Anonymous Poster

Load Sharing Between Two Different Rating Generators

08/07/2010 1:54 AM

We have commissioned one 25MW Machine(Steam Turbine Generator), one year back. Presently one 70MW Machine is under erection. What are necessary requirements to implement the unequal load sharing and VAR sharing (in the ratio of active loads) for both the machines. Both the machines having different droop characteristics and using WOODWARD 505 type Governor.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster
#1

Re: Load sharing between two different rating Generators

08/07/2010 3:24 AM

As u have mentioned both machines have different droop characteristic machine with higher droop will have more load variation with frequency (accept more load in case frequency falls & reject load when freq. rise.). I m not sure of VAR load sharing. It is taken care by automatic voltage regulator

Reply
Power-User

Join Date: Feb 2010
Posts: 187
Good Answers: 11
#2

Re: Load sharing between two different rating Generators

08/07/2010 4:32 AM

Her is an example in fig

In case both machine having different droop characteristics, the load is shared between the machines in such a manner that the volt drop is the same in each and therefore , the machine with the higher characteristic will take the greater proportion of the load If the paralleled sets are of the different ratings, provided that the droop setting of each of the sets are the same, the load will be shared proportionally to their ratings If the droop is not the same, you can parallel as set by adjusting the base speed until the sets share the load. If you have a modern load sharing control panel you should be able to program the size of the various sets into the load controller

Reply Score 1 for Good Answer
Participant

Join Date: Aug 2010
Posts: 3
#3
In reply to #2

Re: Load sharing between two different rating Generators

08/07/2010 5:25 AM

Hi sir,

please tell me the synchronization of two generators connected to one Main distribution board.(rating of generator same)

Reply Off Topic (Score 5)
Power-User

Join Date: Feb 2010
Posts: 187
Good Answers: 11
#4
In reply to #3

Re: Load sharing between two different rating Generators

08/07/2010 6:01 AM

To synchronize AC generators several important factors must be the same.
1- The phase rotation of both generator systems must be the same.

2- The AC voltages of both generators should be equal. In practice,
3- The frequency of the incoming generators must match when synchronized ( in practice the frequency of the incoming generator is 1 to 2 Hz higher than that of the online generator. This can be observed with lights or by using a system chroscope.)

4- The speed and output voltage of the incoming generators are slightly higher to prevent it from becoming a load to the system when it is connected.

for more information see here too.

http://cr4.globalspec.com/thread/57066#newcomments

Reply Off Topic (Score 5)
Anonymous Poster
#5
In reply to #2

Re: Load sharing between two different rating Generators

08/07/2010 7:13 AM

Sir,

Can we programme a suitable logic with a PLC (or DCS system), if load sharing panel is not available.

Reply
Power-User
Engineering Fields - Electrical Engineering - New Member Engineering Fields - Power Engineering - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Construction Engineering - New Member India - Member - New Member Engineering Fields - Nanoengineering - New Member Safety - Hazmat - New Member

Join Date: Mar 2006
Location: Chennai, India
Posts: 312
Good Answers: 3
#6
In reply to #2

Re: Load sharing between two different rating Generators

08/07/2010 11:23 AM

Higher rated machine should be set at less droop than that of lower rated machine,for equal load sharing and smooth operation of system.If both machine ratings are equal,droop should be equal.

__________________
nvmani
Reply
Anonymous Poster
#7

Re: Load Sharing Between Two Different Rating Generators

08/14/2010 9:37 PM

Difinitely there are electrically powered / digital controlled governors thatU has droop features such as the Woodward. You may read your woodward manual on how to do it. proportion Kilowatt sharing is done thru speed adjusting of generator when in parallel operation. The var or power factor is done thru avr with droop characteristics. There are modern governor controller that is being interfaced digitally likewise also the avr. Years ago these these features used analog control (such as potentiometer) to avail the droop characteristics of avr and gov controllr.

Reply
Reply to Forum Thread 7 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (3); Hameedullah Ekhlas (2); nvmani (1); SYEDBASHA-SHAMEEMA (1)