Grounding Under/Below 10 Ohms!

08/06/2010 1:15 AM

Hi Guys!

Please help: I am trying to get a reading on the ground below 10 ohms. The area is so dry that I am getting a reading above 300 ohms. What would be the best way to improve the ground under this circums tances(the soil is dry and we are in dry season here). By the way I am installing a 1000 KVA MCC.

Thanks, Compressor

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster
#1

Re: Grounding Under/Below 10 Ohms!

08/06/2010 2:25 AM

Hai

you can try to install Maintanance free eathing system . because this earthing system consider special material / component to improve the ground value . some body call (or) another name is double earthing system.

Thanks

by Bala

CR4 Admin - email address removed

From the Site FAQ: Do not post phone numbers or email addresses. The CR4 Admin will delete all phone numbers posted in threads or comments, and we strongly urge you not to put up email addresses.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Grounding Under/Below 10 Ohms!

08/06/2010 2:52 AM

So how about saturating the ground near the earth pit with a tanker-load of seawater?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Member

Join Date: Aug 2010
Location: New England
Posts: 9
#3
In reply to #2

Re: Grounding Under/Below 10 Ohms!

08/06/2010 7:11 AM

Or install a lot of ground rods and a tightly spaced ground grid.

__________________
-kg
Register to Reply
Guru
Hobbies - DIY Welding - Wannabeabettawelda

Join Date: May 2007
Location: Annapolis, Maryland
Posts: 7940
Good Answers: 458
#9
In reply to #2

Re: Grounding Under/Below 10 Ohms!

08/07/2010 3:14 PM

Like the man said. Pee on it.

Register to Reply
2
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#4

Re: Grounding Under/Below 10 Ohms!

08/06/2010 9:53 AM

Check out these products. They have been used successfully to lower ground resistance in many difficult situations:

http://www.erico.com/newsDetail.asp?newsid=75

http://www.loresco.com/powerfill.html

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply Good Answer (Score 2)
Participant

Join Date: Jul 2010
Posts: 2
#5

Re: Grounding Under/Below 10 Ohms!

08/06/2010 11:36 PM

Hai, For my siggesstion your reading is very high,no more chance to get less than 10Ω,But for my experience,i got some good value of resistance by using bentonite,salt water,Charcole.you also pour some salt water in your auxillary electrode.

Register to Reply
Anonymous Poster
#6

Re: Grounding Under/Below 10 Ohms!

08/07/2010 2:12 AM

hi..use gypsum,bentonite,sodium sulphate mixture ..one of the best way

Register to Reply
Active Contributor

Join Date: Mar 2009
Location: Makassar, Central Indonesia
Posts: 15
#7

Re: Grounding Under/Below 10 Ohms!

08/07/2010 2:34 AM

Dear compressor,

I have the same problem when I installed the 150 kV LSA grounding up the hill.

First of all, I put more grounding rod ( up to eight rods, 2.4 mtr long) at least 6 to 8 mtr apart and then I linked all of them.

Each grounding rod embedded in to a 1 mtr x 1 mtr hole with 2 mtr depth, each hole I filled at leastwith 25 kg of portland cement mix with 10 kg carbon powder.I did it as how the civil contractor usually do for building cement mixing.

The result is quite good, some of them can reach down to 7 Ohms, in certain place can be as low as 4 ohms.

Please try it.

best regards,

Stanyadji

Register to Reply
Anonymous Poster
#8

Re: Grounding Under/Below 10 Ohms!

08/07/2010 2:19 PM

Hi,

pls tell what type of earth conductor been used and what are meterials used.tell me

Register to Reply Off Topic (Score 5)
Associate

Join Date: Mar 2009
Posts: 51
Good Answers: 4
#10

Re: Grounding Under/Below 10 Ohms!

08/08/2010 1:55 AM

The Methods as Peter T suggested are very good. if you still not able to get the required resistance then do the soil test. if you believe you have a water table below than better you make a hole as deep as possible. i have seen earthing pits upto 12 meters, then a complete filling with bentonite and copper earth rod will do the trick.

All methods can be done but you have an idea about the soil you are using, since you have not mentioned the area or type of soil used its diffiult to say any precise method.

Register to Reply
Commentator

Join Date: Feb 2006
Posts: 55
#11

Re: Grounding Under/Below 10 Ohms!

08/08/2010 8:02 AM

hi

excavate and clear the earth from the earth pit from existing earth fill up with bentonite,salt and charcoal i had excellent results , Bentonite has the property of resistence moisture and reduces the Resistance for flow of current you need to water the earth pits on an on going basis then decide the periodicity of watering good luck

crm

Register to Reply
Commentator

Join Date: Jun 2010
Posts: 75
#12

Re: Grounding Under/Below 10 Ohms!

08/18/2010 5:00 AM

Dear Compressor,

Most of our colleagues on this forum have given you good methods of chemically treating the soil to bring down its resistance. But nobody has given you the method of calculating number of rods to bring down the resistance. I am suggesting the following:

Mathematical expression for Rods arranged in a hollow or solid square is as under:

Resistance of N rods in parallel / Resistance of one rod = (1+kx)/N

where k is a constant and depends upon no. of rods used.

N is the no. of rods in parallel.

x = [L/(ln 48L/a-1)]/d

where

L = Ground Rod length (cms)

a = Ground Rod radius (cms)

d = Distance between two parallel rods

Hollow Square - Solid Square

* * * *****

* * * *****

* * * *****

Values of k/ total no. of rods = 2.7/4;4/8;5/12;6/16;6.5/20;7/24 for hollow sq.

= 6/9;8.5/16/11.5/25;14/36;17/49 for solid sq.

Hope this will help you to arrive at no. of rods required to achieve your target of 10 Ohms.

All the best

BB Raina

Register to Reply
Member

Join Date: Jul 2010
Posts: 5
#13

Re: Grounding Under/Below 10 Ohms!

08/24/2010 1:16 PM

Hi Guys!

Please help: I am still working on this grounding thing. The ground reading got down to 17 ohm. I could have drawn something if I new how to make it happen in this site, but any way: As I said I got the reading from one of the grounding (call it A)to the potential (P) and the current(C) as 17 ohm. I have A separated from P as 10m and from P to C as 10m. But when I reduce the distance from C to P as 8,5m I got a reading of 88 ohm! Would someone explain me in a rational way what is happening?

I am using a SEW Standard ST-1520

I also have a SIRIUS 87, but would not read below 50 ohm, I mean when the the ST-1520 is reading below 50 ohm the Sirius 87 would give the following message(for some reason!): Att

Would someone tell me what is wrong with the Sirius 87?

Thanks, Compressor

Register to Reply
Register to Reply 13 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

amarnath.sn (1); Anonymous Poster (3); BB Raina (1); Brave Sir Robin (1); edisonoic (1); kgil73 (1); mosquito (1); murali (1); PeterT (1); PWSlack (1); tanyadji (1)