4-20mA Current Signal and 24V DV Signal

08/06/2010 6:35 AM

In a plant environment I am using a 32 core signal cable for carrying 4-20mA current signal and 24V DV status signal together. Is that okay or I should separate them?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#1

Re: 4-20mA Current Signal and 24V DV Signal

08/06/2010 8:06 AM

Do you mean 24V DC?

To answer your question, it depends on how fast your signals are changing and how fast you need the control system to react. If the 24V levels are changing state infrequently and you can afford to use a little time filtering the analog signals at the receiving end, you'll probably be OK.

The more frequently the DC levels change state and the faster the response to the analog signals must be, the more likelihood there is of errors due to pickup on the analog side.

Any problems there are will get worse in proportion to cable length.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#2
In reply to #1

Re: 4-20mA Current Signal and 24V DV Signal

08/06/2010 10:23 AM

As John pointed out earlier, placing analog and digital signals in the same cable should only become a problem as the actual frequency of both type of signals increase. I would also presume that the excitation voltage for the 4-20mA sensor will be derived from the same 24VDC source. While I agree with John's analysis for a simple unshielded cable, if you've yet to purchase or install this cable you could just install a cable that will block interference from other signals in the bundle. If the possible interference sensitive signals (4-20 mA) are a carried in an individually shielded twisted pair, then you will not have any interference problems at all. Now custom cable with only one shielded twisted pair can be constructed, but the 24VDC I/O signals won't mind also being a twisted pair connection. So any of the individually shielded twisted pair cables that have enough conductors for all signals can likely give you the optimal noise immunity. That is only if you find that interference is a problem.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Score 1 for Good Answer
Anonymous Poster
#3

4-20mA Current Signal and 24V DV Signal

08/07/2010 5:52 AM

if you are using instrumentation cable there is no problem using same cable for both application

Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4
In reply to #3

Re: 4-20mA Current Signal and 24V DV Signal

08/08/2010 7:45 AM

....though it is best industrial practice to separate analog from digital signals, and not mix the two in the same cable.

  • Digital signals often go down multicore cables.
  • Analog signals often go down multipair cables.

The final decision is with the user. JohnDG has it right, above.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 4 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); JohnDG (1); PWSlack (1); redfred (1)

Previous in Forum: What is Cold Junction Compensation in Thermocouple   Next in Forum: Signal Calculation

Advertisement