated Pressure Reducing Valve

08/02/2010 1:23 PM

Hi Guys

I need some perspective regarding this issue. We have 4 gas turbine which require gas at a pressure of about 19 bar. Unfortunately, gas is being supplied at a pressure of 34 bar (we have no control over this). To achieve the desired pressure of 19 bar, a pilot operated pressure reducing valve was installed on the line. On three separate occasions this set-up has failed to achieve the desired pressure reduction, after being in operation for not more than three weeks (valve has been changed three times).

I will appreciate any information on the possible reasons for this, whether or not this was the best design that should have been implemented and alternate solutions to tackle the issue.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Problem With Pilot Operated Pressure Reducing Valve

08/02/2010 1:42 PM

What is the specification of the valve?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Jul 2010
Posts: 669
Good Answers: 176
#2

Re: Problem With Pilot Operated Pressure Reducing Valve

08/02/2010 2:39 PM

The pressure regulators were new? previously used?

brand name? Model number? all the same brand and model

Failure mode ?

manufacturer's assessment?

Register to Reply
Guru
Engineering Fields - Mechanical Engineering -

Join Date: Sep 2009
Posts: 1651
Good Answers: 71
#3

Re: Problem With Pilot Operated Pressure Reducing Valve

08/02/2010 2:40 PM

If this valve is similar to what I am used to in the fuel industry it works by applying pressure to the top of a valve pinching it closed when excessive pressure is sensed downstream. This pressure is applied through a pressure relief valve downstream set at your fixed pressure (19 bar). If the pressure relief valve opens it sends it's excessive pressure to the top of the control valve reducing flow or pressure.

This is balanced by another relief valve that applies pressure to the bottom of the control valve if there is a pressure drop downstream of the control valve.

Common problems in this system is leaky valve seats allowing pressure to bypass any of the pressure relief valves or the main control valve itself. Also, if the pressure relief valve that pinches down the control valve does not operate quickly enough or is set for the wrong pressure you will have problems.

Hope this helps.

Drew

__________________
Question: What is going on with the American's Government? Response: Who is John Galt?
Register to Reply Score 1 for Good Answer
Guru

Join Date: Feb 2008
Location: Large hole formally occupied by furry woodland creature.
Posts: 3385
Good Answers: 97
#4

Re: Problem With Pilot Operated Pressure Reducing Valve

08/02/2010 3:29 PM

You may have dirt or compressor oil in your lines. Do you have a drop leg and strainer ahead of this valve?

__________________
CRTL-Z
Register to Reply Score 1 for Good Answer
Member

Join Date: May 2010
Posts: 8
#5
In reply to #4

Re: Problem With Pilot Operated Pressure Reducing Valve

08/02/2010 6:22 PM

Hi All, Thanks for your comments so far. I regret I am unable to answer some of your queries due to the fact that I've been unable to access the technical documentation. What I can confirm is that in all cases, the regulators used were new. Also, installation was done by a third party and so the manufacturer's assessment is unavailable. Furthermore, there is no, strainer or drop leg installed. Upon opening the pilot filter, a high level of debris were observed. Even though this was cleaned, the result was the same. On the basis of some of the answers I have received, I would like to ask, are we justified in using a pilot valve(given that the gas stream has a lot of particulate material), or would we be better off using a pneumatic controlled valve.

Register to Reply
Anonymous Poster
#6
In reply to #5

Re: Problem With Pilot Operated Pressure Reducing Valve

08/02/2010 11:35 PM

For This type of pressure sensitive system it would be best to continue with the pilot operated regulator. A sugestion would be to install an inline strainer prior to the regulators.. The fuel gas is always dirty. Have the operators to blow down the filters on a regular basis. The existing regulators would need to be cleaned internally because the gunk in the fuel gas is sticky and therefore the pilot regulators get sticky.

Register to Reply Score 1 for Good Answer
Anonymous Poster
#7
In reply to #6

Re: Problem With Pilot Operated Pressure Reducing Valve

08/03/2010 3:10 AM

You must understand the failure parameters. you cannot repair it when you don't know what to repair. There are a lot of possibilities: dirt, abrasion, damaged diaphragms and of course, the PCV may not be adequate for the job...

Register to Reply
Member

Join Date: May 2010
Posts: 8
#8
In reply to #6

Re: Problem With Pilot Operated Pressure Reducing Valve

08/03/2010 4:29 AM

What would be the comparative advantage/disadvantage, if we decided to use a pressure control valve actuated by instrument air, rather that the current arrangement with the pilot valve where the actuation is by means of the fuel gas stream itself. (from an engineering and economic sense)

Register to Reply
Anonymous Poster
#9
In reply to #8

Re: Problem With Pilot Operated Pressure Reducing Valve

08/03/2010 5:30 AM

This is the only setup that I wopuld allow on my site.

Register to Reply
2
Power-User
United States - Member - New Member Engineering Fields - Chemical Engineering - New Member

Join Date: Apr 2007
Location: Austin, TX
Posts: 367
Good Answers: 10
#12
In reply to #8

Re: Problem With Pilot Operated Pressure Reducing Valve

08/03/2010 9:19 AM

The advantage of the control valve would be as you state, it would mitigate the frequency of the current regulator plugging. Pressure transmitters can be specified to be fairly insensitive to plugging so I would expect the system to be more robust than currently.

Disadvantages include:

More modes of failure (now the actuator, instrument air, power supply, PLC/DCS, etc. all come into the picture for reasons why the valve could fail).

The control valve is probably more expensive, and certainly the entire loop is more expensive than the regulator.

Once the pilot-plugging problem is overcome, you may find that the valve internals are failing prematurely as well. Consider a heavy-duty control valve for this application and tell the vendor about your particulate problem. Other options (like filtration) will be considerably more expensive.

__________________
Money doesn't talk, it screams in your face.
Register to Reply Good Answer (Score 2)
Guru

Join Date: Feb 2008
Location: Large hole formally occupied by furry woodland creature.
Posts: 3385
Good Answers: 97
#11
In reply to #4

Re: Problem With Pilot Operated Pressure Reducing Valve

08/03/2010 7:31 AM

As what I originally suggested appears to be the main cause of the problem, and as the problem you describe is a hazardous condition, I would further suggest that you have the recommended equipment installed as soon as possible, regardless of what type of pressure/flow control you choose.

__________________
CRTL-Z
Register to Reply
2
Power-User

Join Date: Nov 2008
Location: Port Glasgow, Free Republic of Scotland
Posts: 360
Good Answers: 30
#10

Re: Problem With Pilot Operated Pressure Reducing Valve

08/03/2010 6:03 AM

My experience is in a design office for refineries/oil platforms etc so I am always interested in the experience of those that actually work on site.

However to address your issues from my perspective.

The issue of dirt/debris/oil is clearly part of your problem and trying to overcome this is one of the things you need to do. I am a little surprised that you have not seen problems either with the turbines of with filters upstream of the turbines if there is a significant level of debris as my understanding is that the nozzles in gas turbines are small and particulate debris would cause misfiring.

Anyway as you note a pilot operated valve uses the fuel gas as motive force for the valve whereas a PCV uses instrument air. Intrinsically this means that a PCV will be less susceptible to the debris problem. However with a PCV all you do is move the problem as the debris may clog the impulse line for the pressure transmitter causing the same problems but with the measurement instread of the valve operation. You can use sealed units with diaphragms and oil filled impulse lines which can get round this problem by preventing debris getting into the impulse line.

My personal experience is that operators (those that I have worked for include major mid east oil companies) are tending to prefer to use PCVs for this sort of service and only accepting pilot valves for gas blanketing use on atmospheric vessels and tanks - although there is widespread good experience (apart from yours) of using pilot valves in higher pressure service.

I wonder if you need to install some sort of scrubber / filter upstream of the let down valves. Given the continuous problem probably you need to install 2 x 100% so that you can continue operation with a filter always available.

I think you need to identify the source of the debris/gunk/oil/particulate and remove it at source rather than getting to the need to clean valves because there is gunk in the impulse lines so diaphragms on the Pressure Transmitter impulse line could be a good idea.

__________________
Free advice guaranteed or your money back
Register to Reply Good Answer (Score 2)
Anonymous Poster
#13

Re: Problem With Pilot Operated Pressure Reducing Valve

08/03/2010 9:36 AM

If the fuel is gaseous (cng) then your best bet is to use a pressure reducing regulator set to 19 bar outlet. Contact Neil @ 519 496 9755 (BALCKSTONE POWER) HE IS AN EXPERT IN THIS AREA WITH OVER 30 YEARS EXPERIENCE.

Register to Reply
Register to Reply 13 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (4); betomachine (1); Drew K (1); Iris (1); Ortiv (2); PWSlack (1); simonsd (1); Unredundant (2)