Busduct Question

08/05/2010 7:55 AM

A 1150 volt, 6 phase, 50 Hz, 1600A (max) busduct with copper busbars (150mm x 6.35mm each, 1 no./phase) should be with louvres or without louvres ? Louvres will provide cooling for the busbars while it will cause dirt to accumulate inside, which may result in tracking between the phases. Insects may creep in also. Maintenance will not be possible for this particular application more than once a year. Pl give some suggestions.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#1

Re: Busduct

08/05/2010 8:05 AM

Off the cuff (caveat emptor), the busbar seems undersized for the current, and is likely to run hot .... how hot is too hot for your application ? You will most likely need louvres. If you want ingress protection, you can provide a perforated sheet behind them. This may prevent insect ingress, not dust-proof though.

All in all, a conflicting requirement. You should use more copper and seal up the thing airtight.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Anonymous Poster
#3
In reply to #1

Re: Busduct

08/05/2010 8:21 AM

If you feel the busbars are undersized, can you give a rough calculation indicating proper size of busbars for an enclosed arrangement ?

Reply
Associate

Join Date: Dec 2006
Location: Doha Qatar
Posts: 43
#4
In reply to #3

Re: Busduct

08/05/2010 9:10 AM

Mr sridhar thnx a lot for sharing nice article

__________________
Please save the power for Next Generation- Do ur bit
Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#5
In reply to #4

Re: Busduct

08/05/2010 9:19 AM

Glad to have been of help. i urge you to study all the ECT papers of Schneider, they are very informative. Siemens, Eaton, Bussmann...many companies have such informative papers.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply Off Topic (Score 5)
Associate

Join Date: Dec 2006
Location: Doha Qatar
Posts: 43
#2

Re: Busduct

08/05/2010 8:17 AM

952.5 sq mm of copper for 1600A is OK i think

your voltage system suggest u must b having good phase to phase and phase to duct body clearance?

so it will also help in cooling

However system fault is also to be kept in mind -MAx short circuit current of system and time as well, like 70KA for 1 sec etc

__________________
Please save the power for Next Generation- Do ur bit
Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#6

Re: Busduct Question

08/05/2010 4:17 PM

I don't normally do this, but a very rough calculation indicates that a 150mm x 6.35mm bus running 1600A continuous should (and I mean should) work with an expected temperature rise of the bus work of 30 degrees C (when referenced to an ambient temperature of 30 degrees C). Your bus work will likely be running at around 60 degrees C or more, so you may need louvres to remove the heat.

This is a guide only and may not be suitable for you due to unknown application-specific requirements that have not been explained here. You will still need to perform a proper analysis yourself.

Depending on the application, louvres fitted with thin metal mesh screens to prevent insect and dirt ingress may be a suitable option.

__________________
jack of all trades
Reply
Anonymous Poster
#7

Re: Busduct Question

08/06/2010 2:37 AM

I think the busbar size to be revised because current carring capacity is not adequate for the full load (Reff calaculation) .

150 x 6.35 = 952.5 x 1.6 =1524 A

SO The busbar size to be improve to next level and the busduct with louver if not possible please consider sandwitch type busduct with 50kA -1 sec

Bala.A

bala_vlsi@yahoo.com

Reply Off Topic (Score 5)
Anonymous Poster
#8

Re: Busduct Question

08/06/2010 2:47 AM

i think The busbar size to be revised because the size of busbar not adequate at time of full load reff . Below example .

150 x 6.35 = 952.5 x 1.6 = 1524 A

if you consider derating factor the current carring capacity may be reduced and u may be consider louver type , if not possible due to site condition u can consider sandwitch type busduct with 50 kA /1 sec fault condition .

Bala.A

CR4 Admin - email address removed

From the Site FAQ: Do not post phone numbers or email addresses. The CR4 Admin will delete all phone numbers posted in threads or comments, and we strongly urge you not to put up email addresses.