I have a UFER ground that we recently placed in our building. The building has it's own UFER ground that was placed when the building was built. Since we were bringing more loads to the building we decided to make another UFER ground since we were going to make excavations any way. This new UFER ground is located 10 ft away from the building's UFER ground.
I obtained the following measurements:
with the instrument set to read DC values:
V=114 VDC
I=4.5 mA DC
With the buidling UFER having the possitive potential and therefore current 4.5 mA flowing from the building UFER to the new UFER (if you use conventional current flow, that is from positive to negative)
These values with the instrument set to read AC values:
V=106mV
I=7.9 mA
The new UFER was not connected to enything when i took the measurements. The building UFER was still in service since the building electric service was in use.
The instrument i use to measure was a general purpose multimeter Fluke.
Is there any reference that can give some perspective to the measurements that i took? and the other question is are my measurements relevant under the conditions and the instrument used for taking them?