Calibration of DP Flow

08/07/2010 10:32 PM

can any body tell, how can i calibrate the DP flow transmitter (using orfice plate ), and what is formula for calculating the actual flow for both mass and volume flow. we r using Rosemount DP.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Calibration of DP Flow

08/08/2010 7:41 AM

What has Rosemount had to say on the topic?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: Nov 2009
Posts: 335
Good Answers: 63
#2

Re: Calibration of DP Flow

08/08/2010 4:05 PM

Somewhere there's a "sizing sheet" for the orifice plate, which states the maximum flow rate at a calculated DP for that specific orifice plate. The engineering units for flow rate and DP are stated, as well.

Find the sizing sheet and get the calculated DP value, the max flow rate value & the engineering units from it.

Then use a HART communicator (351 or Meriam 4051 handhelds) to set the correct

engineering units
LRV = 0
URV = value from design sheet

on the transmitter.

If you enable the square root, the transmitter's output will be linear will volumetric flow rate.

Multivariable transmitters will calculate inferred mass flow when supplied with an external temperature measurement, but a DP transmitter can only infer volumetric flow from DP, not mass flow.

You can fake a mass measurement by assuming densities at a fixed temperature and pressure and then ranging the 4-20ma volumetric flow signal in your receiver device appropriately.

The formula for mass flow is probably on the forum and definitely on the web, but you don't need it if you're faking it by just ranging the volumetric flow in mass units.

The sizing sheet below is for a multivariable, so the engineering units are mass units, but the concept is identical for volumetric flow sizing.

This orifice plate above was designed to produce 7.00"w.c. DP at a mass flow rate of 3.30 Kg/Min.

Register to Reply
Active Contributor

Join Date: Jan 2010
Location: India
Posts: 14
#3
In reply to #2

Re: Calibration of DP Flow

08/08/2010 6:25 PM

Thanks Very much Mr. Carl

Register to Reply